Look at 905.3.4 (03 ed). It says: Class III standpipe with outlets on both sides of the stage and hose for the 1.5 in outlet shall shall have sufficient length to provide protection of the stage (which I would say either side should reach the other side - would be nasty to go charging out there nozzle in hand and hit the end half way across the stage LOOKING LIKE CHARLIE BROWN TRYING TO KICK THE FOOTBALL).

The question I have is the the allowance to supply it from the sprinkler system. Is the water demand combined since it is more than the common riser combined system (where it is NOT combined)?

Roland

On Mar 26, 2007, at 8:16 AM, Thom McMahon wrote:

We have a stage of 1066 SF , no Proscenium, (over the 1000 SF for hose stations required by 2003 IBC) Is there any info on the following: 1) Minimum hose in Cabinet for a stage only 55 FT across (50' 75' or 100') 2) With hose stations on both sides of stage, should we calc each at 250 Gpm, since the highest elevation is the same, thereby getting the 500 Gpm total at the highest elevation?
3) Any other special considerations for these hose stations, or stage?

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to