Roland, Just to make sure (for Thom's sake)
In reading the exception, if the building is sprinklered throughout that only an 1 1/2" Hose Station in accordance with NFPA 13 Section 8.16.5 OR in accordance with NFPA 14 for a Class II or III. If you go the NFPA 13 route, then the water demands from NFPA 14 are not required. Just the hose allowance at the point of connection. I gotcha. Ken -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Monday, March 26, 2007 12:56 PM To: [email protected] Subject: Re: Stage Hose Stations Look at this again. It's required to be a Class III. IN 2006 The exception for fully sprinklered buildings is just a 1-1/2 outlet and it states it's now a Class II or III. As such, manual (being limited to a Class I in other than high-rise) is a no-go. Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum