[Sprinklerforum] Re: 1500' for Standpipe Test

2024-04-04 Thread Eric Rieve
What's your expected flow rate? You could always tell the GC that they need to rent you an empty pool truck to discharge into if they don't want the driveway to get water on it. 1500' of hose should be a non-starter for you. Hope this helps! Eric Rieve, SET Rieve Fire Protection From: Brian

[Sprinklerforum] Re: Standpipe Calculations

2024-04-03 Thread Eric Rieve
is to not double count standpipes on each side of the horizontal exit it would probably be best to have a specific section stating as such in 10.6.1.1. Sincerely, Eric Rieve, SET Rieve Fire Protection From: Steve Leyton Sent: Wednesday, April 3, 2024 11:57 AM To: Discussion list on issues relating

[Sprinklerforum] Re: Standpipe Calculations

2024-04-03 Thread Eric Rieve
connection is being served from a separate standpipe.” It really does make sense though to consider the hose connections on opposite sides of a horizonal exit to be a single standpipe. I would be interested in getting other readers thoughts on this. Sincerely, Eric Rieve, SET Rieve Fire Protection

[Sprinklerforum] Re: Standpipe Calculations

2024-04-03 Thread Eric Rieve
to the second FDC which would likely be pretty far away from the street. Hope this helps! Sincerely, Eric Rieve, SET Rieve Fire Protection From: rimrock.design.servi...@gmail.com Sent: Wednesday, April 3, 2024 9:43 AM To: 'Discussion list on issues relating to automatic fire sprinklers

[Sprinklerforum] Re: Polybutylene pipe

2024-03-04 Thread Eric Rieve
Todd, My 2002 copies of 13 and 13R have it as an option under specially listed pipe, NFPA 13- section: 6.3.6.1, and NFPA 13R-section: 5.2.2.2. Hope this helps! Sincerely, Eric Rieve, SET Rieve Fire Protection From: Fpdcdesign Sent: Monday, March 4, 2024 10:36 AM To: Sprinklerforum Subject

[Sprinklerforum] Re: Fire Pump testing procedures

2024-01-29 Thread Eric Rieve
. So, your test-header will need to accommodate the combined flow. Hope this helps! Eric Rieve, SET Rieve Fire Protection From: Fpdcdesign Sent: Monday, January 29, 2024 11:51 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Fire Pump testing

[Sprinklerforum] Re: F892 K11.4 Upright Sprinkler

2024-01-22 Thread Eric Rieve
nominal k-factor since NFPA 13 allows the actual outlet to be anywhere from 10.7k-11.7k. Maybe Gem just wanted to be very clear on the exact k-factor for calculations, especially if it is a non-standard thread size. Hope this helps! Eric Rieve, SET Rieve Fire Protection

[Sprinklerforum] AFSA ITM Connection - Sprinkler head security cameras

2023-11-16 Thread Eric Rieve
like that? Yeesh. Eric Rieve Rieve Fire Protection _ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

[Sprinklerforum] Re: Flow test adjustment formula

2023-11-10 Thread Eric Rieve
LOL guess I’m not quite as quick as Kevin just yet. From: Steve Leyton Sent: Friday, November 10, 2023 2:12 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Flow test adjustment formula Yep. From: Eric Rieve mailto:e...@rievefire.com>>

[Sprinklerforum] Re: Flow test adjustment formula

2023-11-10 Thread Eric Rieve
for (Px) Qr= The flow measured during the test correlating with Pr Though please run the calc through a known water supply calc just to make sure its correct before you use it on an un-known. Hope this helps! Thanks, Eric Rieve, SET Rieve Fire Protection From: Steve Leyton Sent: Friday

[Sprinklerforum] Re: Pressure Regulating Valves Residual Pressures

2023-10-31 Thread Eric Rieve
175psi. So, while you may pick a 120psi outlet pressure while flowing 750gpm, the extra play in the curve should allow the valve to maintain an outlet pressure below 175psi when being tested individually at 250gpm. Hope this helps! Eric Rieve, SET Rieve Fire Protection From: Micah Davis Sent

[Sprinklerforum] Re: Spray Foam Insulation

2023-09-28 Thread Eric Rieve
Funny enough I was told the same a few years ago. His reasoning was that the uneven nature of the foam application could cause obstructions that weren't readily apparent so extra clearance was warranted. From: Brian Harris Sent: Thursday, September 28, 2023 2:48 PM To:

[Sprinklerforum] Re: Standpipe PRV Question

2023-09-25 Thread Eric Rieve
from your city connection. Caveat: The above is just based on a quick read of the question and relevant code sections, and not based on past personal experience. Hope this helps! Eric Rieve, SET Rieve Fire Protection From: Anthony Carrizosa Sent: Monday, September 25, 2023 12:45 PM To: Discussion

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Eric Rieve
tively to round out the rest of chapters. [A close up of text] Hope this helps! Eric Rieve, SET Rieve Fire Protection From: Brian Harris Sent: Monday, September 11, 2023 11:32 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CLASS I-IV / CMDA Eric-

[Sprinklerforum] Re: CLASS I-IV / CMDA

2023-09-11 Thread Eric Rieve
Brian, Yes, it does per the "general storage applications" segment of the code section. Eric Rieve, SET Rieve Fire Protection From: Brian Harris Sent: Monday, September 11, 2023 11:19 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] CLASS I-IV / CMDA Would 12

[Sprinklerforum] Re: 3/4" Nipple

2023-08-09 Thread Eric Rieve
; stainless steel nipples and ¾" stainless steel couplings to raise those heads up? The ¾" weld-o-lets aren't stainless, but the relevant section in NFPA 13 only mentions pipe and not fittings. Assuming it calc's out ok hydraulically of course. Eric Rieve Rieve Fire Protection From: Travis Mack S

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Eric Rieve
on the suction side? I’d want to put a gauge somewhere further upstream so you can confirm the pressure loss you are getting along your underground suction pipe. Also definitely add a gauge on the inlet side of your backflow to make sure something isn’t wrong there. Hope this helps, Eric RIeve From

[Sprinklerforum] Re: Elbows in pump suction

2023-07-14 Thread Eric Rieve
” of straight run obviously isn’t great or to code, but it’s not like the elbow is directly attached to the suction flange either. Backflow has OS valves right? Hope this helps, Eric Rieve Rieve Fire Protection From: Fpdcdesign Sent: Friday, July 14, 2023 12:37 PM To: Sprinklerforum Subject

[Sprinklerforum] Re: Forward Flow testing valve arrangements

2023-07-13 Thread Eric Rieve
discharge location. Hope this helps! Eric Rieve Rieve Fire Protection From: Prahl, Craig Sent: Wednesday, July 12, 2023 4:37 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Forward Flow testing valve arrangements Providing an array of 2.5” hose

[Sprinklerforum] Re: Old Pipe Scheduled Systems

2023-07-12 Thread Eric Rieve
, then congratulations! In this case you do not need a hydraulic placard and just need to install a sign the states that the system was installed via the pipe schedule method. Hope this helps! Eric Rieve Rieve Fire Protection From: Bobby Welch Sent: Wednesday, July 12, 2023 2:30 PM To: Discussion list

[Sprinklerforum] Re: Optional sprinkler protection in garage without sprinklers elsewhere

2023-07-05 Thread Eric Rieve
easy to go down the storage hazard protection rabbit hole, especially if you do a lot of design work in that niche, even though the goals of the two standards are significantly different. Hope this helps! Eric Rieve Rieve Fire Protection -Original Message- From: Sean Lockyer Sent: Wedn

[Sprinklerforum] Re: AutoSprink Vs HydraCalc

2023-06-07 Thread Eric Rieve
to see if that makes things match. Just think of this as a great opportunity to sharpen your manual calculation skillset  Hope this helps! Eric Rieve Rieve Fire Protection From: August Hoffman Sent: Wednesday, June 7, 2023 5:41 PM To: Discussion list on issues relating to automatic fire sprinklers

[Sprinklerforum] Re: Pump Suction Pressure

2023-05-26 Thread Eric Rieve
connection. And yes, I am pretty sure you'd use static pressure (though I think I recall being asked once what my expected suction pressure at 150% flow would be on a system with very low incoming pressure) Hope this helps! Eric Rieve Rieve Fire Protection From: Brian Harris Sent: Friday, May

[Sprinklerforum] Re: Sprinklers in Bathrooms 8.15.8.1.1

2023-04-06 Thread Eric Rieve
the IBC was used as the building code this would have allowed the installer to bypass the limitation in NFPA-13 anyways, so it was for the best that the language in both books was kept correlated. Eric Rieve From: James Litvak Sent: Thursday, April 6, 2023 10:52 AM To: AFSA Sprinkler Forum

[Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

2023-04-05 Thread Eric Rieve
you hang really good signage stating what systems they feed. Hope this helps. Eric Rieve Rieve Fire Protection From: Kyle.Montgomery Sent: Wednesday, April 5, 2023 11:12 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: [EXTERNAL] Re

[Sprinklerforum] Re: Too many sprinklers in the bathroom

2023-03-27 Thread Eric Rieve
I wouldn’t rule out residential sprinklers completely Todd. Here is what the NFPA 13 first draft report for 2024 has for a revision for adding annex material to the definition of a dwelling unit: A.3.3.65 Common spaces such as a lounges, group cooking facilities, and group bathrooms that are

[Sprinklerforum] Re: Combining dry system drains

2023-03-14 Thread Eric Rieve
ent.” Hope this helps! Eric Rieve Rieve Fire Protection From: d...@engfirepro.com Sent: Monday, March 13, 2023 7:53 PM To: 'Discussion list on issues relating to automatic fire sprinklers' Subject: [Sprinklerforum] Re: Combining dry system drains Now that is interesting… The wording of the code

[Sprinklerforum] Re: Low Decks

2023-03-08 Thread Eric Rieve
someone could walk below them without needing to crawl. Hope this helps! Eric Rieve Rieve Fire Protection From: Rick Matsuda Sent: Wednesday, March 8, 2023 10:21 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Low Decks As an old AHJ, I

[Sprinklerforum] Re: High School Lab rooms

2023-03-02 Thread Eric Rieve
Bill, In NFPA 13-2016 your best reference is going to be 22.8 which is an excerpt from NFPA 45. You will be either Ord 1 or 2. This may or may not conflict with any IBC requirements though if that is the regional governing code. Eric Rieve Rieve Fire Protection From: BILL MENSTER Sent

[Sprinklerforum] Re: Fire Station Apparatus Bay

2023-02-16 Thread Eric Rieve
that they are a similar hazard and gives you a solid reasoning if you need to "show your work" since apparatus bays are specifically designated in NFPA 13. Hope this helps! Eric Rieve Rieve Fire Protection From: Brian Harris Sent: Thursday, February 16, 2023 2:54 PM To: Discu

[Sprinklerforum] Re: Zone valves and maximum area

2023-02-15 Thread Eric Rieve
If the zone control has a control valve, check valve, drain, flow, and gauge then yep. In this case though you generally wouldn’t have that single “system riser” before those 4 assemblies though. You’d either just have your backflow or fire pump setup feeding the 4 zones in a manifold

[Sprinklerforum] Re: Definition of Volume

2023-02-01 Thread Eric Rieve
Anthony, Looking on NFPALink for NFPA 13-2019 20.4.5.4 (5) says expanded plastics. Are you looking in a hardcopy? Double check if you don’t mind. Eric Rieve Fire Protection From: Anthony Carrizosa Sent: Wednesday, February 1, 2023 11:51 AM To: Discussion list on issues relating to automatic

[Sprinklerforum] Re: Definition of Volume

2023-02-01 Thread Eric Rieve
of expanded plastics. So since the carton is the target object of the rule I do believe you can count the air as part of your volume. This isn’t an interpretation I’ve specifically had to deal with in the past though, so hopefully someone else can chime in. Hope this helps! Eric Rieve Rieve Fire

[Sprinklerforum] Re: Another phantom flow question

2023-01-13 Thread Eric Rieve
putting some theoretical additional flow on a dry system branchline that can’t actually use it. That’s my two cents, let me know what you thin. I’m looking forward to being schooled if I’m totally off base on this interpretation approach! Eric Rieve Rieve Fire Protection From: Fpdcdesign Sent

[Sprinklerforum] Re: Pipe Stands

2022-12-29 Thread Eric Rieve
, but that would be for the engineer to math out instead of you. Eric Rieve Fire Protection Eric Rieve Rieve Fire Protection From: Dennis Wilson Sent: Thursday, December 29, 2022 2:53:22 PM To: Discussion list on issues relating to automatic fire sprinklers Subject

[Sprinklerforum] Re: BFP on underground supply

2022-12-14 Thread Eric Rieve
r accurate waterflow measurement then you can prove your assembly meets the requirements. Hope this helps! Eric Rieve Fire Protection From: Dennis Wilson Sent: Wednesday, December 14, 2022 12:01 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforu