I've had this conversation with state agencies in CA and we're all square on 
the interpretation as I stated it.   I have spoken with fire and building 
officials from other states about this over the years and I'm pretty sure that 
your issues are regional because we're not hearing about a wave of sprinklered 
non-combustible attics industry-wide.    The exemptions in 903.3.1.1.1 go 
beyond the language of NFPA 13, which is why they are codified, but as written 
they do not supersede the exceptions in 13.   If it was the intent of the code 
to unconditionally require sprinklers in any area not equipped with detection, 
that provision would be in the NFPA 13 standard by now.   Taking another look 
at 903.3.1.1, I would also proffer that if it was the intent of the code to 
require sprinklers in non-combustible concealed spaces and attics, those would 
be specifically listed in 903.1.1.1 but they are conspicuously not addressed, 
because it's not the intent of that section to undo the exceptions in 13 
(903.1.1) for those spaces.

This is likely an excellent section to propose amending in the next code cycle, 
because the way it's written, it gives some credence to the interpretation 
you've seen from "some building departments..."


[cid:image005.jpg@01D65A95.D028F3A0]



From: Anthony [mailto:anth...@archerconstruction.com]
Sent: Wednesday, July 15, 2020 10:38 AM
To: Steve Leyton <st...@protectiondesign.com>; 
sprinklerforum@lists.firesprinkler.org; 'Cary Webber' 
<cweb...@reliablesprinkler.com>
Subject: RE: Uprights in non combustible concealed space

Steve,
In the PNW it has been an issue ever since the 2006 edition came out. Some 
building departments and or the fire prevention department has made comments on 
our plans review stating that based on this section in the code unless  some 
type of detention is installed in this Area then sprinklers would be required.
We have had to take the steps to qualify in our sprinkler bids that we assume 
these areas are being protected by a detection system and thus sprinklers are 
not included in these areas.

Thanks

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222

[cid:image001.jpg@01D65A95.0CA27A50]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>



From: Steve Leyton 
<st...@protectiondesign.com<mailto:st...@protectiondesign.com>>
Sent: Wednesday, July 15, 2020 10:30 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>;
 'Cary Webber' 
<cweb...@reliablesprinkler.com<mailto:cweb...@reliablesprinkler.com>>
Cc: Anthony 
<anth...@archerconstruction.com<mailto:anth...@archerconstruction.com>>
Subject: RE: Uprights in non combustible concealed space

Anthony:

The code has never been enforced this way - sprinklers are required to be 
installed per NFPA 13, with its exceptions noted.  (Regarding attics, the term 
"Attic" is defined in the IBC as, "The space between the ceiling framing of the 
top story and the underside of the roof."  An attic is not a room in that 
regard.)   I think you're "reading further than necessary".   903.3.1.1 states 
that where sprinklers are required to be installed per this section, sprinklers 
shall be installed per NFPA 13.  13 includes very specific exceptions for 
non-combustible concealed spaces such as attics and floor/ceiling interstitial 
spaces.  So, where sprinklers are required, follow 13 and the building is 
considered "fully sprinklered" per the code.

903.3.1.1.1 goes further, and clarifies the language in both 13 and the IBC 
that states "all areas" of the building must be protected with sprinklers.  In 
that context, this section expands on the rooms and areas where sprinkler 
protection can be excluded, but ONLY if detection is provided.   I don't 
believe it has ever been the intent of 903.1.1.1 to supersede the exceptions in 
13 for non-combustible concealed spaces.   If that was the intent, we would 
have been putting sprinklers into concealed spaces for years and the NFPA 13 
committee would have already harmonized the standard with the code.


[cid:image002.jpg@01D65A95.0CA27A50]




From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Anthony via Sprinklerforum
Sent: Wednesday, July 15, 2020 6:57 AM
To: 'Cary Webber' 
<cweb...@reliablesprinkler.com<mailto:cweb...@reliablesprinkler.com>>; 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Anthony 
<anth...@archerconstruction.com<mailto:anth...@archerconstruction.com>>
Subject: RE: Uprights in non combustible concealed space

All, in the IBC it says in section 903.3.1.1 NFPA 13 sprinkler systems.
Where the provisions of this code require that a building or portion
thereof be equipped throughout with an automatic
sprinkler system in accordance with this section, sprinklers
shall be installed throughout in accordance with
NFPA 13 except as provided in Sections 903.3.1.1.1
and 903.3.1.1.2.

903.3.1.1.1 Exempt locations. Automatic sprinklers
shall not be required in the following rooms or
areas where such rooms or areas are protected with
an approved automatic fire detection system in
accordance with Section 907.2 that will respond to
visible or invisible particles of combustion.
Sprinklers shall not be omitted from a room merely
because it is damp, of fire-resistance-rated construction
or contains electrical equipment.
4.Rooms or areas that are of noncombustible
construction with wholly noncombustible contents.

This non combustible area above the ceiling is not required to be sprinklered 
per NFPA 13 but as mentioned in the IBC it's only if the area is protected with 
approved automatic fire detection system.
You could check to see if this area has any smoke detectors and if not use this 
section to show that the upright protection of a non-combustible area is 
required per the IBC.


Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222

[cid:image001.jpg@01D65A95.0CA27A50]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>





From: Cary Webber 
<cweb...@reliablesprinkler.com<mailto:cweb...@reliablesprinkler.com>>
Sent: Thursday, June 18, 2020 11:29 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: RE: Uprights in non combustible concealed space

On the downside, if all areas above the ceilings are not protected, it may give 
a false sense of security. On the upside, more sprinklers are better, and even 
if not required they can act as detectors in the space. Bottom line is that the 
AHJ has ultimate decision making authority.



Cary Webber CFPS Director, Technical Services
Reliable Automatic Sprinkler Co., Inc.
1470 Smith Grove Road, Liberty, SC  29657
Tel: 864-843-5161

[https://www.reliablesprinkler.com/sites/default/files/image001.png]<http://www.reliablesprinkler.com/>

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of John Irwin via Sprinklerforum
Sent: Thursday, June 18, 2020 2:21 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: John Irwin <jir...@quickresponsefl.com<mailto:jir...@quickresponsefl.com>>
Subject: Uprights in non combustible concealed space

CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you can confirm the sender and know the 
content is safe.

We installed temporary upright Protection in a partially occupied building 
during a major renovation. We then came back and dropped pendent heads in the 
new ceiling. We left the uprights above the new ceiling. Fire inspector says we 
need to remove the uprights now. Is there a basis for removing these? I realize 
they are not required but are they permitted to remain?

John Irwin