If you take the hoses off per the exception in 14, then it becomes a POC for responders and they're going to be connected to the system. I'm not disagreeing with you about the intent or letter of the standard regarding Class II water supply arrangement and I oversimplified my response.
If the serving fire dept. lets you take the exception for a fully sprinklered building and furnish just the valve and not the hose, then there should be no performance issues with a manual/wet. Steve -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Roland Huggins Sent: Monday, March 26, 2007 8:56 AM To: [email protected] Subject: Re: Stage Hose Stations Look at this again. It's required to be a Class III. IN 2006 The exception for fully sprinklered buildings is just a 1-1/2 outlet and it states it's now a Class II or III. As such, manual (being limited to a Class I in other than high-rise) is a no-go. Roland On Mar 26, 2007, at 9:33 AM, Steve Leyton wrote: > It can most certainly be manual. > > Steve > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] Behalf Of Ken > Holsopple > Sent: Monday, March 26, 2007 8:28 AM > To: [email protected] > Subject: RE: Stage Hose Stations > > > > Thom, Steve, and Roland, > > [F] 905.3.4 Stages. > Stages greater than 1,000 square feet in area (93m2) shall be > equipped with > a Class III wet standpipe system with 1.5-inch and 2.5-inch > (38mmand 64 mm) > hose connections on each side of the stage. > > Could this be a MANUAL wet standpipe? In other words if them there > fire guys > and girls are in the building, has the pumper truck hooked up to > the FDC > yet? I would hope so. > > I don't see the word AUTOMATIC in the IBC verbage. Might save the > owner a > fire pump perhaps? > > Ken > > > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of > Steve Leyton > Sent: Monday, March 26, 2007 12:20 PM > To: [email protected] > Subject: RE: Stage Hose Stations > > A combined system needs to be valved so that sprinklers and > standpipe(s) can > be independently controlled, whether it's two separate risers or a > combination standpipe riser with sprinkler connections however it's > zoned. > And since it's a code thing regarding the hoses, can we take the > exception > from 14 for a fully sprinklered building, where you simply omit the > hose in > favor of a 2.5" x 1.5" reducer and cap? > > I think that the presence of hose stations on stages and in A-2 and > A-3 > occupancies is not congruent with the accepted practice of encouraging > EVERYONE in the building to leave in case of a fire alarm or sign > of fire. > I would ask the serving fire dept. if they can live with points of > connection and bring their hose for mop up. > > Steve L. > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
