What's your expected flow rate? You could always tell the GC that they need to
rent you an empty pool truck to discharge into if they don't want the driveway
to get water on it. 1500' of hose should be a non-starter for you.
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Brian
is to not double count standpipes on each side of the horizontal
exit it would probably be best to have a specific section stating as such in
10.6.1.1.
Sincerely,
Eric Rieve, SET
Rieve Fire Protection
From: Steve Leyton
Sent: Wednesday, April 3, 2024 11:57 AM
To: Discussion list on issues relating
connection is being served from a separate
standpipe.”
It really does make sense though to consider the hose connections on opposite
sides of a horizonal exit to be a single standpipe. I would be interested in
getting other readers thoughts on this.
Sincerely,
Eric Rieve, SET
Rieve Fire Protection
to the second FDC which would likely be pretty far away from the
street.
Hope this helps!
Sincerely,
Eric Rieve, SET
Rieve Fire Protection
From: rimrock.design.servi...@gmail.com
Sent: Wednesday, April 3, 2024 9:43 AM
To: 'Discussion list on issues relating to automatic fire sprinklers
Todd,
My 2002 copies of 13 and 13R have it as an option under specially listed pipe,
NFPA 13- section: 6.3.6.1, and NFPA 13R-section: 5.2.2.2.
Hope this helps!
Sincerely,
Eric Rieve, SET
Rieve Fire Protection
From: Fpdcdesign
Sent: Monday, March 4, 2024 10:36 AM
To: Sprinklerforum
Subject
.
So, your test-header will need to accommodate the combined flow.
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Fpdcdesign
Sent: Monday, January 29, 2024 11:51 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Fire Pump testing
nominal k-factor since NFPA
13 allows the actual outlet to be anywhere from 10.7k-11.7k. Maybe Gem just
wanted to be very clear on the exact k-factor for calculations, especially if
it is a non-standard thread size.
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
like that?
Yeesh.
Eric Rieve
Rieve Fire Protection
_
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
LOL guess I’m not quite as quick as Kevin just yet.
From: Steve Leyton
Sent: Friday, November 10, 2023 2:12 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Flow test adjustment formula
Yep.
From: Eric Rieve mailto:e...@rievefire.com>>
for (Px)
Qr= The flow measured during the test correlating with Pr
Though please run the calc through a known water supply calc just to make sure
its correct before you use it on an un-known.
Hope this helps!
Thanks,
Eric Rieve, SET
Rieve Fire Protection
From: Steve Leyton
Sent: Friday
175psi. So, while you
may pick a 120psi outlet pressure while flowing 750gpm, the extra play in the
curve should allow the valve to maintain an outlet pressure below 175psi when
being tested individually at 250gpm.
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Micah Davis
Sent
Funny enough I was told the same a few years ago. His reasoning was that the
uneven nature of the foam application could cause obstructions that weren't
readily apparent so extra clearance was warranted.
From: Brian Harris
Sent: Thursday, September 28, 2023 2:48 PM
To:
from your
city connection.
Caveat: The above is just based on a quick read of the question and relevant
code sections, and not based on past personal experience.
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Anthony Carrizosa
Sent: Monday, September 25, 2023 12:45 PM
To: Discussion
tively to round out the rest of chapters.
[A close up of text]
Hope this helps!
Eric Rieve, SET
Rieve Fire Protection
From: Brian Harris
Sent: Monday, September 11, 2023 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA
Eric-
Brian,
Yes, it does per the "general storage applications" segment of the code section.
Eric Rieve, SET
Rieve Fire Protection
From: Brian Harris
Sent: Monday, September 11, 2023 11:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] CLASS I-IV / CMDA
Would 12
; stainless steel nipples and ¾" stainless steel
couplings to raise those heads up? The ¾" weld-o-lets aren't stainless, but the
relevant section in NFPA 13 only mentions pipe and not fittings. Assuming it
calc's out ok hydraulically of course.
Eric Rieve
Rieve Fire Protection
From: Travis Mack
S
on the suction side? I’d want
to put a gauge somewhere further upstream so you can confirm the pressure loss
you are getting along your underground suction pipe.
Also definitely add a gauge on the inlet side of your backflow to make sure
something isn’t wrong there.
Hope this helps,
Eric RIeve
From
” of straight run obviously isn’t great or
to code, but it’s not like the elbow is directly attached to the suction flange
either.
Backflow has OS valves right?
Hope this helps,
Eric Rieve
Rieve Fire Protection
From: Fpdcdesign
Sent: Friday, July 14, 2023 12:37 PM
To: Sprinklerforum
Subject
discharge location.
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: Prahl, Craig
Sent: Wednesday, July 12, 2023 4:37 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Forward Flow testing valve arrangements
Providing an array of 2.5” hose
, then congratulations! In this case you do
not need a hydraulic placard and just need to install a sign the states that
the system was installed via the pipe schedule method.
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: Bobby Welch
Sent: Wednesday, July 12, 2023 2:30 PM
To: Discussion list
easy to go down the storage hazard
protection rabbit hole, especially if you do a lot of design work in that
niche, even though the goals of the two standards are significantly different.
Hope this helps!
Eric Rieve
Rieve Fire Protection
-Original Message-
From: Sean Lockyer
Sent: Wedn
to see if that makes things match.
Just think of this as a great opportunity to sharpen your manual calculation
skillset
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: August Hoffman
Sent: Wednesday, June 7, 2023 5:41 PM
To: Discussion list on issues relating to automatic fire sprinklers
connection.
And yes, I am pretty sure you'd use static pressure (though I think I recall
being asked once what my expected suction pressure at 150% flow would be on a
system with very low incoming pressure)
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: Brian Harris
Sent: Friday, May
the IBC was
used as the building code this would have allowed the installer to bypass the
limitation in NFPA-13 anyways, so it was for the best that the language in both
books was kept correlated.
Eric Rieve
From: James Litvak
Sent: Thursday, April 6, 2023 10:52 AM
To: AFSA Sprinkler Forum
you hang really good signage
stating what systems they feed.
Hope this helps.
Eric Rieve
Rieve Fire Protection
From: Kyle.Montgomery
Sent: Wednesday, April 5, 2023 11:12 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: [EXTERNAL] Re
I wouldn’t rule out residential sprinklers completely Todd.
Here is what the NFPA 13 first draft report for 2024 has for a revision for
adding annex material to the definition of a dwelling unit:
A.3.3.65 Common spaces such as a lounges, group cooking facilities, and group
bathrooms that are
ent.”
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: d...@engfirepro.com
Sent: Monday, March 13, 2023 7:53 PM
To: 'Discussion list on issues relating to automatic fire sprinklers'
Subject: [Sprinklerforum] Re: Combining dry system drains
Now that is interesting…
The wording of the code
someone could walk below them
without needing to crawl.
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: Rick Matsuda
Sent: Wednesday, March 8, 2023 10:21 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: Low Decks
As an old AHJ, I
Bill,
In NFPA 13-2016 your best reference is going to be 22.8 which is an excerpt
from NFPA 45. You will be either Ord 1 or 2. This may or may not conflict with
any IBC requirements though if that is the regional governing code.
Eric Rieve
Rieve Fire Protection
From: BILL MENSTER
Sent
that they are a
similar hazard and gives you a solid reasoning if you need to "show your work"
since apparatus bays are specifically designated in NFPA 13.
Hope this helps!
Eric Rieve
Rieve Fire Protection
From: Brian Harris
Sent: Thursday, February 16, 2023 2:54 PM
To: Discu
If the zone control has a control valve, check valve, drain, flow, and gauge
then yep. In this case though you generally wouldn’t have that single “system
riser” before those 4 assemblies though. You’d either just have your backflow
or fire pump setup feeding the 4 zones in a manifold
Anthony,
Looking on NFPALink for NFPA 13-2019 20.4.5.4 (5) says expanded plastics. Are
you looking in a hardcopy? Double check if you don’t mind.
Eric
Rieve Fire Protection
From: Anthony Carrizosa
Sent: Wednesday, February 1, 2023 11:51 AM
To: Discussion list on issues relating to automatic
of expanded plastics. So since the carton is the
target object of the rule I do believe you can count the air as part of your
volume. This isn’t an interpretation I’ve specifically had to deal with in the
past though, so hopefully someone else can chime in.
Hope this helps!
Eric Rieve
Rieve Fire
putting some theoretical additional flow on a dry system branchline that can’t
actually use it.
That’s my two cents, let me know what you thin. I’m looking forward to being
schooled if I’m totally off base on this interpretation approach!
Eric Rieve
Rieve Fire Protection
From: Fpdcdesign
Sent
, but that
would be for the engineer to math out instead of you.
Eric
Rieve Fire Protection
Eric Rieve
Rieve Fire Protection
From: Dennis Wilson
Sent: Thursday, December 29, 2022 2:53:22 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject
r accurate waterflow measurement then you can prove
your assembly meets the requirements.
Hope this helps!
Eric
Rieve Fire Protection
From: Dennis Wilson
Sent: Wednesday, December 14, 2022 12:01 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforu