I think the key phrases here are "cleaned thoroughly" and "somehow" and the every popular "dormant salmonella".

At 04:49 PM 4/5/2007, you wrote:
 OMAHA, Neb. - ConAgra Foods said Thursday that moisture from a leaky roof
and faulty sprinkler was the source of the salmonella bacteria that
contaminated peanut butter at its Georgia plant last year, sickening more
than 400 people nationwide.

Childs said the company traced the salmonella outbreak to three problems at
its Sylvester, Ga., plant last August.

The plant's roof leaked during a rainstorm, and the sprinkler system went
off twice because of a faulty sprinkler, which was repaired.

The moisture from those three events mixed with dormant salmonella bacteria
in the plant that Childs said likely came from raw peanuts and peanut dust.

She said the plant was cleaned thoroughly after the roof leak and sprinkler
problem, but the salmonella remained and somehow came in contact with peanut
butter before it was packaged.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com