Covered Parking in 13R

2020-05-29 Thread John Irwin via Sprinklerforum
I have a 3-story, 13R building. Type IIB construction. On the "engineered" bid set, no sprinklers are shown in the covered parking area. This area is inside the footprint of the first floor, with 2nd floor units being located above the parking area. There are no garage doors and the parking spac

RE: Covered Parking in 13R

2020-05-29 Thread tstone52--- via Sprinklerforum
John, NFPA 13R states sprinklers are not required under a roof or deck above a carport, 6.6.5.1, (13 ed.). From your description it sounds like a Carport. NFPA 13R addresses Type V construction. That would be a question for the local AHJ to answer. Regards, G. Tim Stone G. Tim Stone Cons

RE: Covered Parking in 13R

2020-05-29 Thread Mark.Phelps via Sprinklerforum
This is outside the scope of the NFPA standards. It is in the realm of the local Building or Fire Code to determine the If required. Mark at Aero 602 820-7894 From: Sprinklerforum On Behalf Of John Irwin via Sprinklerforum Sent: Friday, May 29, 2020 2:55 AM To: sprinklerforum@lists.firesprinkle

Re: Covered Parking in 13R

2020-05-29 Thread 321 via Sprinklerforum
John, I have always put sprinklers on the parking level in a situation as you describe. The argument for sprinklers is that if one car catches fire without sprinkler protection, you lose the entire building. Over 46 years working in Florida and I have always done it...AHJ will be the final word.

Re: Covered Parking in 13R

2020-05-29 Thread John Drucker via Sprinklerforum
Are their standpipes in this building ? John Drucker From: Sprinklerforum on behalf of tstone52--- via Sprinklerforum Sent: Friday, May 29, 2020 07:46 To: sprinklerforum@lists.firesprinkler.org Cc: tston...@comcast.net Subject: RE: Covered Parking in 13R John,

RE: Covered Parking in 13R

2020-05-29 Thread John Irwin via Sprinklerforum
If you work in Florida you should know that the AHJ doesn’t have the final say. The code does. And while I agree that I would like to see sprinklers there, I need to know if they are required as this is a BID situation. John Irwin Quick Response Fire Protection “The bitterness of poor qualit

RE: Covered Parking in 13R

2020-05-29 Thread John Irwin via Sprinklerforum
No. John Irwin Quick Response Fire Protection "The bitterness of poor quality remains long after the sweetness of low price is forgotten." - Benjamin Franklin From: Sprinklerforum On Behalf Of John Drucker via Sprinklerforum Sent: Friday, May 29, 2020 8:42 AM To: sprinklerforum@lists.firespr

NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Dewayne Martinez via Sprinklerforum
Is the hanger on the pipe supplying a flexible drop to a pendant sprinkler in a ceiling still required to one that prevents upward movement? Sections 9.2.3.4.4.1,9.2.3.5.2.2 Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL Mechanical* *Building* *Integrity* W234 N2830

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
In my opinion, no. The flexible drop assembly is anchored to the ceiling. The point of this requirement is to keep the pendent sprinkler from moving upwards during activation. The flexible drop assembly accomplishes this requirement. Thanks, John John August Denhardt, PE *Vice President, Engine

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Ron Greenman via Sprinklerforum
I'd agree with John for the very same reason he thinks (intent of the requirement) no, but I'll bet there are AHJs out there that will read the rulebook differently, citing no exception stated, and without concern for intent, and say yes, you need to do it. And probably even some that agree that th

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
I will at the 2022 edition and see if we can add something. Maybe in the Annex. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread AKS-Gmail-IMAP via Sprinklerforum
All the listed flexible drop installation hardware restrain the sprinkler, but not necessarily to the ceiling. Some have gripping hardware supported by threaded rod “from the structure above". The gripping hardware is useful when the architect has some new fangled, odd ceiling design that does n

RE: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Dewayne Martinez via Sprinklerforum
Thanks everyone for the input. My fitter brought this up to me and after I read the sections I was still not sure. John’s comment makes perfect sense. Thank you, Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee,

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Jeff Garrison via Sprinklerforum
The Bracket IS the LAST hanger, per Flex manufacturers I have talked to, but, NFSA gave us an opinion that a 13" arm-over to a Flex still needs a hanger if you are over 100 psi, 'cause that's what the book says. *Jeff Garrison* *248-331-6164 - cell* On Fri, May 29, 2020 at 1:36 PM Dewayne Martin

RE: [EXTERNAL] Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread Kyle.Montgomery via Sprinklerforum
This has been addressed in the 2016 Edition: 9.2.3.4.4.4 and 9.2.3.5.2.2 both state “unless flexible sprinkler hose fittings are used”. So it doesn’t say it in 2013 Edition, but it’s clear what the intent was an the direction the code is going. -Kyle M From: Sprinklerforum On Behalf Of Jeff

Re: [EXTERNAL] Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
Yes sir - it was added for the 2016 edition of NFPA 13 and remained the same for the 2019 edition. Problem solved. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firespri

ESFR spacing

2020-05-29 Thread Matt Grise via Sprinklerforum
NFPA13 talks about shifting ESFR heads to avoid obstructions, but is there any concern with moving them when there is not an obstruction (within the spacing rules). We have a situation where a small wall bump-out effectively spaces some ESFR heads over 10', but less than 11' - along with all of

RE: Covered Parking in 13R

2020-05-29 Thread Art Tiroly via Sprinklerforum
Residential use above a parking garage changes the occupancy requirement to a mixed use and NFPA 13 design criteria is required. Therefore protect the garage. Am I on the right track here? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell

Re: ESFR spacing

2020-05-29 Thread Skyler Bilbo via Sprinklerforum
Matt, My main concern with your application would be that the section you are referring to doesn't apply to the situation you are describing. You can't apply a rule to spacing off a wall that is meant for offsetting a line due to an obstruction. Two different sections/situations. You say you ar

Re: Covered Parking in 13R

2020-05-29 Thread 321 via Sprinklerforum
I think so. I have 2 just like this that I am figuring this way13 R upstairs NFPA Parkling downstairs. John W. Farabee 561-707-5150 On Friday, May 29, 2020, 05:50:22 PM EDT, Art Tiroly via Sprinklerforum wrote: #yiv8323256408 #yiv8323256408 -- _filtered {} _filtered {}#yiv832325

RE: ESFR spacing

2020-05-29 Thread Matt Grise via Sprinklerforum
The situations causing the shift are not the same, but would the resulting protection level be the same or better? If it is ok to shift the sprinklers for an obstruction, is the protection less effective to shift without an obstruction? Matt From: Sprinklerforum On Behalf Of Skyler Bilbo vi

RE: Covered Parking in 13R

2020-05-29 Thread Art Tiroly via Sprinklerforum
Check with the AHJ. I’m not sure you can change from 13 to 13R in the same building. You can use residential rules in a 13 system of course. Do you have combustible concealed spaces in the residential? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-57

RE: Covered Parking in 13R

2020-05-29 Thread Matt Grise via Sprinklerforum
One other thing to watch – if they are considering the S2 and R occupancies to be separate buildings based on a horizontal assembly – IBC 510.2 requires that the lower areas have sprinklers – no NFPA 13 q’s needed. I got hung up on that one recently. Matt From: Sprinklerforum On Behalf Of A

Re: Covered Parking in 13R

2020-05-29 Thread Skyler Bilbo via Sprinklerforum
I don't think this has been said yet on this thread, but I think it is worth mentioning. It is not a fire sprinkler contractor's job to decide where sprinklers are required, and/or which standard is applicable (NFPA 13/13R). I know we all probably do this, but we really shouldn't. I would bet ov

RE: Covered Parking in 13R

2020-05-29 Thread Tom Duross via Sprinklerforum
Kudo’s Skylar. From: Sprinklerforum On Behalf Of Skyler Bilbo via Sprinklerforum Sent: Friday, May 29, 2020 6:57 PM To: sprinklerforum@lists.firesprinkler.org Cc: Skyler Bilbo Subject: Re: Covered Parking in 13R I don't think this has been said yet on this thread, but I think it is worth

Re: ESFR spacing

2020-05-29 Thread Skyler Bilbo via Sprinklerforum
Any argument to what should be equivalent to the standard doesn't matter if the standard blatantly doesn't allow it (unless you are a PE and want to sign off on it, and get the AHJ to do so, as well). Feel free to try and change the standard. By your logic, you could take the small room rule, whi

Re: ESFR spacing

2020-05-29 Thread Matt Grise via Sprinklerforum
I may have mis-stated the scenario. The sprinklers along the wall would be 5-0 from the wall as allowed by code. The next line of sprinklers would be 10-9 away, with 9' spacing along the line as allowed by code...if the line was moved to accommodate an obstruction. What the code is saying is li

RE: ESFR spacing

2020-05-29 Thread Kyle.Montgomery via Sprinklerforum
Matt, For what it’s worth (probably less than $0.02), I agree with you that it should provide an equivalent level of protection to be, say 5’-6” off of the wall as it would be if you were 11’-0” between sprinkler heads due to some obstruction. I suppose someone could make a strong argument that