A combined system needs to be valved so that sprinklers and standpipe(s) can be 
independently controlled, whether it's two separate risers or a combination 
standpipe riser with sprinkler connections however it's zoned.   And since it's 
a code thing regarding the hoses, can we take the exception from 14 for a fully 
sprinklered building, where you simply omit the hose in favor of a 2.5" x 1.5" 
reducer and cap?

I think that the presence of hose stations on stages and in A-2 and A-3 
occupancies is not congruent with the accepted practice of encouraging EVERYONE 
in the building to leave in case of a fire alarm or sign of fire.   I would ask 
the serving fire dept. if they can live with points of connection and bring 
their hose for mop up.

Steve L.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Roland
Huggins
Sent: Monday, March 26, 2007 7:38 AM
To: [email protected]
Subject: Re: Stage Hose Stations


Look at 905.3.4 (03 ed).  It says: Class III standpipe with outlets  
on both sides of the stage and hose for the 1.5 in outlet shall shall  
have sufficient length to provide protection of the stage (which I  
would say either side should reach the other side - would be nasty to  
go charging out there nozzle in hand and hit the end half way across  
the stage LOOKING LIKE CHARLIE BROWN TRYING TO KICK THE FOOTBALL).

The question I have is the the allowance to supply it from the  
sprinkler system.  Is the water demand combined since it is more than  
the common riser combined system (where it is NOT combined)?

Roland

On Mar 26, 2007, at 8:16 AM, Thom McMahon wrote:

> We have a stage of 1066 SF , no Proscenium, (over the 1000 SF for  
> hose stations required by 2003 IBC) Is there any info on the  
> following:
> 1) Minimum hose in Cabinet for a stage only 55 FT across (50' 75'  
> or 100')
> 2) With hose stations on both sides of stage, should we calc each  
> at 250 Gpm, since the highest elevation is the same, thereby  
> getting the 500 Gpm total at the highest elevation?
> 3) Any other special considerations for these hose stations, or stage?
>
> Thom McMahon
> Firetech, Inc.
> 2560 Copper Ridge Dr
> Steamboat Springs, CO 80488-2136
> Tel: 970-879-7952
> Fax: 970-879-7926
> ----- Original Message -----
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to