Re: [RE-wrenches] Utility refuses to upgrade transformer to accommodate photovoltaic system

2014-01-16 Thread jay peltz
Hi Jason

Out of curiosity how big is this PV system?

Good luck and keep us informed. 

Jay 

Peltz power




 On Jan 16, 2014, at 12:45 PM, b...@midnitesolar.com b...@midnitesolar.com 
 wrote:
 
 
 I wonder if anybody at the FSEC might have some good advice here ?
 Just a wild guess...
 boB
 
 On 1/16/2014 12:08 PM, Jason Szumlanski wrote:
 Florida Power and Light (FPL) rejected my request to upgrade a utility 
 transformer (at my cost) to accommodate backfeed from a PV system. Their 
 basis is their own Net Metering Guidelines, which are not the same as the 
 Florida Public Service Commission's Netmetering Rule (law). I believe the 
 property owner is within his rights to proceed with the project and should 
 be approved for interconnection. I'm appealing to the PSC for assistance, 
 but if you have any advice or contacts that may be able to help, please 
 contact me off list.
 
 What is boils down to (I think) is the utility's interpretation of the Rule. 
 They believe the intent is to allow people to netmeter to the extent that it 
 offsets their consumption only. If that were strictly the case, there would 
 be no provision for payment for excess energy produced annually (at 
 wholesale rates). The Netmetering Rule allows backfeed up to 90% of the 
 customer's service capacity, without regard for the energy consumption, but 
 doesn't clarify if the utility is obligated to upgrade service capacity upon 
 request.
 
 They've dug their heels in, and now it's David vs. Goliath. (David did win 
 that one, right?)
 
 
 Jason Szumlanski
 Fafco Solar
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] interchangeability of battery temp sensors

2014-01-15 Thread Jay Peltz
Hi Mac

Outback and midnight are compatible  but not with xantrex 

Jay
Peltz power

Sent from my iPhone

 On Jan 15, 2014, at 8:47 AM, Mac Lewis maclew...@gmail.com wrote:
 
 Hello wrenches,
 
 Does anyone know if the older xantrex bts/15 temp sensor is the 
 interchangeable with the Outback RTS temp sensor.  The pins look the same.  A 
 quick internet search was not conclusive.  I just found an old box jammed in 
 a closet of the bts/15 and want to put them to use.
 
 Thanks in advance
 
 -- 
 
 
 
 Mac Lewis
 
 Yo solo sé que no sé nada. -Sócrates
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flickering LED lights on and Outback Dual 7248VFX system

2014-01-07 Thread jay peltz
Hi bill

My $.02. 

Single vfx3524, Trojan IND in an AC electric house with about a dozen LEDs of 5 
or 6 different types and brands. 

No flickering at all, no dimmers. 

One test I thought of was to,run the generator and see if the flicker 
continues. 
If so, then bypass the inverters to take the chargers off line,

As to bulbs, I've been super happy with the Cree ones from Home Depot. $10 ish 
and beautiful light both warm and daylight. 

Jay

Peltz power






 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flickering LED lights on and Outback Dual 7248 VFX system

2014-01-06 Thread Jay Peltz
Hi Kirpal

Are the lights on dimmers?

Jay
Peltz power

Sent from my iPhone

 On Jan 6, 2014, at 1:09 PM, Kirpal Khalsa solarwo...@gmail.com wrote:
 
 Hi All.have a puzzling problemcustomer has a fully LED lit house.   
 All LED lights are flickering when the fridge compressor, tile saw, grinder, 
 washing machine etc come onThe inverters are about 6 years old Dual 
 Outback VFX7248 power system with rolls surrrette batteries.they are 
 building the house and most motors when they are running, including the 
 fridge seem to cause the LED lights to flicker continuously while the motors 
 are running, the fridge seems to be the worst culprit and just so happens to 
 be the most regular and often runner (fridge is a Amana Model # ARB2257CC 
 rated at 7.7 AmpsFridge is on a GFI outlet...The LED bulbs are Eco Smart 
 made by Cree.Model 499 485 and they are all dimmable lights and they are 
 on Lutron CL dimmer switches which are supposed to be compatible with LED 
 bulbs.)
 Looking for any advice or others experience to try to solve this annoying 
 problem.Anyone else have this problem with these particular bulbs or 
 similar experiences with these or other LED bulbs
 I am having the customer try some other makes and brands of bulbs.
 
 Sunny Regards,
 Kirpal Khalsa
 NABCEP Certified PV Installation Professional
 Renewable Energy Systems
 www.oregonsolarworks.com
 541-218-0201 m
 541-592-3958 o
 ___
 List sponsored by Home Power .org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Flickering LED lights on and Outback Dual 7248 VFX system

2014-01-06 Thread Jay Peltz
Dimmers are super specific to light brand/type.  You'll have to do the research 

For now swapping to regular switches should work

Jay


 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Electric fence, metal buildings, lightning protection systems

2013-12-06 Thread jay peltz
Hi Erika,
What seems to be the issue?
And what equipment ( inverters ) are you using

Jay

Peltz power




 On Dec 6, 2013, at 5:57 AM, Erika Weliczko er...@repowersolutions.com 
 wrote:
 
 Anyone had to contend with electric fence installation (AC controller) using 
 a ground rod (not main service) at remote farm building and messing with 
 inverters? And perhaps causing other issues?
  
 Of course, this is a metal roof with a lightning protection system (i.e. bare 
 braided copper on roof all the way to rod.)
  
 I think we need to redirect the electric fence wire to its own dedicated 
 rods, away from the building that has solar.
  
 Insights are appreciated.
  
 Thanks,
 Erika
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV Wiring methods

2013-11-19 Thread jay peltz
Hi August,

I can only assume that the inspectors are talking about say running a return 
leg which would have no pair back to the combiner/junction box?


jay

peltz power

On Nov 19, 2013, at 9:38 AM, August Goers wrote:

 Hi All –
  
 On a related note, I’ve become good friends with some of the inspectors in 
 San Francisco and they called me yesterday with a question. Is it okay to run 
 individual DC conductors through EMT for wire management purposes? We have 
 always run paired positive and negative conductors in conduit so the question 
 had never occurred to me. Obviously, you have to bond both ends of the 
 conduit if it is over 250 v. I know that AC would have induction issues with 
 running individual conductors but I’m not sure with DC.
  
 Thanks,
  
 August
  
  
 August Goers
 Principal
 Luminalt Energy Corporation
 o: 415.641.4000
 m: 415.559.1525
 www.luminalt.com
  
  
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
 Sent: Monday, November 18, 2013 11:33 PM
 To: 'RE-wrenches'
 Subject: Re: [RE-wrenches] PV Wiring methods
  
 Bill:
  
 There is no need to stuff MC4 cables into standard conduit.  You can either 
 slot the pipe using our easy method or install bulkhead type connectors.  The 
 connectors are readily available.  I get them from PV Cables in Northern 
 California..
  
 Wire routing problems and some solutions can be found on our web-site:
  
 http://millersolar.com/MillerSolar/practices/PV_wiring/_PV_Wiring2.html
  
 Since the industry won’t provide wire management solutions, we are making our 
 own.  Questions:  Just write or call.
  
 William Miller
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of frenergy
 Sent: Thursday, November 14, 2013 7:46 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] PV Wiring methods
  
 William, Billfrom another Bill,
  
 Two things:  For the rest of us (maybe it's just me?!) that's still 
 trying to figure out how (or why) to stuff a MC4 connector into conduit and 
 my hesitation in using SS wire ties for fear of the sharp edges cutting or 
 chaffing into cables, I'm open for advice. Any wire I use on the roof is 
 rated for that type of service and I have some off-grid systems that have 
 been in the sun for some 25 years where the wire still looks nearly new even 
 when flexing it to look for checking/cracks.  It seems the wire/insulation 
 can take it, thus it seems like the key to wire management is to keep the 
 wire from moving and off the roof, secured to the racking, thus not 
 compromising the insulation. 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread jay peltz
Hi Bill,

I get mine from PV-cables
Less expensive and no minimum order

Cheers,

jay 

peltz power
On Nov 14, 2013, at 6:21 PM, Bill Hoffer wrote:

 Jason
 
 I just started using Nine Fasteners, Inc  www.ninefasteners.com  . 410 
 stainless wire management clips.  Got turned on to them at SPI this year. 
 They are awesome, same basic clip concept except they add a nice rounding 
 along the edges that keeps it from cutting into the wire.  A step above the 
 rest and in quantities of 500 buy direct for $.28 - .29 each depending on the 
 style.  They are open to custom design ideas, made in the good old USA, and 
 customer service was outstanding too!
 
 Bill Hoffer
 Sunergy Engineering Services PLLC
 
 
 On Thu, Nov 14, 2013 at 11:08 AM, Jason Szumlanski ja...@fafcosolar.com 
 wrote:
 I know we've had this discussion before, but I wanted to again recommend the 
 WireClips from PV Racking. We are using them on Enphase trunk lines, and find 
 them to be great for this purpose. At $0.25 each, they are cost effective.
 
 That said, wire management is often a matter of strong opinion, and we are 
 far from standardization and an accepted set of best practices.
 
 Jason Szumlanski
 Fafco Solar
 
 
 
 
 On Thu, Nov 14, 2013 at 1:03 PM, Kirpal Khalsa solarwo...@gmail.com wrote:
 Augustthank youyou are right they are actually a Heyco productmy 
 bad!!!  Ray, we recently got them thru 
 http://www.heilind.com/products/heyco/Heyco_solar.asp
 
 Ray...Contact me off list and i will share my sales persons contact info..
 Cheers, 
 
 Sunny Regards,
 Kirpal Khalsa
 NABCEP Certified PV Installation Professional
 Renewable Energy Systems
 www.oregonsolarworks.com
 541-218-0201 m
 541-592-3958 o
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 
 -- 
 Bill Hoffer 
 161 SE Fourth Ave
 P.O. Box 1823
 White Salmon, WA 98672
 suneng...@gmail.com
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] To stack or not to stack? Off-grid 240V

2013-10-30 Thread jay peltz
Hi Hilton,

In my experience the only way to know if it will work is to try it.
( it'll run it, but might not start it)
Because there are so many different quality motors out there all with similar 
ratings but they don't work the same.
I've seen a 5hp completely trip off line a 15kw diesel generator.

One option is to swap the motor for a 3 phase and then get a 240 single phase 
to 3 phase motor speed controller.
This will allow a soft start, very cool stuff.

let us know what you do,

jay

peltz power


On Oct 29, 2013, at 7:47 PM, Hilton Dier III wrote:

 Hello Wrenches,
 
 I have an off-grid client with a 24V system and an old Xantrex SW4024. He 
 wants 240VAC capability with enough oomph for sometimes making a cut with his 
 3 hp table saw without starting the generator.
 
 I am looking at Apollo, Magnum, and Outback inverters. I'm most familiar with 
 Outback. I have a couple of installations out there with stacked 3.6 kW 
 Outbacks.
 
 However, the Apollo marketing promises that their 3.2 kW inverter will start 
 a 3 hp motor. Will it actually, and is this a good idea even if it can?
 
 I'd appreciate hearing about your experiences with 240V Apollo units, stacked 
 Magnums, and stacked Outbacks. I know from experience that the Outbacks 
 require some hundreds of dollars of extra fittings and electronics to make a 
 proper stacked installation. How about Magnum? Any comments on reliability?
 
 Many Thanks,
 
 Hilton 
  -- 
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 12V battery charger

2013-10-30 Thread jay peltz
Hi dave

I have used the power max, it works well. 
Made by some ex Iota engineers if I have the correct info. 
http://www.powermaxconverters.com

Jay

Peltz power








 On Oct 30, 2013, at 1:16 PM, Dave Palumbo d...@independentpowerllc.com 
 wrote:
 
 Wrenches,
  
 I’m looking for a battery charger to augment an OutBack FX 2012 
 inverter/charger for a 12V off-grid system that could use shorter charging 
 times during our cloudy late fall/winter periods in northern Vermont. Both 
 the generator and the battery bank are amply sized as is the PV array. I have 
 used Iota chargers in the past, but wondered if they are other options worth 
 considering.
  
 Thanks,
 Dave
  
 David Palumbo
 Independent Power LLC
 462 Solar Way Drive
 Hyde Park, VT 05655
 www.independentpowerllc.com
 Vermont Solar Partner
 25 Years Experience, (802) 888-7194
  
  
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
 Sent: Wednesday, October 30, 2013 10:57 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] To stack or not to stack? Off-grid 240V
  
 Hilton,
 Kevin's comments are well taken. To add a bit:
 
 Magnum are exceptionally easy to set up and program. The user interface is 
 well designed. A few issues to be aware of from my experience: 
 - All of our Magnum-based off grid systems have been single inverter. At 4 
 kW, a single inverter may not be enough for that particular 3hp motor - best 
 to CYA with the customer on the possible need for a stacked pair. 
 - Magnum allows a pretty wide voltage dip to accomplish surge capacity, so 
 when the saw starts, expect lights to flicker. Our CF bulbs flicker when the 
 refrigerator starts.
 
 Our trial with Apollo a couple of years ago was probably the single most 
 negative experience with an inverter manufacturer of my career. Kevin's 
 comment that the most basic programming required hooking up to a computer is 
 accurate. The computer must have their proprietary software installed, and 
 the hookup was necessary even to initiate an equalize charge from an AC 
 source. We have several warranty replacement and takeout units on a shelf 
 here, from two installations (including in my own home) where the equipment 
 was replaced after being unable to get it to work reliably. Ultimately, 
 Apollo agreed in writing to reimburse us for the cost to replace their 
 equipment with another brand. They never came through. 
 
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified PV Installation Professional
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder, Positive Energy, Inc.
 A Certified B CorporationTM
 3209 Richards Lane
 Santa Fe, New Mexico 87507
 505 424-1112 office 780-2738 cell
 www.positiveenergysolar.com
  
 On 10/29/2013 10:32 PM, Kevin Pegg wrote:
 Hi Hilton,
  
 My $0.05 worth as off-grid is my primary domain.
  
 The SW4024 is an excellent inverter, reliable, robust and if you can find 
 another stack them for 240 and will have no issues with the 3 HP table saw 
 (assuming batteries can handle that is). I run my whole home from a 13 year 
 old pair of them.
  
 Magnum makes an excellent, robust, and reliable off-grid inverter. Available 
 in 120 or 240 without stack. Stacking Magnums (for more power) is 
 straightforward and the user interface is very simple and intuitive. There is 
 some different hardware required for stacking. If a second SW4024 isn't an 
 option then this is what I would do.
  
 I test installed an Apollo unit last year. What a frustrating experience that 
 was. It requires a computer and a RS485 interface to program the most basic 
 features to make the unit usable. Nice when I was real remote and without 
 Internet. That alone makes it unappealing in my books. Seems they are a bit 
 behind the rest of the crowd. I'd not trust a marketing department claim it 
 will start that saw unless they can demonstrate it. (with of course some 
 other loads on the system - having to power down the house so one can work in 
 the shop is hardly usable).
  
 Outback units are common, though suffer from weak battery chargers and power 
 quality issues while under charge so for off-grid that involves any 
 significant generator charging they are not ideal. They are complex to 
 program and operate and end users report lots of frustration.
  
 Kevin
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Hilton Dier III
 Sent: October 29, 2013 6:48 PM
 To: re-wrenches@lists.re-wrenches.org
 Subject: [RE-wrenches] To stack or not to stack? Off-grid 240V
 
 Hello Wrenches,
 
 I have an off-grid client with a 24V system and an old Xantrex SW4024. He 
 wants 240VAC capability with enough oomph for sometimes making a cut with his 
 3 hp table saw without starting the generator.
 
 I am looking at Apollo, Magnum, and Outback inverters. I'm

Re: [RE-wrenches] Adding Charge Controller(s)

2013-10-24 Thread jay peltz
Hi Jeffe,

I don't know the specs on those Kyocera, but if they are the same VOC then they 
are fine together.

As to a enclosure for the CC's, I'd look at Midnight.
They have about a million different boxes, you'll find one that will do the job 
for you I'm sure.

Depending on the area, you might look at a midnight 150v, or  200v or 250v 
controller, as you can then run all in series.

jay

peltz power


On Oct 24, 2013, at 1:13 PM, Jesse Dahl wrote:

 Hello,
 
 Looked at a system today that consisted of the following:
 
 15 - Kyocera 158W modules
 3 -   Kyocera 185W modules
 1 -   Outback MX60
 8 -   New Trojan L16RE (48V system)
 1 -   Xantrex SW Plus 
 
 6 months ago he swapped out his old charge controller to the new MX60 and 
 purchased the new batteries at that time.  The array wiring did not change 
 and is wired in 6 strings of 3.  (confusing to the MX60?)
 
 He is now adding 4 Kyocera 240W modules.  He also purchased another MX60 for 
 this array.
 
 From my perspective, removing the 3 185W modules and getting them on their 
 own controller would be a better use of the modules.  The system currently 
 does not have any disconnects on the PV side.  There are fuses in the 
 combiner boxes on the array, but no disconnects inside at the charge 
 controller.  So adding 3 charge controllers, and now needing to add GFDI, 
 means a box of some kind needs to be added to house these breakers. 
 
 Outbacks GFPs and panel mount breakers will work, but what is the best 
 mounting solution for these?  One DC Flexware enclosure? It will of course 
 allow for all the DC OCPD  and allow for the landing of the output of the 
 charge controllers.  Or is there another enclosure/OCPD solution I should 
 look at?  
 
 
 Thanks as always!
 
 Jesse
 
 
 
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] 230 50 hz kWh meters

2013-10-23 Thread jay peltz
Hi All,

Does anyone know of either dial or EZ read kWh meters that can work with 230v 
50 hz,
100 amp is more than enough

thanks

jay 

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Pump end repair needed_helical rotor SQFlex

2013-10-09 Thread Jay Peltz
Hi Mick

Have you tried preferred pump here in ca?

Jay
Peltz power

Sent from my iPhone

 On Oct 9, 2013, at 9:11 AM, Mick Abraham m...@abrahamsolar.com wrote:
 
 Hello, Wrenchies~
 
 I supplied the Grundfos SQFlex 11 SQF-2 helical rotor pump to a client back 
 in the good old days before dear Grundfos decided us solar guys weren't good 
 enough to shepherd their pumps. 
 
 Serious drought caused the well to dry up; the pump got pulled but did not 
 get a rinse-through with clean water. The mud inside the rotor dried out and 
 cemented the rotor in place. I think the motor is fine but is repeatedly 
 going into self-protect mode since things won't turn. 
 
 My client needs a repair that I am not qualified to handle since...after 
 all...I'm just a solar guy not good enough to receive customer support from 
 the Mother Ship.
 
 ++
 
 Authorized Grundfos pump guy #1 opened things up, declared that the machined 
 rubber volute was chewed, and he offered to install parts from his shelf, but 
 his parts were for model 6, not 11 so the gallons per minute would go way 
 down. 
 
 Authorized Grundfos pump guy #2--the wholesaler in El Paso from whom I 
 originally bought the pump--says these are never repaired, just replaced and 
 of course for close to $3000.
 
 +
 
 Non-authorized pump guy me finds the universe to be absurd at times but not 
 this absurd...surely not this absurd...
 
 So there's my dilemma of the week, Friends. Kindly point the way to any shop 
 that could repair this problem child. Thanks  Jolliness, 
 
 Mick Abraham, Proprietor
 www.abrahamsolar.com
 
 Voice: 970-731-4675
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GTBB resistance

2013-10-09 Thread jay peltz
Hi William

I have been giving this some though. 

As we know it makes no sense, now. 
What don't we know about electric prices in the near future that might make 
this 
cost effective?

Jay

Peltz pow




 On Oct 9, 2013, at 12:03 PM, William Miller will...@millersolar.com wrote:
 
 Friends:
  
 I have been informed of another article on this subject:  
 http://www.bloomberg.com/news/2013-10-07/battery-stored-solar-power-sparks-backlash-from-utilities.html
  
  
 The subject came up on this forum recently and most of us said or thought, 
 “how stupid, there is no good reason to ever do this, the efficiency losses 
 do not justify this!”
  
 Ironically, just a few days later one of us posted questions about how to do 
 something quite like this (SW Inverters in energy management mode).
  
 Food for thought…
  
 William
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunBandit Hybrid Solar Water Heater

2013-10-03 Thread jay peltz
Hi Jason

I would only add that this continues the issue with single tank solar/ grid 
combos
IE it's hard to make sure the heat is coming from solar, as the tank has the 
thermostat from the grid side as well. 

It's a solution still looking for a problem. 

Jay

Peltz power




 On Oct 3, 2013, at 1:13 PM, Jason Szumlanski ja...@fafcosolar.com wrote:
 
 Anyone else getting inundated with SunBandit Hybrid Solar Water Heating 
 System marketing emails? Any first impressions? Here are my initial thoughts:
 
 Pros - provides hot water in utility outages, no interconnection hassles, 
 possibly easier permitting hurdles, eliminates moving parts in active SDHW 
 systems
 Cons - no grid-tie, any excess energy produced is wasted, AHJs won't know how 
 to categorize equipment for permitting and may chargesolar water heating and 
 PV permits and inspections
 
 I haven't dug too deep, but one strange thing I think I saw on a spec sheet 
 was that the micro-AC Grid (aka microinverter) is UL 1703. If that is the 
 case, how does the PV continue to provide water heating in a utility outage? 
 What I really don't understand is why there is a need for a microinverter at 
 all? Why not just use a DC element? I guess a microinverter, despite minor 
 efficiency losses, is cheaper than a load controller.
 
 Jason Szumlanski
 Fafco Solar
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generator automatic disconnect

2013-10-02 Thread Jay Peltz
What about running the genny through one inverter and putting a transfer switch 
on the AC out which opens the ac out. 
Meaning 100% charging but no loads. 

Jay

Sent from my iPhone

 On Oct 2, 2013, at 9:50 AM, Larry Crutcher, Starlight Solar Power Systems 
 la...@starlightsolar.com wrote:
 
 Ray,
 
 I had thought about this but it seems that with all inverters paralleled and 
 controlled through the router that it would not allow one to charge and pass 
 through the generator power while the others are inverting. Do you know a way 
 of doing this.
 
 Larry
 
 On Oct 1, 2013, at 9:10 PM, Ray Walters r...@solarray.com wrote:
 
 If they HAD to have the wee Generac, you could have it feed only one 
 inverter, and the other 3 Magnums could stay in invert mode.  I have large 
 systems where I'm not using the charger off every inverter.  
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer, 
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760
 On 10/1/2013 11:09 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
 You are right. Normally I would not even consider a generator of this size. 
 My constant thinking outside the box took me down this rabbit trail. I'm 
 back.
 
 Thank you,
 
 Larry 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generator automatic disconnect

2013-10-02 Thread Jay Peltz
Exactly

Jay

Sent from my iPhone

 On Oct 2, 2013, at 11:48 AM, Larry Crutcher, Starlight Solar Power Systems 
 la...@starlightsolar.com wrote:
 
 If you mean automatic transfer, how would you trigger it since AC power will 
 be present from both sources at the inverter output? Do you mean a N.C. 
 contactor that would open on gen power, something like attached drawing?
 
 Larry 
 Screen Shot 2013-10-02 at 11.43.47 AM.png
 
 On Oct 2, 2013, at 10:37 AM, Jay Peltz j...@asis.com wrote:
 
 What about running the genny through one inverter and putting a transfer 
 switch on the AC out which opens the ac out. 
 Meaning 100% charging but no loads. 
 
 Jay
 
 Sent from my iPhone
 
 On Oct 2, 2013, at 9:50 AM, Larry Crutcher, Starlight Solar Power Systems 
 la...@starlightsolar.com wrote:
 
 Ray,
 
 I had thought about this but it seems that with all inverters paralleled and 
 controlled through the router that it would not allow one to charge and pass 
 through the generator power while the others are inverting. Do you know a 
 way of doing this.
 
 Larry
 
 On Oct 1, 2013, at 9:10 PM, Ray Walters r...@solarray.com wrote:
 
 If they HAD to have the wee Generac, you could have it feed only one 
 inverter, and the other 3 Magnums could stay in invert mode.  I have large 
 systems where I'm not using the charger off every inverter.  
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer, 
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Using legacy modules on micro-inverters

2013-09-28 Thread Jay Peltz
Hi Bill

Is there a new M250?
Enphase shows the 250 at 48vdc max and states 60 cell only modules. 

That would be nice if it did both

Jay

Peltz power. 



Sent from my iPhone

 On Sep 27, 2013, at 10:14 AM, Bill Brooks billbroo...@yahoo.com wrote:
 
 William,
  
 Just to add one more thing. I said that the M215 does not match well, but if 
 you have them on hand, they would still work. You will probably power limit 
 in the spring and fall, but the rest of the year you will probably do fine. 
 The M250 has a higher operating voltage for 72-cell arrangements. The M215 is 
 more suited for 60-cell modules and circuits.
  
 Bill.
  
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
 Sent: Thursday, September 26, 2013 10:01 PM
 To: RE-wrenches
 Subject: [RE-wrenches] Using legacy modules on micro-inverters
  
 Friends:
  
 I am trying to upgrade a long time off-grid client to a grid-connected 
 installation.  They have a mix of Siemens PC4JF and Shell SQ-150P modules.  
 It is my understanding that putting two of the PC4JFs in series is exactly 
 one SQ-150.  I don’t have spec sheets for the PC4JFs but I am told they are 
 an SP75.  If I use the data for the SP75 and multiply the voltages by two I 
 get exactly a SQ-150P.
  
 Anyway, putting two 36 modules together makes one 72 cell module.  This would 
 likely work with an Enphase M190 but those are no longer manufactured.  Same 
 with the M215.  Power One makes a micro that meets the predicted voltage 
 window.
  
 I did this a while ago with pairs of SR100s.  It worked great.  Anyone try 
 this with even older modules, like those cited???
  
 Thanks in advance.
  
 William Miller
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] On demand WH

2013-09-28 Thread jay peltz
Hi bill

Just installed a takagi TK4
6 watts standby, pilotless
87 watts on
110 watts freeze element. 
Solar preheat ready
This one has a fan

Others I've seen have no fan, and some with no standby watts or pilot

Jay

Peltz power. 




On Sep 28, 2013, at 9:19 PM, frenergy frene...@psln.com wrote:

 Off-grid Wrenches,
  
 I'm working on a load sheet and am having a hard time finding standby 
 and while firing electrical usage for a propane-fired on demand water heater. 
  Do they some/all have standing pilots, glow bars, something else?  I'm 
 guessing the standby power needs are very low but we all know how even 10-15 
 watts adds up over 24 hrs when you're off-grid.
  
 If any body has some actual numbers rather than just pdf.specs 
 (though manus specs might help some), I would be most grateful.  Thanks in 
 advance.
  
 Bill
 Feather River Solar Electric
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system with microinverters

2013-09-18 Thread Jay Peltz
I believe this is the tenK solar product being talked about. 

Jay
Peltz power

Sent from my iPhone

On Sep 18, 2013, at 8:49 AM, August Goers aug...@luminalt.com wrote:

 Hi Charlie,
  
 I can't help but be intrigued by your setup here. It seems like the complete 
 opposite of where our commercial systems are going with transformerless 1000 
 V inverters entering the market. Anyway, I'm sure it's an interesting project 
 and there may very well be advantages to the system you're building.
  
 I agree with Dave below that you should be okay with a #6 run to a ground 
 rod. Otherwise, your logic for sizing the GEC seems correct. We deal with 
 this similar issue when designing battery backup systems and the GEC can get 
 unwieldy very quickly. I would just point out your sizing logic per 
 250.166(C) on your plans for the inspector to see.
  
 Best,
  
 August
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
 Sent: Wednesday, September 18, 2013 5:38 AM
 To: re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] GEC sizing for a high amp, low voltage PV system 
 with microinverters
  
 I think Gary may be overthinking this. If the micro-inverters have a GEC lug 
 then you'll need to run a GEC.
 
 If you run your GEC to a ground rod, then you don't need to use one larger 
 than #6 per 250.166(C). (note also (D) and (E) but they're less useful to you 
 here)
 
 Commentary:
 It makes no sense to me why the NEC can require a 0.9in diameter, #600mcm GEC 
 for some systems (not this one) per 250.166(B) and then say oh wait, you 
 installed a single ground rod? Then a #6 is all you need! in 250.166(C). But 
 it certainly makes our lives easier.
 
 If the building GE is not a ground rod, you could still run your #6 GEC to 
 that new ground rod, and then bond that rod to the existing electrode using 
 whatever size jumper is required per 250.53 (which I believe would also be a 
 #6). This lets you keep that 300' run as a #6 rather than a #4 or #2 that may 
 be required otherwise.
 
 DKC
 
 On 2013/9/17 23:56, Gary Willett wrote:
 Charlie:
 
 The answer depends on whether the system (modules and micro-inverters) is 
 grounded or ungrounded. I think you are describing a grounded system, 
 but it's not totally clear based on your issue description.
 
 If the micro-inverter is transformer-less the conductors are not isolated 
 between the DC-in and the AC-out. This requires the micro-inverter to have no 
 DC-side system ground. The micro-inverter AC-side always requires an EGC.
 
 I am assuming that the PV modules are in close proximity to the 
 micro-inverters, and the 300' home-run is for the AC outputs of the 
 micro-inverters.
 
 Is either DC bus (PV+ or PV-) a grounded conductor, or are both busses 
 ungrounded? If the DC-side combiners and re-combiners have OCPDs and 
 disconnecting means for both PV+ and PV-, then your system is considered to 
 be floating or ungrounded.
 
 If the system is ungrounded, a GEC is not required on the DC-side of the 
 micro-inverter, and only an AC-EGC sized per NEC 690.45 is required.
 
 If the DC-side combiners and re-combiners have OCPDs and disconnecting means 
 for only one conductor (PV+ or PV-), then your PV system is considered to be 
 grounded. If the system is grounded, the combined DC-GEC and AC-EGC 
 sizing requirements in NEC 690.47(C)(3) apply. The larger of the EGC (Table 
 250.122) and GEC [250.166(B)] sizes will be required.
 
 More specifics on the PV module Vmpp and micro-inverter you're dealing with 
 would be helpful.
 
 Regards,
 
 Gary Willett
 Icarus Solar
 
 
 On 9/17/13 8:37 PM, Aladdin Solar wrote:
 We will be installing a 40KW grid-tied PV system that uses PV modules wired 
 in parallel as per the module manufacturer -- so it's a high amperage, low 
 voltage system on the DC side. 2 branches of about 3KW of parallel wired 
 modules each come together onto a DC bus. The DC branch conductors are sized 
 as 2AWG.
  
 The inverter system provided by the manufacturer consists of a number of 
 UL1741 single phase microinverters that all are powered off of the low 
 voltage DC bus. So there's a bunch of microinverters in parallel, combined 
 output is single phase power.
  
 Those microinverters have a ground lug labeled GEC. You know where this is 
 going...
  
 Assuming we are following NEC 690.47(C)(3), we'll be treating this ground as 
 GEC and following all the GEC rules. My understanding is that because the DC 
 conductors within the array are 2AWG (NEC 250.166(B), we will need to connect 
 all 12 branches and 6 DC buses with continuous 2AWG and bring it all the way 
 back 300' to where the AC GEC bond is located. We're getting a lot of 
 pushback from the electrical sub and even some disagreement from the module 
 manufacturer on this--no one's ever seen a grounding conductor of this size 
 being required for this application.
  
 Please don't get too bogged down

Re: [RE-wrenches] Off Grid LP Gen advice

2013-09-15 Thread jay peltz
Hi all

FYI. 

But if you live in ca, they don't sell them here according to the website. 

Jay

Peltz power






On Sep 15, 2013, at 9:19 AM, Dave Palumbo d...@independentpowerllc.com 
wrote:

 Ecogen it is. Thanks everybody.
  
 Dave Plaumbo
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of John 
 Blittersdorf
 Sent: Sunday, September 15, 2013 7:11 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Off Grid LP Gen advice
  
 Dave,
 I have sold 8 Eco-Gens so far and first impressions are great.  I wasn't 
 aware of the govt funded research but it makes sense.  I have one installed 
 on top of Herrick Mtn doing an average of 4 hours a day backing up a 
 transmitter site.  This winter will be the test.  So far we have almost 500 
 hours on it (first oil change coming up) and no problems.  This is a remote 
 site with only  snowmobile access in winter.  The gen is doing great on fuel 
 economy. About .7 gph at 2300 watt load.
  
 John Blittersdorf 
  
  
  
 I
 S
  
  
 Tn
  
 
 
 Sent from my iPhone
 
 On Sep 14, 2013, at 8:56 PM, Gary Willett g...@icarussolarservices.com 
 wrote:
 
 Ditto Chris's comment. The EcoGen was designed by Generac with research 
 funded by the Propane Council from the ground-up as an off-grid propane-only 
 generator used to charge batteries.
 
 Regards,  Gary
 
 On 9/14/13 1:44 PM, Chris Mason wrote:
 Generac Ecogen is your best choice. It was specifically designed for the long 
 runs associated with charing batteries for off-grid work.
  
 
 On Sat, Sep 14, 2013 at 11:58 AM, Dave Palumbo d...@independentpowerllc.com 
 wrote:
 Wrenchsters,
  
 Looking for a good quality, long lasting, LP gas genset for my off grid 
 rental house. 6 to 8kW. Full power at 120Vac would be nice. In the past some 
 have recommended a Coleman off grid model as I remember. I’m also wondering 
 how the smaller Kohlers, and the like, have been holding up for off grid use 
 over the past few years.
  
 This for northern Vermont where even with C/8 PV to battery charge rate we 
 need to run the generator about 250 hours per year as the cloud cover is 
 dense for weeks at a time.
  
 Thanks,
  
 Dave Palumbo
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
  
 -- 
 Chris Mason
 President, Comet Systems Ltd
 www.cometenergysystems.com
 Cell: 264.235.5670
 Skype: netconcepts
 
 
 
 ___
 List sponsored by Home Power magazine
  
 List Address: RE-wrenches@lists.re-wrenches.org
  
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
  
 Check out participant bios:
 www.members.re-wrenches.org
  
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Advice Needed: L16 Accident! Damage Questions

2013-09-14 Thread jay peltz
Hi Jeff,

All of the advice is just that advice.
There is no way to know if there has been damage, regardless of what has 
happened in other situations.
There are no guarantees you can give your customer


I'm not advocating not using them, only that I would only use them with caution 
and careful observation for the first days/weeks to see if any problems appear.

Jay 

peltz power




On Sep 13, 2013, at 8:45 PM, Jeff Clearwater wrote:

 Thanks folks - it's apparent from the feedback that my post was not presented 
 in a clear way.  I wasn't asking about how to proceed with the customer 
 liability wise. There is zero issue there. .  We are best of friends and they 
 know its all their fault. 
 
 I was merely asking on a technical level what to advise them in terms of what 
 to expect from batteries that have had a fall in terms if shock to the 
 plates. 
 
 Is the Trojan rep listening?  How resistant are RE-Bs to a fall on their side 
 assuming acid levels are good?  
 
 And Am I right to assume that a more violent fall capable of cracking posts 
 is likely to have caused damage deeper? 
 
 Sent from my iPhone
 
 On Sep 13, 2013, at 11:13 AM, Allan Sindelar al...@positiveenergysolar.com 
 wrote:
 
 Jeff,
 I'd offer to order replacement cells for the customer, for as many of the 16 
 as the customer wishes to replace - let them decide. As you have already 
 made your margin on the sale, you could offer the replacements at a 
 substantial discount just to cover your time and expenses. I'd decline 
 offering repairs or even more than cursory advice that might come back to 
 bite you years from now when one or more cells fail prematurely.
 
 Re loss of acid: of course the voltage is holding fine - the amount of 
 electrolyte in the cell doesn't affect voltage. But you are guessing at the 
 amount of H2SO4 to add. A bad estimate could also come back to haunt you 
 down the road.
 Allan 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sundanzer questions

2013-09-12 Thread jay peltz
Hi Allan

I've had mine for 4-5 years now, no issues
12 cuft, freezer, running on DC

Jay

Peltz power




On Sep 11, 2013, at 12:27 PM, Allan Sindelar al...@positiveenergysolar.com 
wrote:

 Wrenches.
 We have sold four Sundanzer chest refrigerators or freezers over the last ten 
 years. All have worked without a hitch. Today I got a call from a customer 
 asking about DC refrigerators; when I mentioned Sundanzer, she stopped me. 
 She said the reviews on Amazon convinced her not to buy one. I checked the 
 reviews; of nine (among all four chest models), I read five 5-star, one 
 4-star, one 3-star, and two 1-star. The 1- and 3-star reviews were about both 
 failure of the units and lack of support from the manufacturer.
 
 So I'm curious: who has sold many of these? How have they performed? And what 
 has been your experience with dealer support?
 Thanks, Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified PV Installation Professional 
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc., a Certified B CorporationTM
 3209 Richards Lane
 Santa Fe, New Mexico 87507
 505 424-1112 office 780-2738 cell
 www.positiveenergysolar.com
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Who has the best overall solar racking solution?

2013-09-11 Thread Jay Peltz
Sub question/

Best ballasted flat roof rack?

Jay
Peltz power

Sent from my iPhone

On Sep 10, 2013, at 1:04 PM, James Rudolph jamesrudolp...@gmail.com wrote:

 Greetings Fellow Wrenchies,
 With all the racking options out there today, are there any stand outs in 
 terms of quality and installation time.
 We are in the process of evaluating our racking system and with all the 
 options its a little mind boggeling.
 
 Mahalo in advance!
 
 
 
 
 James B Rudolph
 Heleakala Solar 
 Director of Construction
 NABCEP Certified PV Installer
 Licensed ES Electrician
 
 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Search mode

2013-09-08 Thread jay peltz
HI Jesse,

Can you tell us which model inverter?

jay

peltz power
On Sep 8, 2013, at 3:38 PM, Jesse Dahl wrote:

 Hello,
 
 A friend of mine in the woods just put in a new xantrax inverter and is 
 having a search mode problem. They can't get 25W search mode to work and are 
 stuck with using the 50W setting. So they've had to put a few incandescents 
 in to make this setting work. His calls to tech support have been less then 
 helpful. 
 
 Advice I can pass on?
 
 Thanks as always!
 
 Jesse

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PSX-240 wiring question

2013-09-07 Thread Jay Peltz
Hi Allan

I have had to address this issue before. 
My two choices are either a mechanical  disconnect or a relay ahead of the 
Tformer. 

Whether its a cool custom interlock,simple switch or relay,  you get the fun 
call on that one. 

And yes if there was room for an addition 60 amp breaker in the box it would 
really help. 

Jay
Peltz power

Sent from my iPhone

On Sep 7, 2013, at 11:56 AM, Allan Sindelar al...@positiveenergysolar.com 
wrote:

 Wrenches,
 Here's a small issue on which I need help. It concerns the best functional 
 way to wire up an Outback PSX-240 balancing autotransformer for a specific 
 purpose.
 
 I have somehow succeeded in transferring the wiring diagram on page 6 of 
 Outback's PSX-240 installation manual into this message. This is for a 
 step-down/generator balancing function. 
 
 The situation: 8kW 240V AC generator serving an older system with a single 
 Trace SW4024. The 240V from the generator enters the PSX240 as wired 
 according to the diagram. The primary role of the generator is to provide 
 occasional backup charging to the batteries through the inverter. The 
 specific issue is that the client also wants 240V AC from the generator to be 
 available to a single shop receptacle to run a stationary woodworking tool. 
 The generator is not large enough to both run the tool and charge at full 
 (33A @120V AC / 120A @24V DC) AC2 amps in setting, and we don't want to 
 reduce the charge rate, as it's currently ideal for the new HUP industrial 
 flooded batteries.
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Conext inverter

2013-08-28 Thread jay peltz
HI Allan,

I think you have me here.

I was under the impression that this is just a new name for what is the old XW 
series?


jay

peltz power


On Aug 28, 2013, at 5:24 PM, Allan Sindelar wrote:

 Wrenches,
 When a new product comes out I usually wait for a few reviews on this list 
 before using it. That would have been the case with the new Schneider Conext 
 series, the low-cost 120/240 SW off grid unit. But I was talking with Tom 
 Carpenter of Midnite about other issues and he happened to speak quite highly 
 of the unit he was bench testing. So I'm asking: has anyone worked with this 
 unit yet? What's the feedback, please?
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified PV Installation Professional 
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc., a Certified B CorporationTM
 3209 Richards Lane
 Santa Fe, New Mexico 87507
 505 424-1112 office 780-2738 cell
 www.positiveenergysolar.com
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] cool fan

2013-08-27 Thread jay peltz
Hi Todd

Is the relay cycling or could it be the fan is having issues?
Did you try manual on?

On a side note. For the turbo units in warm areas, I replace the fan with a 
high output AC fan controlled with relay, really helps. 

Jay

Peltz power. 






On Aug 26, 2013, at 10:21 PM, toddc...@finestplanet.com wrote:

 wrenches...
  
 im having a vexing problem with an outback system and cannot seem to get any 
 help from outback... so, im posting this here in hopes some wrench knows more 
 about the 'cool fan' option than i do.
  
 this is a sealed gtfx2524 system... so it has the 'turbo fan' connected to 
 the aux output which is set to coolfan. i called tech support and the guy i 
 spoke with was unable to find much about this so is sending out a control 
 board as kind of a blind, i hope this fixes it solution... but, before i 
 unwire and dismount the inverter for the second time (the internal fan died 
 after 6 months of use), i thought id write and ask someone else.
  
 here are the symptoms and parameters:
 the grid tied unit is in a greenhouse so it gets hot in there (a couple of 
 days ago it was 95 f).
 at max, the unit processes around 1100 watts/minus local loads so sells 
 around 900 to 1000 watts. the lowest (hottest) temp counts i have seen are:
 air (xmfr) 88
 fets 132
 caps 136
  
 during this heat event i saw the unit throttling back on selling, as the dc 
 voltage went from 26 (sell voltage default set point) to 28, where the charge 
 controller started throttling back... so i know it was running hot. during 
 this the coolfan would cycle... on for a second or 2 and then off again for 
 an equal time. when i set the aux control from 'auto' to 'on' the fan comes 
 on and stays on... well, mostly. it still cycles on and off, but less 
 frequently.
  
 does anyone have access to the temp counts for:
 when the coolfan is supposed to turn on and off 
 when the unit starts throttling back on selling due to overheating 
 when the unit will totally shut down from overheating
  
 another strange thing is when i set the aux control from coolfan to vent or 
 diversion, and program the parameters so the fan would be on (ie: vent fan / 
 diversion on above 24 volts with the battery voltage at 26+) the fan does 
 not come on.
  
 guesses? will replacing the control board change anything? any help is 
 appreciated.
  
 thanks, todd
 
 
 
 Sent from Finest Planet WebMail.
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] cool fan

2013-08-27 Thread jay peltz
Hi Todd,

As the fan won't even stay on, when ON, then the board being bad is a good 
choice

As to the AC fan, I wasn't suggesting an external thermostat, but just a larger 
cfm fan

Jay




On Aug 27, 2013, at 9:11 AM, toddc...@finestplanet.com wrote:

 thanks for the ideas jay!
  
 the fan comes on and off with the aux output led on the board where the 
 in/out ac wires connect, so i do not believe this is an issue with the fan.
  
 as i mentioned below:
  
 when i set the aux control from 'auto' to 'on' the fan comes on and stays 
 on... well, mostly. it still cycles on and off, but less frequently.
  
  
 i guess i could mount an external thermostat on the fx case and have this 
 control a relay to operate the 'cool fan', but id really like to figure out 
 why the unit is not performing as it is supposed to... and why outback's tech 
 support seems so deficient these days. shouldnt someone have access to the 
 code and be able to give me the temp counts for cool fan on/off and when the 
 unit throttles back on selling from over-temp conditions?
  
 todd
  
  
  
  
  
 On Tuesday, August 27, 2013 8:47am, jay peltz j...@asis.com said:
 
 Hi Todd
 Is the relay cycling or could it be the fan is having issues?
 Did you try manual on?
 On a side note. For the turbo units in warm areas, I replace the fan with a 
 high output AC fan controlled with relay, really helps.
 Jay
 Peltz power.
 
 
 
 
 On Aug 26, 2013, at 10:21 PM, toddc...@finestplanet.com wrote:
 
 wrenches...
  
 im having a vexing problem with an outback system and cannot seem to get any 
 help from outback... so, im posting this here in hopes some wrench knows more 
 about the 'cool fan' option than i do.
  
 this is a sealed gtfx2524 system... so it has the 'turbo fan' connected to 
 the aux output which is set to coolfan. i called tech support and the guy i 
 spoke with was unable to find much about this so is sending out a control 
 board as kind of a blind, i hope this fixes it solution... but, before i 
 unwire and dismount the inverter for the second time (the internal fan died 
 after 6 months of use), i thought id write and ask someone else.
  
 here are the symptoms and parameters:
 the grid tied unit is in a greenhouse so it gets hot in there (a couple of 
 days ago it was 95 f).
 at max, the unit processes around 1100 watts/minus local loads so sells 
 around 900 to 1000 watts. the lowest (hottest) temp counts i have seen are:
 air (xmfr) 88
 fets 132
 caps 136
  
 during this heat event i saw the unit throttling back on selling, as the dc 
 voltage went from 26 (sell voltage default set point) to 28, where the charge 
 controller started throttling back... so i know it was running hot. during 
 this the coolfan would cycle... on for a second or 2 and then off again for 
 an equal time. when i set the aux control from 'auto' to 'on' the fan comes 
 on and stays on... well, mostly. it still cycles on and off, but less 
 frequently.
  
 does anyone have access to the temp counts for:
 when the coolfan is supposed to turn on and off 
 when the unit starts throttling back on selling due to overheating 
 when the unit will totally shut down from overheating
  
 another strange thing is when i set the aux control from coolfan to vent or 
 diversion, and program the parameters so the fan would be on (ie: vent fan / 
 diversion on above 24 volts with the battery voltage at 26+) the fan does 
 not come on.
  
 guesses? will replacing the control board change anything? any help is 
 appreciated.
  
 thanks, todd
 
 
 
 Sent from Finest Planet WebMail.
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 Sent from Finest Planet WebMail.
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Xantrex XW system stability

2013-08-22 Thread Jay Peltz
Hi Kevin

Given how that system works, could you install the CC's on their own?

Ie use a seperate scp to keep track of data?

Jay
Peltz power. 

Sent from my iPhone

On Aug 22, 2013, at 10:18 AM, Kevin Pegg kp...@energyalternatives.ca wrote:

 Hello Wrenches, 
 
 Curious how others are finding the stability of larger Xantrex XW 
 deployments? We have an installation with 12 Xanbus devices (4 x XW6048, 6 x 
 XW-MPPT60, 1 x AGS, 1 x SCP) and it keeps crashing. Power cycle the whole 
 system and it's fine for a few weeks and then it crashes again. 
 
 I find with smaller deployments under 5 Xanbus devices the stability is much 
 better, but still get the occasional customer call with a system gone haywire 
 and a power cycle fixes. 
 
 This particular installation is in the high arctic darn near the north pole 
 and sending a tech up there next week to resolve. Needless to say, it's an 
 expensive ordeal to get up there. 
 
 Kevin
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] MC4 center conductors

2013-08-19 Thread jay peltz
PV-cables.com


Jay




On Aug 19, 2013, at 4:10 PM, penobscotso...@midmaine.com wrote:

 Hi all,
   Does anyone have a source of just the center conductor (small metal
 inserts) for MC4 connectorsI seem to have accumulated a lot of
 female - plastic without the associated crimpable center conductor
 
 Daryl
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback efficiency?

2013-08-18 Thread jay peltz
Hi Ray,

#1, I don't see any improvement. But then I find it rarely used anymore with 
many small loads ( cell phone chargers etc), coupled with cyclic loads and 4 
watt LED's etc.
Its got to be a really small system to have this be active.
I find that if people really want to use this that I'll wire up the remote 
on/off and they can use that from their bed at night.

#2.  It depends on how they measure the efficiency.  Since the no load is 
around 20 watts, if you have a 20 watt load, that makes a efficiency of like 
50%, not including the inverter loss's of 6-10% which isn't really helpful in 
any sort of calculations.
I usually use 90% ish ( I think they publish 94% as peak eff.)  as my INV 
design efficiency ( sometimes it'll be lower, sometimes higher), and then add 
in the idle watts x 24 hrs day.

Hope this helps,

jay

peltz power

On Aug 18, 2013, at 3:01 PM, Ray Walters wrote:

 I have a couple of Outback questions.  On my load analysis sheet, I include 
 20 w x 24hr/ day for the inverter's no load draw.
 In the past I had very poor luck with the search mode on most inverters, and 
 found that when I adjusted it so that it came on with efficient lighting, 
 that the no load draw was still 15 watts.  I've just taken to disabling 
 search mode, and add more modules.
 So question 1: has the search mode been improved in the past 5 years?
 question 2:  Is the no load draw most of the efficiency losses, so could I 
 set inverter total efficiency to say 98%, while keeping the 480 wh/ day  
 inverter draw?  I don't want to overstate or understate the inverter losses.
 
 Thanks,
 
 -- 
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV Assist

2013-08-16 Thread Jay Peltz
Hi William 

Thx helps a lot. 
I can only say how I do it. 
I'll give the client some options, including the change of appliances and 
usually the price difference makes the sale one way or the other. 

Funny reminds me of the old days, only with much smaller loads/$. 

Good luck

Jay



Sent from my iPhone

On Aug 16, 2013, at 12:49 PM, William Miller will...@millersolar.com wrote:

 Jay:
  
 There are four systems in question.  In three the loads are year round and 
 one is summer only AC loads.  The year round loaded systems have loads day 
 and night.
  
 One is a highway maintenence station with at least 4 residences.
 One is a family compound with two homes with electric ranges,  water heaters, 
 AC units (I know its stupid, lord knows I've tried to convince them to change 
 appliances.)
 One is an animal rescue operation with heater loads.
 One is a large home with 5 very small, very new, very sophisticated and 
 frugal AC units
  
 I know it is silly to move these loads off-grid, but people do it and they 
 will hire someone to work on the systems.  It may as well be me, doing the 
 best I can to use the resources as wisely as possible.
  
 William
  
 PS:  It always happens like this:  I get a call from a client with problems.  
 Well, of course their expensive battery bank died and it died because of 
 wasteful appliances.  The prescription is a new, expensive battery bank and, 
 at the same time, new, expensive, efficient appliances.  They complain can't 
 afford both and they have to have the batteries, so that is what they get.  
 Repeat every two years.  Sad
  
 Wm
  
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz
 Sent: Friday, August 16, 2013 12:22 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] PV Assist
 
 Hi William
 
 I feel it's impossible to discuss without more specifics. 
 
 For example if the extreme loads are only every ( just run the genny) so 
 often vs seasonal ( maybe AC coupling makes more sense vs cycling a extremely 
 expensive battery 4 x day),  vs year round vs what is do able etc
 
 I would be curious to know what some of the parameters are, as I'm sure 
 others as well
 
 Jay
 
 Peltz power. 
 
 
 
 
 
 Sent from my iPhone
 
 On Aug 16, 2013, at 10:53 AM, William Miller will...@millersolar.com 
 wrote:
 
 Friends:
  
 We have been receiving a flurry of requests for design of off-grid systems 
 where the loads are enormous, relative to normal off-grid requirements.  It 
 is obvious that the size of PV and battery arrays to power these loads is 
 beyond what is practical.  We have dubbed these systems Generator/battery 
 with PV assist, or PV assist for short.
  
 These systems will cycle batteries multiple times per day.  It is my 
 understanding that the extra battery cycels will shorten battery life.  
 Since generator run is expected, we are willing to increase generator run 
 time in order to prolong battery life.
  
 The parameters I suggest are an aggressive load start and a very high 
 battery start parameter.  This will prevent deep discharge of the battery 
 bank.  I know shallow discharge is not the norm, but I don't believe shallow 
 cycling isa problem as long is it as at the top of the voltage window, 
 i.e. the batteries achieve absorption at least once per day.
  
 We know a load start ciuld result in an abbreviated run time, curtailing 
 absorption period, but we are assuming there will be a battery votage start 
 at least once per day allowing full absorption.
  
 Has anyone else considered these issues, and what conclusions did you make
  
 I am looking forward to a spirited discussion as usual.  I throuroughlyenjoy 
 and beneift from them, even thought the advice is usually conflilcting.  
 Thanks in advance.
  
 William Miller
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive

Re: [RE-wrenches] Hawker versusu MK

2013-08-13 Thread jay peltz
I agree with Daryl and Tump

And would add Trojan IND as an option to the Rolls and made in SoCal

Also most of the industrial battery folks make 2v cells. 

Jay
Peltz power. 




On Aug 13, 2013, at 4:55 AM, penobscotso...@midmaine.com wrote:

 I second Tump's experience!
 
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design
 
 
 I install large battery banks ALL the time. We DO NOT use any battery that
 is incased in a metal enclosure.
 REAL pain to move, cells DO go bad  when they do its a real pain to bring
 the engine hoist to remove them. Hard to keep the cases from leaking 
 rusting.
 We DO use the Surrette 2 volt cells in the dual container exclusively.
 These are rated as a containment vessel,  much easier to move. In the
 event when a cell does go bad, use a jumper to bypass the bad cell,
 operate w/ a lower LBCO setting leave the CC settings the same, while
 waiting for replacement.
 1700 AH -2400 AH.
 By the time you have the tractor/back hoe on site, my 2 volt cells are up
 n running! E mail me off list and I can give you a few tricks to move
 them.
 On Aug 13, 2013, at 3:28 AM, William Miller wrote:
 
 Friends:
 
 We are shopping for industrial, flooded, lead acid batteries.  We are
 considering 12 volt packages in the 1800 AH range.  Under consideration
 are:
 
 Hawker 12-25W-23S at 1705 AH or MK 106M1033STB at 1896 AH.
 
 Have any of you had experience with either, or recommend another option?
 
 As always, I am extremely grateful to all of you for the limitless
 wisdom offered.
 
 Sinceerly,
 
 William Miller
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 t...@swnl.net   www.SWNL.net
Solarwinds Northernlights
   Serving Mid Coast Maine  Northern California
 207-832-7574   Cl. 610-517-8401
  Blair TUMP May
     MAINE'S CHARTER 
  NABCEPCertified PV Installer
 
    MAINE'S CHARTER 
  Trace Xantrex Certified Dealer / Installer
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Hawker versusu MK

2013-08-13 Thread jay peltz
Hi Dick,

Best trick I ever learned for these metal cased is to build  a 
wheeled base with steel wheels.  
Yea, still have to get them onto the base, but then its easy.

Also when I  use metal cased batteries I like to have them with removable 
series interconnects
not the welded type. 

Interesting to hear the comments on the Rolls shipping.  I've seen that problem 
myself, but 
didn't realize that it was so common.


jay

peltz power
On Aug 13, 2013, at 9:31 AM, Richard L Ratico wrote:

 I've got two Hawker installs out here, a 48 Volt and a 24 Volt system. Both 
 are
 going on 6 years or so. Clients are happy, I'm happy. It does resemble work to
 move and place them. We typically use Egyptian techniques when heavy 
 equipment
 isn't available or appropriate. Inclined plane, big pry bars, rollers, come
 along, block  tackle. It's kind of fun to try to outsmart the mass. It's
 interesting to experience gravity's effect on lead, atomic weight 207.2. Glad
 it's not Uranium at 238. Thankfully, we've not had to replace a cell. That
 always sucks, regardless.
 
 If I remember correctly, the steel cans had welded seams. The cans make the 
 use
 of insulated tools even more important. Should you ground the cans???
 
 Speaking of replacing cells. I looked at a 5 year old bank of 8 Rolls L16s 
 this
 weekend. Two of the batteries had a dead cell. This in a bank that had a 
 single
 battery replaced at 6 months or less because of a bad cell. 
 
 I've also got a 7 year old bank of 12 Surrette / Rolls 2 Volt units installed.
 The only problem so far was on day one when they arrived. They were shipped 
 on a
 single, narrow, beat up pallet. Some had obviously tipped over in transit and
 had lost a considerable amount of electrolyte. Northern Arizona Wind  Sun
 user's forum has posts reporting similar experiences. 
 
 I dread receiving expensive pallets of batteries and modules from shippers. 
 High
 percentage of damage. Steel cans instead of plastic wrap is worth thinking
 about.
 Hope this doesn't just muddy the water.
 
 Dick Ratico
 Solarwind Electric
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS -1500w

2013-08-11 Thread jay peltz
hi Jeremy,

Sorry to pull teeth here, but which inverter is it?

jay

peltz power
On Aug 11, 2013, at 11:08 AM, All Solar wrote:

 It's a sine wave unit and the manufacturer has been very involved in this 
 case. The owner is going to try a UPS that he already owns and will bring it 
 out the next time he travels back. 
 
 Sent by Jeremy's iPhone. Sorry for typos and shorthand!
 
 On Aug 9, 2013, at 6:16 PM, RE Ellison reelli...@gmail.com wrote:
 
 I assume the easy choice of changing the coffee pot isn't going to happen?
 
 What inverter does it happen to be, Although sometimes weird stuff like this 
 happens with inverters of all makes.
 
 Back from my days of being an APC dealer most UPS's are modified square wave 
 
 Bob ellison
 
 
 Bob Ellison
 
 On Aug 9, 2013, at 4:00 PM, All Solar allso...@scswifi.net wrote:
 
 Looking for recommendations for a reliable UPS for a problem load that will 
 not run off the homes inverter
 The load is 1200 w max  120v
 Thanks in advance
 
 Jeremy Rodriguez
 All Solar
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] UPS -1500w

2013-08-09 Thread Jay Peltz
What's the load, the inverter?

Jay
Peltz power

Sent from my iPhone

On Aug 9, 2013, at 1:00 PM, All Solar allso...@scswifi.net wrote:

 Looking for recommendations for a reliable UPS for a problem load that will 
 not run off the homes inverter
 The load is 1200 w max  120v
 Thanks in advance
 
 Jeremy Rodriguez
 All Solar
 
 Sent by Jeremy's iPhone. Sorry for typos and shorthand!
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Relay for 48v Vent Fan

2013-08-08 Thread jay peltz
HI Rich,

Grainger will have 12v coil relays that will switch 48v.


jay

peltz power
On Aug 8, 2013, at 4:49 PM, Rich Nicol wrote:

 Hello Wrenches,
  
 Does anyone have any advice about what to use for a relay to power a 48 volt 
 Zephyr battery vent fan using the 12 volt auxiliary output from the Midnite 
 Classic Charge controllers. The fan only draws 6 watts but my problem is the 
 48 volt side of the equation. A supplier has recommend  a double pole/double 
 throw relay rated for up to 30 amps at 24 volts wired in series. I’m curious 
 if anyone knows of a relay rated for 48volts (actually higher voltage since 
 the fan is signaled to come on when the battery reaches gassing voltage) that 
 would work in this application or if there is widespread agreement that the 
 24volt rated relay would work fine since we are requiring only minimal 
 current and spreading between two contacts.
 As always, your input is greatly valued!
 Thanks,
 Rich
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SW AGS

2013-08-07 Thread jay peltz
HI Eric,

Sounds like the stop absorb might have been enabled.
This will stop the AGS when the battery volts reach absorb setpoint.

But has no impact if starting the generator manually.

jay

peltz power



 Sounds like you talked to the right guy, that's his info...except that he 
 has, according to what he told me, an SW not an XW. I'm assuming he's maybe 
 at 50% capacity on his original 1260Ah bank based on everything he told me 
 this morning. He did say that his bank will last him through the night and 
 that he has some pretty hefty air conditioning loads. He also said he had 
 equalized in the past but not in the last 18 months. I'm just not convinced 
 that his batteries are shot. But all this battery talk may be beside the 
 point if he's not experiencing the same on/off cycling problem when he 
 manually starts the genny, right? That is, assuming the disco settings remain 
 in effect regardless of start mechanism. Thanks for indulging me tocayo.
  
 Eric
 SunHarvest
 001.530.798.3738 (Cell)
 - Original Message -
 From: eric.bent...@schneider-electric.com
 To: RE-wrenches
 Sent: Wednesday, August 07, 2013 12:54 PM
 Subject: Re: [RE-wrenches] SW AGS
 
 
 Hi Eric, 
  Sounded like bad batteries to me also (I think he called in this AM). He has 
 (2) XW6048 units that are 
 capable of 200ADC between them, and he also has 1260Ah of flooded capacity. 
 DC Start V is set for 46.5V, so if we assume he was close to 50% 
 discharge (depending on load), it should take almost 2 hours to reach the 
 bulk voltage (80% replaced). His batteries were ramping up to bulk 
 in just a couple of minutes, meaning the batteries were not absorbing the 
 charge. I have heard varying opinions on the symptoms of sulfation, 
 but it does sound like a battery issue (5 yrs old). He was advised to 
 equalize to try and recover them (he has never done this), or replace them. 
 Rgds, 
 
 _
  
 
 Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
 |   Technical Support Representative 
 Phone: +(650) 351-8237 ext. 001#  |   
 Email: eric.bent...@schneider-electric.com  |   Site: 
 www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
 Livermore, CA 94551 
 
 Mail Attachment.jpeg
 *** Please consider the environment before printing this e-mail 
 
 
 
 From: SunHarvest e...@harvesthesun.com
 To:   RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: 08/07/2013 12:39 PM
 Subject:  [RE-wrenches] SW AGS
 Sent by:  re-wrenches-boun...@lists.re-wrenches.org
 
 
 
 
 I read through the archives on the XW AGS thread but have a query on behalf 
 of a customer with an SW AGS issue. I'm heading out to the remote site 
 tomorrow and would like, if possible, to show up knowing what I might be up 
 against. 
   
 The customer recently replaced his AGS for his two SW 6048s and then upgraded 
 his firmware a week later. He reported that his problem with the AGS began 
 after firmware upgrade. Here's the particular issue: 
   
 AGS will try to start the 15.8kW Multi-Quip genny due to low battery voltage 
 (event 306 DCV start). After about 5 minutes the AGS will stop the genny due 
 to battery absorption level reached (event 313 ABS stop). The AGS will go 
 through this event 306/313 cycle on and off until the homeowner shuts down 
 the AGS. To me this sounds like bad batteries. But, the homeowner says this 
 cycling does not occur when he manually starts the generator. This doesn't 
 sound like a complicated problem but so far I'm unfamiliar with the SW AGS. 
 So, I would greatly appreciate any insight you guys can offer me. 
   
 Thanks!! 
   
 Eric
 SunHarvest
 001.530.798.3738 (Cell) 
 
 __
 This email has been scanned by the Symantec Email Security.cloud service.
 _
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE

Re: [RE-wrenches] retail price lists

2013-08-06 Thread jay peltz
Hi Tom and all

Thanks for the price list. 

I'm sorry, I guess my question should have been more clear. 

Why is it that some of our manufacturing companies don't publish retail price 
lists, but actually have them?

There must be a reason? ( however dopey)

Thanks

Jay



On Aug 6, 2013, at 7:30 AM, Tom Duffy t...@thesolar.biz wrote:

 Jay
 
 I have sent you an OutBack retail price list in a separate e-mail let me know 
 if you don't get it.
 
 Tom Duffy
 Senior Solar Design Engineer
 
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810 
 Grid tie sales 888-895-7847 
 Off Grid sales 888-895-4058 
 Other Product Sales 888-895-9612 
 Central America Sales (Panama) 507-6-126-1253 
 Shipping and Receiving 888-895-6497 
 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] RS 232/tristar

2013-08-05 Thread jay peltz
Hi All,

Any special issues with using a RS232 to USB for programing the Tristar?

IE will any USB/RS232 adapter do?

thanks in advance,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] retail price lists

2013-08-05 Thread jay peltz
Anybody know the logic on why some manufacturers don't publish a retail price 
list?
For example, Outback?

thx,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC coupling Sunpower?

2013-07-31 Thread jay peltz
Hi Corey,

Did you mount the SS relays to a good heat sink with heat compound?
They are quite sensitive to heat damage and also like a lot things 
optimistically rated.
I use a 2X oversize ratio for SS relays if they are used very much at all or 
for longer periods of time.

And I think  you are correct to install a back up to the frequency shift that 
may or may not work.


jay

peltz power


On Jul 31, 2013, at 11:24 AM, Corey Shalanski wrote:

 Mac,
 
 We have installed about ten AC coupled Magnum systems over the past year.
 
 Overcharge protection is accomplished by frequency shift, but Magnum 
 recommends an auxiliary form of battery management. The cheapest way to do 
 this is to program the relay driver on the Magnum advanced remote control 
 (ARC) to open/close a solid state relay at specified battery voltage 
 setpoints - similar to what Kelly mentioned. Unfortunately the cheapest way 
 sometimes comes back to haunt us in the form of unanticipated extra costs. We 
 had two customer callbacks indicating their inverter had mysteriously shut 
 down - site visit revealed a fried relay in each case.. so I would recommend 
 at least investing in a good quality relay if you choose this route.
 
 One other thing we have learned is that not all grid interactive inverters 
 are compatible with the Magnum inverters. Specifically Power One Aurora 
 string inverters cannot seem to synchronize in off-grid mode - we have had to 
 switch out Auroras on two projects because of this. We have had no such 
 synchronization issues with SMA inverters so far.
 
 --
 Corey Shalanski
 Joule Energy
 New Orleans, LA
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback AC coupling Sunpower?

2013-07-30 Thread Jay Peltz
Hi ray

Magnum does have a way to do it 
Theirs is a bit different, but all the data is on their web site

Jay
Peltz power

Sent from my iPhone

On Jul 30, 2013, at 4:23 PM, Ray Walters r...@solarray.com wrote:

 The Outback rep got me some good info, and I'm liking the Radian with the 
 Remote controlled breaker to control the GT inverter when the grid is out.  
 I've heard of quite a few problems related to the Sunny Island frequency 
 controlled system.
 My question is can off grid inverters like the Magnum be AC coupled?  I'm 
 trying to get the price down, and still handle the 240 vac input from the GT 
 inverter.
 I penciled out the Radian and I was topping $10k before installation.   This 
 customer is hoping for a solution under $10k, and closer to $5k if possible.  
 I think an elegant lower cost solution for Grid tie with battery back up is 
 in order.  A Radian Lite?
 For backup, it could even be mod sine, as it wouldn't be much worse than 
 generator power or the average UPS setup.
 
 
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Tri-Star MPPT

2013-07-23 Thread jay peltz
Hi Eric,

While agree with most all your assessments, 
Can you please elaborate on the sulfation causes the voltage not to climb?

This is quite counter to what I have seen and what the battery people say?

Thanks

Jay

Peltz power

Sent from my iPad

On Jul 23, 2013, at 2:48 PM, eric.bent...@schneider-electric.com wrote:

 
 Hi William, 
 
  If the SG was 1.26, of course the battery voltage would increase 
 quickly to 30V (which is high for warm weather, BTW). 
  It has been my experience that sulfation causes the voltage NOT to climb. 
 Especially when you have a very large bank, and a 
  relatively small amount of solar. 
  Sometimes it is necessary to reduce the bank size into smaller sets to 
 equalize them and recover their performance. 
 This method of reducing bank size is also effective to compare performance 
 and weed out a potentially bad battery. 
  Systems that have a lot of capacity, with a relatively small amount of 
 charge current usually creates problems, because 
  the load demand exceeds solar production. 
  This results in batteries that operate with partial SOC, which is when 
 sulfation is most prevalent. With (8) L16s, you have approx 
  800Ahrs of capacity (24V bank). It would take significantly more than 8A of 
 charge current to properly care for a bank that size. 
 
 Rgds,
 _
  
 
 Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
 |   Technical Support Representative 
 Phone: +(650) 351-8237 ext. 001#  |   
 Email: eric.bent...@schneider-electric.com  |   Site: 
 www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
 Livermore, CA 94551 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Trojan L-16s

2013-07-22 Thread Jay Peltz
Hi Tom

Where did you get the .42 from?

Jay
Peltz power 

Sent from my iPhone

On Jul 22, 2013, at 11:04 AM, Tom Duffy t...@thesolar.biz wrote:

 Drake
 
 Keep the absorb rate recommended for the CC. The trimetric strays over time 
 and will become accurate again when you overcharge (equalize)
 
 The math:
 Amp hours of battery @ 20 hour rate divided by max charge available in amps, 
 from whatever you using to charge (solar or inverter/charger)
 Times .42 = absorb time in hours 
 
 i.e. your system 980 watts,  980 divided by 28.8 (average volts) = 34 amps 
 max charge
 370 AH divided by 34 = 10.88 X .42 = 4.57 round up to 4.6 hours absorb time 
 for the CC
 Your inverter VFX3524 max charge 85 amps... 370 divided by 85 = 4.35 X .42 = 
 1.82 absorb time for the inverter/charger when running generator
 
 Tom Duffy
 Senior Solar Design Engineer
 
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810 
 Grid tie sales 888-895-7847 
 Off Grid sales 888-895-4058 
 Other Product Sales 888-895-9612 
 Central America Sales (Panama) 507-6-126-1253 
 Shipping and Receiving 888-895-6497 
 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
 Sent: Monday, July 22, 2013 10:04 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Trojan L-16s
 
 Hi Larry,
 
 I will bump up the absorb voltage to 29.6 V. How long do you think the bank 
 should stay in absorb at that rate?  The bank now seems healthy, with the bad 
 battery replaced.  It does accept charge, without going high prematurely.  
 The max charge rate from the array is around C/10. The system can also be 
 fast charged from a Honda 6500 inverter generator through the Outback 3524 
 VFX.
 
 We have a Trimetric meter on the system. The discrepancy between the percent 
 charge and the voltage is what demonstrated that we had a problem.
 
 Thanks,
 
 Drake
 
 
 
 At 09:30 PM 7/19/2013, you wrote:
 Hi Drake,
 
 It always concerns me when I hear that a battery bank reaches absorb 
 setting very quickly. It typically means one of two things: very few AH 
 were removed from the bank; the battery bank has sulfated cells due to 
 chronic undercharging. Far too often I find the latter to be true.
 
 Healthy batteries will accept current and hold the charge voltage down 
 with a fairly linear, slow climb to absorption voltage. Sulfated 
 batteries do not accept current well which allows voltage to climb 
 rapidly as the battery presents little load on the charging system. I'm 
 not sure how this plays into your original post about a bad cell but it 
 seemed worth mentioning.
 
 My opinion is to aggressively charge, by using higher voltage, large 
 flooded batteries. This is especially true when the PV system is 
 moderate or undersized. 29.6 volts is what Trojan recommends. You can 
 go as high as 32 volts on the L-16's but make sure the temperature 
 compensation is installed properly and working. You will use more water.
 
 One last comment, I highly recommend that ALL off grid systems have a 
 battery capacity monitor installed. It's kind of like flying an 
 airplane without a fuel gauge...it might not end in disaster.
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 On Jul 18, 2013, at 1:11 PM, Drake
 drake.chamber...@redwoodalliance.org wrote:
 
 Tom,
 
 The batteries usually reach absorb voltage shortly after the sun hits 
 the array. The reason the bank wasn't working correctly is that one 
 cell was dead in one of the batteries.
 
 I could increase the absorb time to 4.6 hours and the voltage to 29.6, 
 especially since the bank has a new battery. That is longer and higher 
 than I'd previously heard recommended.
 What would be the effect on water
 consumption?  How did you calculate the absorb time?
 
 Thanks,
 
 
 Drake
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http

Re: [RE-wrenches] Trojan L-16s

2013-07-18 Thread jay peltz
Hi Todd

Where can we find info and pricing?

Thanks

Jay 

Peltz power

 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Tape on modules for wire management

2013-07-10 Thread jay peltz
Hi all, 

You code wonks can help out here

I had a friend ask about an install he saw that used electrical tape to attach 
the PV wires to the modules, yep actually taping them to the back of the 
module. 

I'm having trouble figuring out if this actually breaks any codes and if so 
which ones

Then there is the whole ul,listing of the modules and is that approved?

Thanks,

Jay
Peltz power


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Square D QO breaker DC question

2013-07-09 Thread jay peltz
Hi Dan
I'm guessing the wire can handle the 100 amp if they are already running 60a. 
I've had QO breakers go bad, even ones not tortured like that one. 

The derate is interesting as it has to do with less atoms of air per volume. 
Less air, equals less cooling

Jay
Peltz power

Sent from my iPad

On Jul 8, 2013, at 10:07 PM, Dan Fink danbo...@gmail.com wrote:

 Esteemed Wrenches;
 
 A weird troubleshooting call today for my business partner DanB. I wish I had 
 been along if only for shock and awe and lessons learned.
 
 A nicely installed vintage 12VDC PV system that someone else designed and 
 installed over 10 years ago, we replaced a dead/frozen battery bank a month 
 ago. DanB went back today because customer reported low battery bank voltage.
 
 He found the PV input breaker tripped, a Square D QO 2-pole 60 amp. About 600 
 watts of PV 12vdc nominal on the roof. Reset the breaker, and a few minutes 
 later it was too hot to touch.
 
 So our working theory -- the 60a QO on *DC* has a 1.2x ampacity derate, which 
 puts 600w PV right at 60 amps instead of 50. There's also a bit of a high 
 altitude derate, which I don't understand at all. And during the battery 
 disaster last year bank voltage was certainly 11vdc or less, and was a bit 
 over 11vdc on DanB's arrival since the PV had not been charging. That puts us 
 at possibly 65.5 amps. The breaker was maybe just doing its job correctly, 
 though the heat was disturbing I am told.Or maybe it got damaged during the 
 battery disaster..both + and - were connected thru the 2 poles.
 
 In any case, our question --- due to my fuzzy memory and poor shopping 
 skills, we have a 100 amp QO 2 pole breaker in stock that needs a home, and 
 it'll plug right in. I have a nice tech bulletin from Schneider Electric 
 about DC ratings of their breakers that doesn't show that a 100a QO 2 pole 
 even exists, and a Schneider FAQ that says it'll work fine:
 http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=contentcountry=USlang=enid=FA125383redirect=true
 
 Any advice on this? We'd sure love to just drop by and pop in the new 100a 
 amp QO breaker instead of installing a whole new DC rated Midnite box. But we 
 don't want to leave a fire hazard either. With 15 years service on our local 
 volunteer fire department, It would be  rather embarrassing if a fix we 
 made to this old off-grid system caused a fire. ;-) We are aware of the 5k 
 AIR issue with these breakers, but the battery bank is small enough I don't 
 think it's quite up there, and information on AIR interruption from battery 
 manufacturers is hard to find..and of course it's a weird curve.
 
 Thanks in advance;
 
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342
 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generac Ecogen (was RE: generator suggestions)

2013-07-07 Thread jay peltz
Hi Kirk 

One trick I learned from my generator guy is to hook up the remote start to the 
manual on position
This bypass's the auto position and the extra load on the battery

Best I can tell only difference on the Koehler anyway is how fast it starts. On 
auto right now
On manual a few seconds delay. 

Jay

Peltz power

Sent from my iPad

On Jul 6, 2013, at 10:46 AM, Kirk Herander k...@vtsolar.com wrote:

 Alan and others,
  
 I have an off-grid customer looking at the Ecogen. Now that 6 months have 
 passed since your comments, can you tell us more of the pros and cons of this 
 unit?
 I read somewhere the phantom load of the controller (and charger?) is 20 to 
 50 watts total. Is it just the controller which needs to stay awake? Is there 
 a separate charger for the battery, meaning no alternator / rectifier direct 
 from the engine? Regardless,  it seems dumb to me that a generator designed 
 for off-grid would mandate a phantom load to operate. For that reason, it 
 seems no more appealing than the Kohler R series. Is there an on-board 
 hour-meter? Thanks. The brochure does not address these questions.
  
 Kirk Herander
 VT Solar, LLC
 dba Vermont Solar Engineering
 NABCEPTM Certified Inaugural Certificant
 NYSERDA-eligible Installer
 VT RE Incentive Program Partner
 802.863.1202
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
 Sent: Wednesday, January 30, 2013 3:21 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] generator suggestions
  
 Ray,
 Everything has changed. The Kohler 6.5RMY and the Onan 6.5 Commercial were 
 wonderful units, but also both flathead twins, eventually discontinued for 
 efficiency and emissions reasons, as I came to understand. Also, the American 
 residential market was (and remains) almost exclusively about home standby, 
 not off grid, and the major manufacturers went in that direction. Home 
 standby is a competitive market, and generators aren't expected to run for 
 many hours over their useful life, so internals can be cheapened and features 
 to make them more like a home appliance are added. Many of us have customer 
 horror stories about home standby units used off grid.
 
 I have written favorably about the Generac EcoGen here and in Home Power, as 
 it's pretty much currently the only under-10K unit designed for off grid use. 
 I have now had two at my home - we had a fire in May that took out an 
 outbuilding and the gennie, and I replaced it with the same model, because it 
 had performed well and there was nothing else to compete with it. Always 
 starts, minimal maintenance, exceeds its rated output on occasion, doesn't 
 require a separate enclosure, and is sealed against mice. Oh, and very quiet. 
 So far the only disadvantage is the need for either an AC feed for the 8W 
 phantom load to keep the controller awake, but a PV module and small 
 controller on the starting battery will handle that one of these days. It's 
 not just one of their standard units with different bells and whistles, but 
 has hardened valves, lower (2,500) rpm, longer maintenance intervals, and 
 other reliability features.
 
 I know all about Generac's otherwise-poor reputation, and am willing to stick 
 my neck out about this model, as I think it's the best we currently have in 
 this size range. My understanding is that the Propane Reliability Council (or 
 some similar organizational name) was involved with sponsoring development of 
 an LP gennie tough enough to handle off grid demands. They first approached 
 Kohler, who turned them down, and then worked with Generac (all this is 
 hearsay; don't quote me on it).
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
  
  
 On 1/30/2013 10:41 AM, Ray Walters wrote:
 Hi Randy and all;
 
 I definitely like the water cooled 1800 rpm machines too, but for regular off 
 grid homes, they just are way out of the budget.  We jumped on the inverter 
 generator band wagon for a while, but had the same load issues Allan 
 described.  (Microwave kicks the breaker, and you're running the genny for 
 hours for nothing)  Many customers have turned to the contractor portables 
 with equally disappointing results, but often they already have the genny, 
 and we just provide an inlet box and cord.  
 The Generac looks like a good idea, I wish Onan or Kohler would build one. 
 Kohler used to make a 6.5 Kw that fit the one inverter household fairly well.
 
 Ray Walters
 
 THeOn 1/30/2013 8:55 AM, Larry Crutcher, Starlight Solar Power Systems wrote:
 Randy, 
  
 I concur, the Cummins/Onan generators are built well and are reliable. They 
 provide a 1 year, 1000 hour

Re: [RE-wrenches] double insulated wire

2013-07-02 Thread jay peltz
HI Ray,

I agree and think that at least high voltage DC should have its own color code.
Labels go away, but wire colors are forever.

thanks,

jay

peltz power


On Jul 2, 2013, at 11:15 AM, Ray Walters wrote:

 Hi Dick;
 
 What you're suggesting is actually something I thought would work too: having 
 totally odd colors that immediately said DC.
 IT really would be the best, because if you go in with a meter set to read 
 AC, and show no voltage, then get your voltage sniffer out, and it doesn't 
 beep, you think you're double safe, when actually you could get hit with 500 
 v dc.
 
 I try and mark every J-box that has DC conductors in it with the DC voltage.  
 The life I save probably will be my own, as I'm getting more forgetful with 
 age..
 
 I think one of the problems is that this is actually not a NEW issue;  we are 
 reviving the 100+ year old AC vs DC battle that Edison Westinghouse, and 
 Tesla, et al. fought before.  Factories have AC and DC on site, and it just 
 amazes me that marking polarity isn't required by code.  We have to mark the 
 bonded conductor, or the high leg in certain 3 phase systems, so identifying 
 DC polarity seems just as important.
 I actually really like your purple with a white stripe idea.  At one time I 
 tried to color code for DC voltage too, (Red for 12 v, purple for 24, Orange 
 for 48 v) and even used yellow tape for my PV inputs as they had a higher V 
 than the battery.  Now I just try to label everything copiously, and have 
 polarity align with my meter.
 My biggest problem is still old 12 v house wiring on Romex (white and black)  
 or which side of those Monkey face outlets should be + or - ..  These 
 days, I just try to switch the circuit over to AC   (go Tesla!)
 
 R.Ray Walters
 CTO, Solarray, Inc
 Nabcep Certified PV Installer,
 Licensed Master Electrician
 Solar Design Engineer
 303 505-8760

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Wet NiCad batteries

2013-06-25 Thread jay peltz
HI All,

I'm looking for information on how you recondition wet cell NiCad batteries,

Thanks in advance,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Wet NiCad batteries

2013-06-25 Thread jay peltz
HI Dan and Bob-O,

I totally agree with you both.

But as you guys both know, some folks really wont take no for an answer.
This person has the money and talent to do this, and he really wants to,
just trying to get him the correct info rather than some garbage off the WWW.

thanks,

jay


On Jun 25, 2013, at 10:19 AM, Exeltech wrote:

 Jay,
 
 I second Bob-O's comment - completely.
 
 I inherited a number of pocket-plate ni-cad cells in the early 90s
 and went through the same exercise as Richard Perez -- including
 the same bad words he used (maybe more).
 
 If the cells are truly diminished in capacity, recycle them.  The
 reconditioning effort required in an attempt to bring them back
 to life wasn't worth it.
 
 You may as well consider a DIY re-cap of your old tires while you're
 at it.
 
 Words of experience from the old guard
 
 
 Dan
 
 
 --- On Tue, 6/25/13, Bob-O Schultze bo...@electronconnection.com wrote:
 
 From: Bob-O Schultze bo...@electronconnection.com
 Subject: Re: [RE-wrenches] Wet NiCad batteries
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Tuesday, June 25, 2013, 11:55 AM
 
 You might want to check your early Home Powers. We went thorough
 that dance in 1989 or so. It's ugly and the spent electrolyte is
 serious toxic waste.
 
 
 
 On Jun 25, 2013, at 9:32 AM, jay peltz wrote:
 
 HI All,
 
 I'm looking for information on how you recondition wet cell
 NiCad batteries,
 
 Thanks in advance,
 
 jay
 peltz power
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 690.55 - maximum operating voltage

2013-06-11 Thread jay peltz
HI All,

I mean as its worded, it would also be 240vac?

jay 

peltz power


On Jun 11, 2013, at 7:30 AM, eric.bent...@schneider-electric.com wrote:

 
 Hi Bob, 
 I would rather it be worded maximum normal operating voltage. 
 Maximum operating voltage would be the recommended BULK voltage for the 
 battery type being utilized. 
 Equalization is a maintenance procedure, which is why it calls for separate 
 listing. 
 It must also include polarity of grounded conductor. 
 
 Eric
 _
  
 
 Eric Bentsen  |   Schneider Electric   |  Solar Business  |   UNITED STATES  
 |   Technical Support Representative 
 Phone: +(650) 351-8237 ext. 001#  |   
 Email: eric.bent...@schneider-electric.com  |   Site: 
 www.schneider-electric.com/solar  |   Address: 250 South Vasco Rd., 
 Livermore, CA 94551 
 
 Mail Attachment.jpeg
 *** Please consider the environment before printing this e-mail 
 
 
 
 From: Bob Clark bcl...@solar-wind.us
 To:   'RE-Wrenches' re-wrenches@lists.re-wrenches.org
 Date: 06/10/2013 08:08 PM
 Subject:  [RE-wrenches] NEC 690.55 - maximum operating voltage
 Sent by:  re-wrenches-boun...@lists.re-wrenches.org
 
 
 
 
 RE_Wrenches: 
   
 Can someone tell me what is being referred to in NEC 690.55 when it says 
 “Photovoltaic power systems employing energy storage shall also be marked 
 with the “maximum operating voltage, . . .” ? 
   
 We have an off-grid system which employs energy storage [i.e.; batteries]; so 
 I need to know what exactly is referred to when this section mentions 
 “maximum operating voltage” so I can put it on a sign. 
   
 Bob Clark 
 SolarWind Energy Systems, LLC

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] battery watering systems

2013-06-08 Thread jay peltz
HI Tom,

Thanks,

I need 3 of the VB-TB5-S

For Trojan L-16's.

we'll work out the details.

thx,

jay




On Jun 8, 2013, at 1:43 PM, Tom Duffy wrote:

 Jay
 
 We have them
 
 Tom Duffy
 Senior Solar Design Engineer
 
 Toll Free 888-895-8179
 t...@thesolar.biz
 Customer Service and Accounting 888-895-6810 
 Grid tie sales 888-895-7847 
 Off Grid sales 888-895-4058 
 Other Product Sales 888-895-9612 
 Central America Sales (Panama) 507-6-126-1253 
 Shipping and Receiving 888-895-6497 
 Tech Support 888-895-8179
 SKYPE:  thesolarbiz
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
 Sent: Friday, June 07, 2013 3:53 PM
 To: RE-wrenches
 Subject: [RE-wrenches] battery watering systems
 
 HI All,
 
 Any good places to order watering caps from Battery watering technologies?
 
 thanks,
 
 jay
 
 peltz power
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] battery watering systems

2013-06-07 Thread jay peltz
HI All,

Any good places to order watering caps from Battery watering technologies?

thanks,

jay

peltz power


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] would this work?

2013-06-05 Thread jay peltz
Hi Todd

As bob-0 and Larry have said

And the sqflex is a mppt unit, nothing else needed

Jay

Peltz power

Sent from my iPad

On Jun 5, 2013, at 7:30 PM, toddc...@finestplanet.com wrote:

 ok wrenches... here is a hair brained idea i came up with.
  
 i have this customer with the grundfos pump being powered, array direct by 10 
 astropower 75's in series... so around  170 vdc.
  
 what would happen if a hv mppt charge controller were paralleled with the 
 panel output feeding the pump?
 would the cu200  charge controller mppt algorithms fight each other?
  
 thanks,
  
 todd
 
 
 
 Sent from Finest Planet WebMail.
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Defective modules

2013-06-03 Thread jay peltz
HI  Carl,

I can't seem to be able to get that data off the site.

Maybe someone else can.

It is a main reason I bought the subscription,  just to support their great 
testing work.

jay




On Jun 2, 2013, at 8:30 PM, Carl Emerson wrote:

 Hi Jay,
  
 Thanks for that, yes, I have seen the setup you refer to and it is very 
 comprehensive, but I thought that your reference to the 151 modules was a lab 
 test at STC and not an outdoor test for energy yield.
  
 Can you send the link to the outdoor test results please…
  
 Many Thanks,
 
 Carl Emerson
  
 Hi Carl,
  
 Here is the link to how Photon measures each module.
  
 http://www.photon.info/photon_lab_modul_ertragsm_en.photon?ActiveID=1289
  
 and
  
 http://www.photon.info/photon_lab_modul_ertragsmAD_en.photon?ActiveID=4382
  
 Can you please tell me how they are doing it wrong, and what the test would 
 look like in doing it right?
  
 Many thanks,
  
 jay
  
 peltz power
  
  
 On Jun 2, 2013, at 3:27 PM, Carl Emerson wrote:
 
 
 Jay,
  
 The short answer is no…
  
 These are not real world tests of energy yield under ‘normal’ outdoor 
 conditions.
  
 Photon are setting up field tests for 2013 in Germany and the middle East.
  
 Then they will have some useful data.
  
 Carl E.
  
 Hi Carl
  
 Would like to see real data. 
  
 Photon publishes their module data, and thin film are no where near the top 
 of the list. 
  
 Nexpower. #14
 First solar. #131
 Total of 151 modules in the test. 
  
 Jay
  
 Peltz power
 
 Sent from my iPad
 
 On Jun 1, 2013, at 6:20 PM, Carl Emerson c...@solarking.net.nz wrote:
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Defective modules

2013-06-02 Thread jay peltz
Hi Carl

Would like to see real data. 

Photon publishes their module data, and thin film are no where near the top of 
the list. 

Nexpower. #14
First solar. #131
Total of 151 modules in the test. 

Jay

Peltz power

Sent from my iPad

On Jun 1, 2013, at 6:20 PM, Carl Emerson c...@solarking.net.nz wrote:

 Hi there,
  
 Thin film is still getting bad press after early production suffered 
 degradation issues way back in the 90’s.
  
 There is plenty of evidence that thin film produces at least 10% more energy 
 because it performs better at temperature and responds better to global 
 irradiance.
  
 Some brands may be problematic today but this is equally true of crystalline 
 modules.
  
 Sure the efficiency is down and more area is needed for the same rated power 
 but some brands are delivering 20% more energy in some climates.
  
 As for degradation, I have seen crystalline BP’s with every panel turning 
 brown and clapping out after just 12 years in the pacific Islands.
  
 So let’s be Brand specific and not lump all thin film together and tar it 
 with the same brush, based on early failures 30 years ago.
  
 Current issues backed up with hard data would be very useful…
  
 Regards
 Carl Emerson
  
  
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Defective modules

2013-06-02 Thread jay peltz
Hi Carl,

Here is the link to how Photon measures each module.

http://www.photon.info/photon_lab_modul_ertragsm_en.photon?ActiveID=1289

and

http://www.photon.info/photon_lab_modul_ertragsmAD_en.photon?ActiveID=4382

Can you please tell me how they are doing it wrong, and what the test would 
look like in doing it right?

Many thanks,

jay

peltz power


On Jun 2, 2013, at 3:27 PM, Carl Emerson wrote:

 Jay,
  
 The short answer is no…
  
 These are not real world tests of energy yield under ‘normal’ outdoor 
 conditions.
  
 Photon are setting up field tests for 2013 in Germany and the middle East.
  
 Then they will have some useful data.
  
 Carl E.
  
 Hi Carl
  
 Would like to see real data. 
  
 Photon publishes their module data, and thin film are no where near the top 
 of the list. 
  
 Nexpower. #14
 First solar. #131
 Total of 151 modules in the test. 
  
 Jay
  
 Peltz power
 
 Sent from my iPad
 
 On Jun 1, 2013, at 6:20 PM, Carl Emerson c...@solarking.net.nz wrote:
 
 Hi there,
  
 Thin film is still getting bad press after early production suffered 
 degradation issues way back in the 90’s.
  
 There is plenty of evidence that thin film produces at least 10% more energy 
 because it performs better at temperature and responds better to global 
 irradiance.
  
 Some brands may be problematic today but this is equally true of crystalline 
 modules.
  
 Sure the efficiency is down and more area is needed for the same rated power 
 but some brands are delivering 20% more energy in some climates.
  
 As for degradation, I have seen crystalline BP’s with every panel turning 
 brown and clapping out after just 12 years in the pacific Islands.
  
 So let’s be Brand specific and not lump all thin film together and tar it 
 with the same brush, based on early failures 30 years ago.
  
 Current issues backed up with hard data would be very useful…
  
 Regards
 Carl Emerson
  
  
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] pump questions

2013-05-31 Thread jay peltz
HI all

All those 75 watt panels were really close to the same parameters.

According to one catalog, it was:  4.4 imp,  4.8isc,  17 vmp, 21 voc

From memory, they did poorly in hot weather, heavy voltage drop.


jay

peltz power




On May 31, 2013, at 10:30 AM, Allan Sindelar wrote:

 Bob-O and Todd,
 In theory you're right, Bob-O. I find the program awkward to use, given that 
 it thinks in some weird (Danish?) way, that I don't use often enough to 
 remember how to navigate. But in this case my bigger concern would be how to 
 input data for a bunch of old used Astropower 75s. Astropower's been gone for 
 over ten years, I think, and data isn't likely to show up on the backsheets. 
 WINCaps doesn't account for module degradation, either. 
 
 Todd, I might have a copy of a module spec sheet for the AP75 in our files at 
 the office. Not sure, as we never used any, but I collected a lot of that old 
 crap. Contact me off list on Monday if you need me to look. 
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] used panel mount questions

2013-05-30 Thread jay peltz
Hi Allan and Todd.

these modules sound like the ones that Powerlight used back many years ago.

These modules were mounted flat with the blue foam as insulation/mounting.

the concept while pretty cool at first look didn't work out.

Not sure what to tell you about what/how to mount them too however.

jay

peltz power
On May 30, 2013, at 3:46 PM, Allan Sindelar wrote:

 Todd,
 I don't have your answers, only the caution that blue foam to many of us 
 with a construction background means extruded polystyrene or blueboard, 
 commonly used around foundations. It deteriorates with exposure to sunlight, 
 so could only be used in an application such as this if protected from UV.
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 
 On 5/30/2013 4:14 PM, Todd Cory wrote:
 wrenches,
 
 i have a customer who purchased 20 used astropower ap75 modules. they are 
 frameless and appear to have been previously mounted using four, 2 wide X 
 10 long strips of blue rigid foam, glued to the back of each module with 
 some kind of adhesive.
 
 two questions:
 
 this seems to be a reasonable mounting system id like to repeat. would 
 anyone familiar with this kind of mounting technique be willing to 
 comment/speculate on an adhesive that would not degrade the tedlar 
 backsheet? whatever was previously used worked great.
 
 what kind of flat/smooth mounting surface would folks suggest the other side 
 of the blue foam be attached to? the only thing i can think of is plywood, 
 but that would rot over time.
 
 thanks,
 
 todd
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] used panel mount questions

2013-05-30 Thread jay peltz
Hi Dan,

Schletter solar has some.

under their Laminate modules and accessories section.

jay

peltz power


On May 30, 2013, at 4:25 PM, Exeltech wrote:

 I've seen rack edge clamps for frameless PV advertised, but didn't make a
 mental note of made by whom, or where I saw the ad.  I *do* recall the clamps
 were intended to be located along the long edges, not the ends.  Otherwise,
 expansion/contraction would stress/break the glass.
 
 There's a wealth of knowledge and know-how here.  Someone with the answer
 will chime in.
 
 
 Dan
 
 --- On Thu, 5/30/13, toddc...@finestplanet.com toddc...@finestplanet.com 
 wrote:
 
 From: toddc...@finestplanet.com toddc...@finestplanet.com
 Subject: Re: [RE-wrenches] used panel mount questions
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Thursday, May 30, 2013, 6:06 PM
 
 good point dan... i wonder how frameless modules are intended to be mounted?
  
 todd
  
  
  
  
 On Thursday, May 30, 2013 4:00pm, Exeltech exelt...@yahoo.com said:
 
 I agree with Allen, and would like to add a related comment.  Foam boards are
 thermally insulative in nature.  If affixed to the PV with adhesive, they 
 would
 cause the PV module to run hotter than if the backsheet was fully exposed
 to the air.
 
 This results in reduced energy output under all conditions, and increased
 thermal stresses on the PV cells, internal buss, bonds, and other aspects
 of the PV.
 
 
 Dan
 
 
 --- On Thu, 5/30/13, Allan Sindelar al...@positiveenergysolar.com wrote:
 
 From: Allan Sindelar al...@positiveenergysolar.com
 Subject: Re: [RE-wrenches] used panel mount questions
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: Thursday, May 30, 2013, 5:46 PM
 
 
 Todd,
 I don't have your answers, only the caution that blue foam to many of us 
 with a construction background means extruded polystyrene or blueboard, 
 commonly used around foundations. It deteriorates with exposure to sunlight, 
 so could only be used in an application such as this if protected from UV.
 Allan
 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 On 5/30/2013 4:14 PM, Todd Cory wrote:
 wrenches,
 
 i have a customer who purchased 20 used astropower ap75 modules. they are 
 frameless and appear to have been previously mounted using four, 2 wide X 
 10 long strips of blue rigid foam, glued to the back of each module with 
 some kind of adhesive.
 
 two questions:
 
 this seems to be a reasonable mounting system id like to repeat. would anyone 
 familiar with this kind of mounting technique be willing to comment/speculate 
 on an adhesive that would not degrade the tedlar backsheet? whatever was 
 previously used worked great.
 
 what kind of flat/smooth mounting surface would folks suggest the other side 
 of the blue foam be attached to? the only thing i can think of is plywood, 
 but that would rot over time.
 
 thanks,
 
 todd
 
 
 
 
 ___ List sponsored by Home Power 
 magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address 
  settings: 
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules 
  etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
 www.members.re-wrenches.org
 
 -Inline Attachment Follows-
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 Sent from Finest Planet WebMail.
 
 -Inline Attachment Follows-
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List

[RE-wrenches] modules

2013-05-30 Thread jay peltz
A question about US made modules.

Who actually makes the cells here in the us?

Only 2 that i know of, Im sure there are more.
Solar world.
First solar

who else?

thanks,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling different brands

2013-05-28 Thread Jay Peltz
Hi Lars

I'm curious what you found those efficiency differences to be?

And how are you measuring inverter charging efficiency in the bi directional 
mode

Thanks

Jay

Peltz power



Sent from my iPhone

On May 28, 2013, at 10:53 AM, lars Ortegren l...@cal-solar.com wrote:

 We have done a number of off grid AC coupling projects over the last eight
 years. We have found they are successful with anything that comes close to a
 true sign wave, including some of the old Trace inverters. I would be
 careful to not come too close to the wattage of the source inverter, and
 keep in mind that your battery charging is only one stage (bulk), and might
 not be the best choice without another charging source (i.e. the grid, or a
 semi regular generator). I can't say it makes a lot of sense, but when we
 have tested grid tied inverters and charge controllers side by side, the GT
 inverters produce significantly more than any CC's on the market.. Any more,
 I think that it is a better design to have the larger array tied to a GT
 inverter, and a small array tied to a charge controller for absorb and float
 charging...Just sayin.
 
 Lars Ortegren
 Director of Operations
 California Solar Electric Company
 10141 Evening Star Drive, Suite 6
 Grass Valley, CA 95945
 http://www.californiasolarco.com/
 
 Phone : (530)274-3671
 Fax: (530)274-7518
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] PV-direct electric water heating

2013-05-14 Thread Jay Peltz
Hi Hilton

What controller did he use?

Jay

Peltz power

Sent from my iPhone

On May 14, 2013, at 5:22 PM, Hilton Dier III hiltond...@gmail.com wrote:

 A friend of mine lives off grid with PV and wind. He added a shunt-type 
 controller to his battery bank and connected it to a DC heating element in 
 his hot water tank. Below a set voltage the element is dormant. When the 
 battery bank hits a high voltage (at the end of a particularly sunny day or 
 during a windy spell) the element comes on. That way, instead of just a PWM 
 shutoff and wasted energy, he gets some benefit.
 
 I wouldn't deliberately install PV just for hot water, but in an off grid 
 situation where the excess would go to waste, it makes sense.
 
 Hilton
 -- 
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Boxes

2013-05-12 Thread jay peltz
Hi Jesse

What is your concern with a wood based battery box?

Thanks

Jay

Peltz power

Sent from my iPad

On May 11, 2013, at 10:16 PM, Jesse Dahl dahlso...@gmail.com wrote:

 Hello,
 
 I visited a site on Friday to do some trouble-shooting on a system and 
 noticed the battery box was homemade by the installer of the system. Made 
 from lumber.  Seems to me like there may be some safety and liability issues 
 with a homemade/lumber battery box. Maybe I'm getting gun shy after hearing 
 sue stories.  Is this a common practice?  I did some looking and there really 
 isn't a single box that would work for this system so it would've taken two 
 boxes to do it, so that could be why they did it. 
 
 Thanks as always,
 
 Jesse
 
 Sent from my iPhone
 ___
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Battery Back-up and Grid Tie

2013-04-26 Thread Jay Peltz
Hi bill

Just how often is your grid down?

Jay
Peltz power

Sent from my iPhone

On Apr 26, 2013, at 10:01 AM, Bill Turberville billt...@ece-llc.com wrote:

 I live in a TVA area where there is a Feed In Tariff.  Everything that is 
 generated by the PV array feeds into the grid through a Generation Meter that 
 ties-in ahead of the house meter.  I have started getting calls from 
 customers who hate having a solar array that does not generate when the grid 
 is down but the sun is shining, but who also want to get the $.12 premium 
 when the grid is connected.  We have lots of systems with SMA Sunnyboy 
 inverters, but more with Enphase micro-inverters.  Rather than trying to 
 reinvent the wheel, what you found to be the best solution for this type of 
 installation?
  
 W.C. (Bill) Turberville P.E.
 President
  
 ECE Solar
 Electrical Contracting Enterprises LLC
 3080 Stage Post Road Suite 107
 Bartlett, TN 38133
  
 901-348-9230 ext 101 phone
 901-348-2192 fax
 901-289-6346 cell
 billt...@ece-llc.com
  
 NABCEP Certified PV Installation Professional 032611-320
  
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] large ground mounts

2013-04-26 Thread jay peltz
HI All,

Wondering if anyone has recommendations of the following ground mounts.


Unirac ULA
vs
Iron Ridge ground mount.

Thanks in advance,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] ground mount options?

2013-04-18 Thread jay peltz
How large an array are you needing?

Jay

Peltz power

Sent from my iPad

On Apr 17, 2013, at 9:23 PM, Jesse Dahl dahlso...@gmail.com wrote:

 Hello,
 
 I've been asked to put together a proposal for a local community and the only 
 option is a ground mount (pole mount would work too).  I've looked at a few 
 options today and was wondering if anyone has any opinions on the DPW Power 
 Peak mounting system?  
 
 Also, I would be interested in any other ground mount options that people 
 like/recommend.  I've used the two-tier mount on a few projects and the DPW 
 MPM and liked them good enough, but I'm always interested in trying new 
 mounts.  
 
 Thanks!
 
 
 Jesse
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Micro-inverters for 3-phase 220/127 in Mexico

2013-04-18 Thread jay peltz
Hi all

You might look at HiQ
http://www.hiqsolar.com/

Dave Katz has been using them and likes them a lot

They are a true 3 wire 3 phase. 
And have bidirectional communication. 

Jay

Peltz power

Sent from my iPad

On Apr 18, 2013, at 7:20 AM, Chris Mason cometenergysyst...@gmail.com wrote:

 Do you think Enphase be willing to increase the VMax? That's what we do here 
 when we have 220V 3ph issues. As we are not US based, there is no UL issue.
 I have a project right now that Enphase is the best solution, but the voltage 
 would be 129v typically, so I would be unwilling to put in stock units.
 
 
 On Mon, Apr 15, 2013 at 8:03 PM, Kent Osterberg k...@coveoregon.com wrote:
 Enphase lists the standard operating range for the 208-volt 3-phase 
 configuration as 183 to 229 volts. Seems like 220-volt 3-phase might work 
 with a little caution about wiring losses.
 Kent Osterberg
 Blue Mountain Solar, Inc.
 www.bluemountainsolar.com
 
 
 On 4/15/2013 4:28 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
 Interesting….Here is a reply from Enphase received on 4-11-13, Hi Larry, 
 No we do not have a inverter that will work with this. Our inverter is for 
 240AC 2 Phase, 208AC 3 Phase…
 
 
 
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 
 
 
 On Apr 15, 2013, at 1:54 PM, Nick Soleil nsol...@enphaseenergy.com wrote:
 
 Hi Larry,
 
 Enphase is supplying microinverters into Mexico and supporting the 127/220 
 applications.  We have hundreds of installations installed at this voltage 
 now.  Feel free to contact me off-line, and I would be happy to discuss the 
 details.
 
 
 
 
 
 On Mon, Apr 15, 2013 at 1:25 PM, Larry Crutcher, Starlight Solar Power 
 Systems la...@starlightsolar.com wrote:
 Wrenches, 
 
 A customer in Mexico wants to start with about 10kW PV. They have a 225 
 kva transformer supplying 220/127 volt 3-phase to the property. They are 
 adding buildings/roof space in several stages over the next 4 years and 
 want to grow the installation to 120kW of PV solar power.
 
 Manufacturer data sheets are not real clear. Who makes micro-inverters 
 suitable for this? I know Enphase does not.
 
 Thank you,
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 -- 
 Cordially,
 Nick Soleil
 Field Applications Engineer
 Enphase Energy
 Mobile: (707) 321-2937
 
 Enphase Commercial Solar. Limitless.
 
 1420 North McDowell
 Petaluma, CA 94954
 www.enphase.com
 P: (707) 763-4784 x7267
 F: (707) 763-0784
 E: nsol...@enphaseenergy.com
 image002.jpg Certified Solar PV Installer #03262011-300
 
 “Don’t get me wrong: I love nuclear energy! It’s just that I prefer fusion 
 to fission. And it just so happens that there’s an enormous fusion reactor 
 safely banked a few million miles from us. It delivers more than we could 
 ever use in just about 8 minutes. And it’s wireless! .”  
 - William McDonough
 
 This email message is for the sole use of the intended recipient(s) and may 
 contain confidential and/or privileged information. If you are not an 
 intended recipient, you may not review, use, copy, disclose or distribute 
 this message. If you received this message in error, please contact the 
 sender by reply email and destroy all copies of the original message. 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 -- 
 Chris Mason
 President, Comet Systems Ltd
 www.cometenergysystems.com
 Cell: 264.235.5670
 Skype: netconcepts
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http

Re: [RE-wrenches] outback fx series inverters

2013-04-13 Thread jay peltz
Hi guys,

While I agree that its probably crazy talk.

There is one story I have to share.

Just like this one, the customer was complaining of the emf's.
then she called the install company to say that they were gone!.
She didn't know that just that morning the install guys had put a faraday cage 
around the inverter, put in extra grounds etc.

No way she could have known, but she did notice the difference.

So don't discount everyone, just almost everyone.

jay

peltz power

On Apr 13, 2013, at 1:09 PM, Chris Daum wrote:

 I don't knowI have perhaps three customers, over the past ~20 years, who 
 claim to be 'allergic to electricity', for lack of a better term.  As you can 
 imagine, existing in our current society is actually painful for them.  
 They've all bought (for example) propane 'fridges since they use no 
 electricity and don't cause them to have that 'pins  needles' feeling they 
 get when they are near electrical fields.  I try not to laugh at them, yet I 
 believe they are sincere when they tell me, I can't stand to be near 
 anything electrical.  So perhaps there needs to be some sort of independent 
 test to confirm what these folks claim to feel.
  
 Chris Daum
 Oasis Montana Inc.
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Randy Brooks
 Sent: Saturday, April 13, 2013 1:53 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] outback fx series inverters
 
 Have you used a gaus meter 
 (http://www.amazon.com/Gen-El-Gauss-Master/dp/B0004IR6J6/ref=sr_1_2?ie=UTF8qid=1365882645sr=8-2keywords=gaus+meter)
  to measure the EMF near the inverters and other places?  Might put it in 
 perspective.
 
 Randy
 
 On Apr 13, 2013, at 12:17 PM, Todd Cory toddc...@finestplanet.com wrote:
 
 wrenches...
 
 put on our tin foil hats... i have a customer who claims the emf from their 
 grid tied gvfx3648 is making them sick. does anyone know the switching 
 frequency of the inverter and has anyone else reported this? also any ideas 
 on how to mitigate it?
 
 thanks,
 
 todd
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Advanced PV Training Recommendations

2013-04-12 Thread jay peltz
HI Eric,

I'm going to advise you to look at SEI
Solar energy international.

http://www.solarenergy.org/

Full disclosure, I teach part time from them.

Cheers,

jay

peltz power

On Apr 12, 2013, at 12:46 PM, SunHarvest wrote:

 Wrenchers -
  
 I am in need of hands-on advanced training for my own continuing education. I 
 have a California C46 solar contractor's license and plenty of experience 
 designing and installing systems. But, as you all know, there are always more 
 details to master, code issues to be clarified, and new technologies coming 
 down the pike. I'd like to focus on off-grid and on-grid w/BB systems over 
 straight grid-tie.
  
 I'm looking at Solar Living Institute as that's here in NorCal, where I live.
  
 Are there any training schools/programs that you guys would recommend?
  
 My main requirements are that the instructor has 20+ years of hands-on 
 experience and that the training is hands-on and fully comprehensive. I am 
 interested in getting NABCEP certified but I'm more concerned with getting 
 professional, in-depth training than with qualifying for NABCEP exam 
 requirements.
  
 Thanks!
  
 Eric
 SunHarvest
  
  
 - Original Message -
 From: John Berdner
 To: RE-wrenches
 Sent: Thursday, April 04, 2013 11:44 AM
 Subject: Re: [RE-wrenches] Combining conductors
 
 Larry:
  
 Yes, you can parallel conductors (there is an NEC limit on minimum size 
 allowed to parallel).
 You just add the ampacity of the two conductors.
 To convince yourself you can also check Table 8 Conductor Properties and sum 
 the cross sectional areas of all the parallel conductors to see the 
 equivalency to a single larger conductor.
  
 Best Regards,
  
 John Berdner
 General Manager, North America
  
 SolarEdge Technologies, Inc.
 3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new 
 address.)
 T: 510.498.3200, X 747
 M: 530.277.4894
  
 From: re-wrenches-boun...@lists.re-wrenches.org 
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry 
 Crutcher, Starlight Solar Power Systems
 Sent: Thursday, April 04, 2013 9:51 AM
 To: RE-wrenches
 Subject: [RE-wrenches] Combining conductors
  
 Wrenches,
  
 Here's a tough one for me to understand. I am installing 2 volt AGM 
 batteries. There are two terminals for each battery polarity. I have some 
 height limits so I need to use the minimum wire size. Here's my question: If 
 I combine two identical conductors, what is the equivalent single conductor 
 size? 
  
 I found one rule of thumb that says doubling like conductors creates a AWG 
 decrease of 3. Example: two #2 will be equivalent to 2/0. Is this true?
 
 Thank you,
 
 Larry Crutcher
 Starlight Solar Power Systems
  
  
 
 
 
  
 CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
 the use of the individual or entity who is the intended recipient and may 
 contain information that is privileged, confidential and exempt from 
 disclosure or any type of use under applicable law. If the reader of this 
 e-mail is not the intended recipient, or the employee, agent, or 
 representative responsible for delivering the e-mail to the intended 
 recipient, you are hereby notified that any dissemination, distribution, 
 copying, or other use of this e-mail is strictly prohibited. If you have 
 received this e-mail in error, please reply immediately to the sender. 
 P  Please think of the environment before printing this email
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cable tray

2013-03-30 Thread Jay Peltz
 Hi Bill

I'm with you all the way. I love to do things 
Telecomm style. Very clean, safe and better IMHO. 

1000v PV wire can be bought at PV cables.com

Cheers

Jay

Peltz Power. 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Auto Gen on Outback

2013-03-28 Thread Jay Peltz
Hi drake

It's the mate which has had issues. 
Make sure the mate is current rev. 
Outback will put in latest version for no charge. 

Jay

Peltz power

Sent from my iPhone

On Mar 27, 2013, at 12:51 PM, Drake drake.chamber...@redwoodalliance.org 
wrote:

 Hello Wrenches,
 
 We are adding a Generac EcoGen to an existing Outback VFX 3648 system.  It 
 was the recommendations from those of you on this list who have installed 
 them that led to this choice. Your testimonials are very much appreciated.
 
 I've read, on this list, that people have had issues with FX family inverters 
 starting and stopping generators reliably. The plan was to go with the 
 Atkinson GSCM and a separate voltage controlled relay.  It appears that if 
 the system is 48 volts, it is necessary to center tap the battery bank for a 
 24 volt feed to the GSCM. This I don't want to do.
 
 Is it still agreed that the FX inverters are not reliable for starting and 
 stopping generators? 
 
 Has anyone used a GSCM on a 48 volt system without problems?
 
 Thank you,
 
 Drake 
 
 
 
 
 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling Situation

2013-03-18 Thread Jay Peltz
Hi Jeremy

Seems like a perfect place for  the 600v controller from xantrex

Jay
Peltz power. 





Sent from my iPhone

On Mar 18, 2013, at 7:23 PM, Jeremy Rodriguez- All Solar Inc. 
allso...@scswifi.net wrote:

 Wrenches,
 Here is my situation:  GT string inverter - 3 strings of mods, 10KW DC. We 
 need to reduce the PV when the grid is down as to not overload the AC coupled 
 inverters.  
 Is there a good way to limit PV input like shunt off some power or short part 
 of the array? (part)
 I was first thinking of dropping off 2 of the three strings, but that would 
 not leave enough input for the critical loads. 
 Has anyone done such a thing?
 
 Jeremy
 All Solar
 CO- USA  
 Sent via BlackBerry. Sorry for typos and shorthand!
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] bad battery = system overvoltage = dead inverter

2013-03-16 Thread Jay Peltz
Hi Dan

Can you tell us which CC?

Thx

Jay

Peltz power

Sent from my iPhone
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Temperature sensor compatibility for inverters, charge controllers

2013-03-11 Thread jay peltz
HI Larry,

Been wanting to know that myself.

I know that outback and midnight are compatible.

jay

peltz power


On Mar 11, 2013, at 3:48 PM, Larry Crutcher, Starlight Solar Power Systems 
wrote:

 Battery Wrenches, 
 
 There are a myriad of battery temperature sensors for inverter/chargers and 
 charge controllers. Does anyone know of compatibility between sensors? For 
 example, I need some of the old Heart (then Xantrex, then Schneider) 
 20-0022-00 temperature sensors but they are now special order, weeks of 
 waiting with drop ship fees. 
 
 1. Will anything else work? 
 2. Does anyone have a part #/specification for the sensor device?
 
 Thank you,
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] DC generators

2013-03-06 Thread jay peltz
I just wanted to follow up on one thing about the kohler DC gensets.

I talked to my genny buddy about the Kohler and he said:

The voltages are adjustable.  On the 24v unit, from 24 to 33v.
It also tapers  the current down to around 40 amps, from a peak of 222.

thanks,

jay

peltz power








___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] DC generators

2013-03-05 Thread jay peltz
HI All,

I know many of you like this concept.

I was just made aware of a new product from Kohler.

Kohler 6vsg.  Natural gas or propane, 24, 36,48v dc only
looks pretty good, I understand it was made for the telecom industry.

And while Im not normally on board with the DC genset idea, that i can get 222 
amps from 6kw at 24v is very appealing.

http://www.kohlerpower.com/industrial/filterresults.htm?categoryNumber=12061sectionNumber=13261filter_1=Variable%20Speed,%20Direct%20Current

Cheers,

jay

peltz power


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Wireless AC relay

2013-02-20 Thread jay peltz
 Hi all

I seem to remember some folks using a wireless remote to control a AC relay
Any info on this would be appreciated 

Thanks in advance

Jay

Peltz power


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] MC3-MC4 Connectors

2013-02-13 Thread jay peltz
Hi Jason

Contact. PV cables

br...@pv-cables.com
707-923-3000

Jay

Peltz power


Sent from my iPad

On Feb 13, 2013, at 3:55 PM, Jason Szumlanski ja...@fafcosolar.com wrote:

 I'm getting an odd number of calls recently from local people who want MC4 
 connectors. When I tell them a crimping tool is needed, they tell me they 
 could also use MC3 to MC4 adapters. I'm guessing that somebody dumped a bunch 
 of old modules with MC3 connectors in the local market to DIY'ers. I keep 
 trying to probe to see if they need MC3 locking clamshells for 
 interconnections to meet code, but they have no idea what I'm talking about, 
 of course. 
 
 Anyway, can someone give me a source for adapter cables. My usual sources 
 have stopped carrying them. Eventually I'll get one of these guys to let the 
 pros take over. :)
 
 Jason Szumlanski
 Fafco Solar
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generator Controlled Mini Grid

2013-02-12 Thread jay peltz
Hi guys,

You might look into AC direct hydro controls.  Thompson and Howe make them 
they are designed to keep both frequency and voltage within tolerance with dump 
loads.

jay

peltz power
On Feb 12, 2013, at 5:13 PM, Glenn Burt wrote:

 Sounds like a job for a directional relay - utilities use them.
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
 Sent: Tuesday, February 12, 2013 7:29 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Generator Controlled Mini Grid
 
 Hi Kevin,
 
 Right now we are in the stages of investigating what is possible.  The
 design is for 10kW of PV - inverter capacity.  The inverters will be Sunny
 Boys, so if may be possible to regulate them.
 
 We haven't decided on a generator yet.  A dump load sounds like a good way
 to absorb excess power.
 
 Have you heard of electronic controls to facilitate this process?
 
 Thanks,
 
 Drake
 
 
 At 03:43 PM 2/12/2013, you wrote:
 Hi Drake,
 
 Further, can you give us an idea what scale you are talking here - ie 
 PV and Generator capacity? With your mention of inverter/generator if 
 your talking ie the small Honda EU6500 or such?
 
 I did think of another project that I am involved with - it's a remote 
 community with conventional diesel power plant (100 kW day,
 30 kW night). There is 27 kW of distributed PV over 5-6 different 
 homes, using the older Xantrex GT inverters. It's not the most 
 elegantly designed solution - as it's possible for PV output to be 
 greater than the load which causes shutdowns. In that case, a dump load 
 is kicked in briefly and that bumps the frequency enough to kick the GT 
 inverters offline, and then the cycle repeats.
 
 Not my design, but it does work and has been this way for several years
 now.
 
 Kevin
 
 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org]On Behalf Of Drake
 Sent: February 10, 2013 10:46 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] Generator Controlled Mini Grid
 
 
 Hi Kevin,
 
 Thanks for the Eigg video.  What a great place.
 
 I didn't see evidence of any AC coupling of inverter produced AC to a 
 generator produced mini grid.  I understand this is being done in a 
 homebrew manner by some.
 
 The current wisdom on the issue is that the less the PV contribution to 
 the generator supplied grid is, the easier.  It would seem that if a 
 grid tie inverter output could be regulated, using Sunny Island type 
 controls, it should be possible to have a small inverter generator 
 create a mini grid that could be fed by PV.
 
 A system featuring this type of technology was linked in a posting on 
 this list some years ago, The link seems dead now.  In that case a 
 large generator was feeding a number of houses, and PV was fed into the 
 system.
 
 The reason for this interest is that battery backup systems are much 
 more expensive than generators.  We need to find a way to utilize PV 
 arrays during outages without the expense of battery backup systems.
 
 Drake
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Accessibility of Equipment on Roof was Are PV Systems Mechanical Equipment?

2013-02-08 Thread jay peltz
Hi jason,

3 questions, 
I can't find the MNPV-AC in midnites price list, is this something custom or 
just new?
And 
if you don't need breakers why not just do a junction box on the roof.
and
the inspectors I've had have requested a disconnecting means on the roof or 
visible from the roof.  So I've done the enphase suggested switches on the 
roof, but no overcurrent.  It doesn't appear that is a requirement from your 
inspector?


jay

peltz power


On Feb 8, 2013, at 7:27 AM, Jason Szumlanski wrote:

 Oh, yes - that is a great application for the MNPV-AC. I didn't mean to imply 
 there isn't a good use for them. In this particular instance the three 
 MVPV-AC's are really subcombiners that get all get tied together in another 
 subpanel at ground level. They really were not necessary, but made it more 
 convenient and cost effective.
 
 It's just interesting how Midnite advertises that they can be mounted as flat 
 as a 3:12 pitch. What application would allow this mounting angle where it is 
 still readily accessible? The spec/advertising seems to imply that these can 
 be roof mounted in an AC string combining application.
 
 The Soladeck combiner with fuses would appear to be non-code compliant in any 
 situation. I would love for someone to refute that in a convincing way given 
 the access requirements in 240.24(A).
 
 Jason Szumlanski
 Fafco Solar
 
 
 On Thu, Feb 7, 2013 at 7:31 PM, jay peltz j...@asis.com wrote:
 Hi Jason,
 
 Is it possible to install them on the side of a building?
 And Dan's suggestion for the remote midnite might be perfect.
 
 jay
 
 
 On Feb 7, 2013, at 3:55 PM, Jason Szumlanski wrote:
 
 Jay,
 
 I assume you mean pitched roofs, or not readily accessible flat roofs. This 
 particular project happens to be a flat commercial roof, but with no 
 permanent ladder or hatch. I really didn't have to use the MNPV6-AC's, but 
 it made sense in this case (excluding the access issue).
 
 Looks like my options are to remove the combiners or install a permanent 
 access. Neither are fun options. Live and learn...
 
 Jason Szumlanski 
 Fafco Solar
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Accessibility of Equipment on Roof was Are PV Systems Mechanical Equipment?

2013-02-07 Thread jay peltz
I'm with your inspector on this.

I don't install fuses or breakers on roofs

jay

peltz power


On Feb 7, 2013, at 12:02 PM, Jason Szumlanski wrote:

 While I haven't completely convinced the latest inspector about PV not being 
 mechanical equipment, I'm running into another issue. 
 
 I decided to try out the new Midnite MNPV6-AC combiner for Enphase circuits. 
 Because there are overcurrent devices inside, the inspector now insists that 
 NEC 240.24(A) applies and that the enclosure must be readily accessible, 
 meaning you have to reach it without a ladder. That would seem to make the 
 MNPV6-AC as a roof mounted solution, or Soladeck combiner boxes, or any other 
 combiner box incorporating overcurrent protection, pretty much useless on a 
 pitched roof or flat roof without a permanent access ladder or hatch. 
 
 I'm debating whether to go to battle on this one or just capitulate. 
 
 Jason Szumlanski 
 Fafco Solar
 
 P.S. To answer benn's question, there is no definition of 'mechanical,' but 
 it does define 'equipment,' and it's clear to me that PV does not fit the 
 description.
 mbers.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Accessibility of Equipment on Roof was Are PV Systems Mechanical Equipment?

2013-02-07 Thread jay peltz
Hi Jason,

Is it possible to install them on the side of a building?
And Dan's suggestion for the remote midnite might be perfect.

jay


On Feb 7, 2013, at 3:55 PM, Jason Szumlanski wrote:

 Jay,
 
 I assume you mean pitched roofs, or not readily accessible flat roofs. This 
 particular project happens to be a flat commercial roof, but with no 
 permanent ladder or hatch. I really didn't have to use the MNPV6-AC's, but it 
 made sense in this case (excluding the access issue).
 
 Looks like my options are to remove the combiners or install a permanent 
 access. Neither are fun options. Live and learn...
 
 Jason Szumlanski 
 Fafco Solar
 
 
 
 On Thu, Feb 7, 2013 at 6:27 PM, jay peltz j...@asis.com wrote:
 I'm with your inspector on this.
 
 I don't install fuses or breakers on roofs
 
 jay
 
 peltz power
 
 
 On Feb 7, 2013, at 12:02 PM, Jason Szumlanski wrote:
 
 While I haven't completely convinced the latest inspector about PV not being 
 mechanical equipment, I'm running into another issue. 
 
 I decided to try out the new Midnite MNPV6-AC combiner for Enphase circuits. 
 Because there are overcurrent devices inside, the inspector now insists that 
 NEC 240.24(A) applies and that the enclosure must be readily accessible, 
 meaning you have to reach it without a ladder. That would seem to make the 
 MNPV6-AC as a roof mounted solution, or Soladeck combiner boxes, or any 
 other combiner box incorporating overcurrent protection, pretty much useless 
 on a pitched roof or flat roof without a permanent access ladder or hatch. 
 
 I'm debating whether to go to battle on this one or just capitulate. 
 
 Jason Szumlanski 
 Fafco Solar
 
 P.S. To answer benn's question, there is no definition of 'mechanical,' but 
 it does define 'equipment,' and it's clear to me that PV does not fit the 
 description.
 mbers.re-wrenches.org
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sunny Island DC wire size

2013-02-04 Thread jay peltz
HI Howie,

I've seen someone use a single 4/0 fine stranded cable with a regular lug on 
the end of it.
they then cut the top of the hole out to make in a sense a U shape.
Each side of the U fit into each side of the 2 hole barrel connector on the SI.

Super slick iI thought.

I can send you a pic if you want.

jay

peltz power

On Feb 4, 2013, at 11:46 AM, Howie Michaelson wrote:

 Hi it has been more than a year since I wired up a Sunny Island 5048
 system and I'm trying to determine lug size for the DC conductors.  My
 memory is that the maxiumm wire size was (2) #1 conductors each for
 positive and negative.  Looking in the most recent SI manual states The
 Sunny Island has a MAX DC terminal rated for 2x #2/0 AWG for DC+, DC- and
 PE.  Not sure if that is a typo - anyone no definitively?  The tech
 support line has gotten to have as long a hold time as Outback, Xantrex,
 etc...
 
 Thanks,
 Howie
 -- 
 Howie Michaelson
 NABCEP Certified Solar PV Installer™
 
 Catamount Solar, LLC
 Renewable Energy Systems Sales and Service
 VT Solar Electric  Hot Water Incentive Partner
 http://www.CatamountSolar.com
 802-272-0004
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wrenches] Husqvarna 5500 and VFX3524Compatibility question

2013-02-03 Thread jay peltz
Hi Carl,

Your 230vac is a single wave form right?
 RMS peak to zero crossing of 230v

vs our

240vac which is 2 phase wave form
RMS peak to zero crossing of 120v 

Have I got this right?

thanks,
jay

peltz power




On Feb 2, 2013, at 6:56 PM, boB wrote:

 
 Carl,   NZ is 240 VAC right ?   240 VAC 2 wire ?
 
 I think that the problem may have to do with leg to leg voltage cross 
 regulation
 imbalance in 120/240 3 wire systems.
 
 boB
 
 
 On 2/2/2013 3:23 PM, Carl Emerson wrote:
 Goodness knows why 240V Sunny Island’s are unavailable in the US…
  
 We have been installing these in NZ for years !!!
  
 Regards
 Carl Emerson
  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wrenches] Husqvarna 5500 and VFX3524Compatibilityquestion

2013-02-03 Thread jay peltz
Hi Carl,

thanks and yes, I think its why they only did a 120v version here.

Another question for you there.

Its my understanding that neither of your legs is bonded to ground correct?



jay

peltz power


On Feb 3, 2013, at 4:22 PM, Carl Emerson wrote:

 Hi Jay,
  
 Yes you have described our grid waveform correctly.
  
 It is strange to me that they call yours 240V, the rationale used to describe 
 yours and mine are different I guess.
  
 Your grid seems to present less volts and more current.
  
 If this is correct then I am guessing that the transformers used in the units 
 here will not work for you.
  
 Regards
 Carl Emerson
  
  
 Hi Carl,
  
 Your 230vac is a single wave form right?
  RMS peak to zero crossing of 230v
  
 vs our
  
 240vac which is 2 phase wave form
 RMS peak to zero crossing of 120v 
  
 Have I got this right?
  
 thanks,
 jay
  
 peltz power
  
  
  
  
 On Feb 2, 2013, at 6:56 PM, boB wrote:
 
 
 
 Carl,   NZ is 240 VAC right ?   240 VAC 2 wire ?
 
 I think that the problem may have to do with leg to leg voltage cross 
 regulation
 imbalance in 120/240 3 wire systems.
 
 boB
 
 
 On 2/2/2013 3:23 PM, Carl Emerson wrote:
 Goodness knows why 240V Sunny Island’s are unavailable in the US…
  
 We have been installing these in NZ for years !!!
  
 Regards
 Carl Emerson
  
  
 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] generator suggestions

2013-01-30 Thread Jay Peltz
Hi Dan

So true. But never had it explained to me why propane is different than 
gasoline or diesel at altitude. 

Thx

Jay
Peltz power

Sent from my iPhone

On Jan 30, 2013, at 11:42 AM, Dan Fink danbo...@gmail.com wrote:

 And because of our Colorado location here, we are always dealing with 
 altitude de-rate factors. We are usually installing at 7000 - 1 feet 
 elevation, which is a big hit. Propane de-rates gennys even further.
 -- 
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342 (voicemail)
 
 
 On Wed, Jan 30, 2013 at 12:38 PM, Jay Peltz j...@asis.com wrote:
  Hi all
 
 I've found through hard experience that all generators except diesels seem 
 to be smaller than name plate rating.
 
 And while the charging maybe reduced if I am conservative in telling the 
 inverter how large the genny is I rarely get the genny to trip its breaker.
 
 
 Jay
 
 Peltz power
 
 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] generator suggestions

2013-01-30 Thread Jay Peltz
Hi guys 
Right on all accounts but I continue to hear that propane/nat gas is further 
derated than the liquid fuels. 
Or is this just bad info?

Thx

Jay

Sent from my iPhone

On Jan 30, 2013, at 12:44 PM, Larry Crutcher, Starlight Solar Power Systems 
la...@starlightsolar.com wrote:

 Jay, 
 
 In addition to what Dan has said, 1 gallon of propane has about 35% less 
 BTU's compared to 1 gallon of gasoline. So the propane derating must be added 
 to the altitude derate to determine generator output.
 
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 
 On Jan 30, 2013, at 1:32 PM, Dan Fink wrote:
 
 Jay;
 The standard seems to be 2-3% derate for every 1000 feet above sea level 
 for gasoline, diesel or LP gas generators, and supposedly more like 5% for 
 natural gas. (in general we don't work in areas that have natural gas 
 service, we only do off-grid). So the propane de-rate for altitude is no 
 worse than the diesel or gasoline de-rate, it's just added on top of it. In 
 practice, we are not seeing that big a hit, but it is hard to really judge. 
 Also, air-cooled generators don't cool as well at high altitudes and tend to 
 run hot.
 
 A fairly common troubleshooting call we've seen in the past is clients who 
 have purchased cheap portable generators from Home Depot, Harbor Freight etc. 
 and then find that they can't tune them for anything above 6000 feet -- the 
 carb adjustment screws don't go that far, and the fine print in the warranty 
 actually says 6000 ft max. Ouch! They run so poorly that very few modern 
 inverter/chargers will even look at their input. I've been a local 
 firefighter for 14 years now, even worse problem with chainsaws (2-stroke). 
 We've learned how to bust out the plastic EPA stops on the carb adjust 
 screws, with the of course unofficial instructions to throw the saw into the 
 fire if the EPA shows up..
 
 Never had the slightest high-altitude issues with the Honda x000i series 
 running OK, and I have no idea why. The de-rate factor is certainly still 
 there, but no issues idling or running, no matter what the draw. My Honda 
 3000i issues are from a different cause I think; there is an extensive thread 
 on that in the archives here that I started in July 2011 I think.
 
 DAN FINK
 
 On Wed, Jan 30, 2013 at 1:12 PM, Jay Peltz j...@asis.com wrote:
 Hi Dan
 
 So true. But never had it explained to me why propane is different than 
 gasoline or diesel at altitude. 
 
 Thx
 
 Jay
 Peltz power
 
 Sent from my iPhone
 
 On Jan 30, 2013, at 11:42 AM, Dan Fink danbo...@gmail.com wrote:
 
 And because of our Colorado location here, we are always dealing with 
 altitude de-rate factors. We are usually installing at 7000 - 1 feet 
 elevation, which is a big hit. Propane de-rates gennys even further.
 -- 
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342 (voicemail)
 
 
 On Wed, Jan 30, 2013 at 12:38 PM, Jay Peltz j...@asis.com wrote:
  Hi all
 
 I've found through hard experience that all generators except diesels seem 
 to be smaller than name plate rating.
 
 And while the charging maybe reduced if I am conservative in telling the 
 inverter how large the genny is I rarely get the genny to trip its breaker.
 
 
 Jay
 
 Peltz power
 
 
  
 ___
 
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 
 -- 
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342 (voicemail)
 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE

Re: [RE-wrenches] Husqvarna 5500 and VFX3524 Compatibility

2013-01-27 Thread jay peltz
Many versions of the Iota, Todd before them and now Power Max ( 12v and 24v are 
available, not sure yet on the 48v) are adjustable or can be ordered with an 
adjustment feature which will allow for   higher than normal setpoints.  16v+ 
if you want it

Jay 
peltz power


On Jan 27, 2013, at 6:31 PM, Carl Hansen wrote:

  Dan,
You may be do this as well, but I frequently deal with homeowners with 
 inexpensive generators, I find that the Outback and Magnum inverters are very 
 tolerant but I do generally have to load the generator up to where I want it 
 bulk charging the batteries, then adjust the generator speed to dial in the 
 freqency to 60Hz using the throttle adj.  screw.
Do you find the Iota chargers can reach bulk charge voltages, or even EQ 
 voltages ?
 
 Carl Hansen
 
 On 1/27/2013 5:15 PM, Dan Fink wrote:
 We have run into many problems on very remote sites with various really 
 nice, small newer inverter/chargers not accepting waveforms from various 
 newer (inverter-based) generators. For example on one particular system 
 Honda 1000i works fine, Honda 2000i works fine, Honda 3000i and the charger 
 says no. Plug a different Honda 3000i into the the same inverter/charger, 
 works fine. After sling-loading the Honda there by helicopter. Argh! 
 Inverter makers have been very helpful but the settings just can't be 
 tweaked that far, RE Wrenches list gurus have been awesomely helpful, Honda 
 not so helpful but at least honest.
 
 My service calls by helicopter this year will include an O-scope. I really 
 want to get to the bottom of the problem. It plagues us. I like Iota  
 chargers more and more every summer.
 
 -- 
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342 (voicemail)
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] high insolation value and inverter undersizing

2013-01-27 Thread jay peltz
There are many reasons you might want to limit AC output.  Say 120%buss bar 
rule or some other rebate situation where its sized on AC, not DC size.  So you 
can maximize your daily production without going over the peak AC limit.

Jay

peltz power


On Jan 27, 2013, at 8:05 PM, William Miller wrote:

 Jesse:
 
 Do you have any way to compare the total harvest for the day for a given 
 module in a clipping scenario versus an unclipping?  The question I want to 
 answer is: Do we improve production enough on the shoulders of the clip to 
 justify the loss on the peak?
 
 Thanks,
 
 William Miller
 
 
 At 06:25 PM 1/27/2013, you wrote:
 A while back (3 years)I installed a system (bid spec) for a school that used 
 215W RECs and D380s on a dual axis tracker.  With the ability to monitor the 
 array, I see constant clipping.  The modules will usually produce 199Ws 
 regularly.  A few days ago we had temps of -34F and clear skies.  My array 
 at home had one of its best days this winter.  I have Tigos on so I can 
 monitor watts, current, temp and voltage. I was seeing anywhere from 215W to 
 223W from my modules between 11:30am and 1pm.  The modules on the tracker 
 were still producing 199W.  I didn't get an irradiance reading that day but 
 my Tigos showed above IMP readings and way above VMP reading that day.
 
 I've only been doing this for 6 years, so I don't have the experience  that 
 some people on this list have, but it seems foolish to me to waste that 
 production.  It's kinda site specific, but where I live the cold temps and 
 snow reflection seem like something we should be utilizing.
 
 _
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Jay Peltz
Hi guys

I've buying the new 6 cell x 72 cell from Trina from a few suppliers. 
Big yea, but same 44voc  so it's an easy add to existing systems. 

A huge relief. 

Jay

Peltz power

Sent from my iPhone

On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com wrote:

 Hi Allan;
 
 I've been in the same conundrum lately.  I found that AEE and others have 12 
 v modules (Solartech), but the price per watt is double or triple.  My take 
 is that somewhere around 200 to 400 watts, its more cost effective to go to 
 the GT modules with an MPPT controller.  Blue Sky makes the 1524, and 3024 
 that can take up to 57 Voc, so those would work at still fairly low cost.  
 Unfortunately many of the other low cost MPPT controllers won't work with the 
 60 cell modules.  At some point, it may actually be cost effective to just 
 use 60 cell modules with non MPPT controllers, and just forget about the 
 extra 24 cells.  (I know that sounds crazy, but PV less than $1/ watt is 
 crazy too)
 
 I'm trying to add modules to an existing array of 8 Siemens 12 v modules, and 
 it just doesn't work out, except with separate controllers. 
 Also, its amazing how much PV you can throw at an off grid project these days 
 for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting to 
 really up size, and then reuse the old modules for small systems?
 
 Ray
 
 On 1/24/2013 12:35 PM, Allan Sindelar wrote:
 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
 battery-based customers. Most of our systems are 24V or 48V nominal. Over 
 the last few years, sources of conventionally-sized 72-cell modules have 
 dried up - as cells have increased in size, most modules and most newer 
 factory production lines have either gone to 60-cell (20V) modules, or 72 
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V 
 modules in the 150-190 watt range, which are well-suited to integrating into 
 existing systems, are no longer available.
 
 60-cell modules in the common 220-250 watt range can't be added to an 
 existing system unless run through a dedicated MPPT charge controller that 
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added cost 
 of any of these controllers cancels out the low prices of the modules.
 
 Who continues to manufacture 72-cell modules? Which distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used 
 negative ground, but it's very high efficiency (and with high Voc/Vmp as 
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules, and 
 I think they make some. But we had to replace lots of failed BP modules in 
 that size range, and are hesitant to use their technology, fearing that the 
 problems may persist in the continued line.
 
 Thank you for any discussion and recommendations.
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] lithium batteries

2013-01-24 Thread jay peltz
HI All,

Is there a rough voltage range ( high/low nominal) for the lithium family of 
batteries?

I'm curious if our current range of inverters can work with these batteries, at 
least on the load side, probably not on the charging side.

thanks,

jay

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-16 Thread jay peltz
Or often science

Jay

Peltz power

Sent from my iPad

On Jan 16, 2013, at 6:50 AM, Drake drake.chamber...@redwoodalliance.org wrote:

 That is an interesting point.  The Code issue is one of definition, not of 
 function or safety. 
 
 At 04:02 PM 1/15/2013, you wrote:
 Hi August,
 
 I maintain that the WEEB is an irreversible splice.
 If you want to disconnect a WEEB from a structure, you must irreversibly 
 damage the device. It cannot be reused.
 
 Admittedly the force required to remove a WEEB is less than that required 
 for a thermal splice, but it doesn't take much force to just cut a wire 
 either.
 
 I would argue that the intent of the code is to prevent inadvertent removal 
 of the ground. You must knowingly remove a WEEB from the grounding path and 
 if you do so in the maintenance of an array, good workmanship requires that 
 you restore the connection. 
 
 Best Regards,
 Brian 
 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] GEC for Micro-Inverters and ACPV Modules

2013-01-16 Thread jay peltz
Dear John and Brian

Thanks for a great discussion. 

My question is:

If you used a WEEB to connect the inverter to the rail, is the rack rail listed 
as a GEC?
Or does it have to be listed as a GEC?

Thanks

Jay

Peltz power





Sent from my iPad

On Jan 16, 2013, at 12:09 PM, Brian Wiley btwinfin...@gmail.com wrote:

 Hi John,
 
 I don't feel that you are argumentative. I am glad for this forum and people 
 to put forth honest opinions.
 
 I think you just may not be aware of how the WEEB actually works. It is a 
 type of rivet, not just a pronged thing that makes connection as part of a 
 bolted connection.
 
 It does use a bolt to engage the part, but the teeth on the WEEB are 
 specially shaped. When the bolt is torqued, the teeth deform, similarly to a 
 rivet.
 The metal that it is connecting to mushrooms up around the tooth and the 
 tooth pinches in around the metal.
 This deforming action is what forms an exceptional electrical connection and 
 also forms an air-tight seal between the part and embedded metal to resist 
 corrosion.
 
 If you remove the bolt, the WEEB will still be connected to the metal. You 
 must forcibly remove the WEEB from the metal.
 
 Hope that clears things up for you.
 
 Best Regards,
 Brian Wiley
 
 
 
 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] off grid PV connected to generator

2013-01-15 Thread jay peltz
Hi Dan

Would like to know what they suggested besides changing it to a VFX?

Jay

Peltz power


Sent from my iPad

On Jan 15, 2013, at 1:54 PM, Dan Fink danbo...@gmail.com wrote:

 Talk to Outback. It's an easy fix, on-site.
 -- 
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342 (voicemail)
 
 
 On Tue, Jan 15, 2013 at 2:50 PM, SunHarvest e...@harvesthesun.com wrote:
 (snip)
 Further, I recently installed a GVFX for a customer. I'm hearing from 
 certain sources that the grid-tied line of inverters from Outback are not 
 designed to interface with a generator. Really??
 (snip) 
 
 
 
 
 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] mate + flexnet DC

2013-01-13 Thread jay peltz
Hi All,

Can you use a Mate 1 with only a flexnet dc?
IE no hub, or inverter or CC?

thanks,

jay
peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] XW AGS

2013-01-12 Thread jay peltz
 I wanted to update you with the AGS issue I had with an XW.

It in the end, it was unknown, settings were all correct, but after a full 
reboot of the XW and the AGS 
It all works. 

Here's to the ghost in the machine


Jay

Peltz Power


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



<    7   8   9   10   11   12   13   14   15   16   >