It can most certainly be manual.  

Steve

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Ken
Holsopple
Sent: Monday, March 26, 2007 8:28 AM
To: [email protected]
Subject: RE: Stage Hose Stations



Thom, Steve, and Roland,

[F] 905.3.4 Stages.
Stages greater than 1,000 square feet in area (93m2) shall be equipped with
a Class III wet standpipe system with 1.5-inch and 2.5-inch (38mmand 64 mm)
hose connections on each side of the stage.

Could this be a MANUAL wet standpipe? In other words if them there fire guys
and girls are in the building, has the pumper truck hooked up to the FDC
yet? I would hope so.

I don't see the word AUTOMATIC in the IBC verbage. Might save the owner a
fire pump perhaps?

Ken



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Monday, March 26, 2007 12:20 PM
To: [email protected]
Subject: RE: Stage Hose Stations

A combined system needs to be valved so that sprinklers and standpipe(s) can
be independently controlled, whether it's two separate risers or a
combination standpipe riser with sprinkler connections however it's zoned.
And since it's a code thing regarding the hoses, can we take the exception
from 14 for a fully sprinklered building, where you simply omit the hose in
favor of a 2.5" x 1.5" reducer and cap?

I think that the presence of hose stations on stages and in A-2 and A-3
occupancies is not congruent with the accepted practice of encouraging
EVERYONE in the building to leave in case of a fire alarm or sign of fire.
I would ask the serving fire dept. if they can live with points of
connection and bring their hose for mop up.

Steve L.




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to