And these same nit wits don't care about sinks and toilets, severe weather,
roof leaks, electrical issues, floods and all the other possible causes of
damage.  When I ask if they considered all the other possible sources of
damage or interruption with fire or sprinklers being among the least
probable they usually put it in the new context and drop the issue.  Or at
least stop pushing to spend the owner's money (vs. theirs) and compromise on
a concealer and high temp.  

Bigger rooms with high value critical infrastructure for a mutli-million
business then maybe DIPA.  But these are usually multiple redundant remote
systems and thus any one site is not important and they accept the risk all
3 (or more) won't have problems at the same time.  

I'm not sure what John Drucker means about IFC 904.2. But be careful about
substituting alternate agents for sprinklers.  904.2 ('00 ed.) last sentence
may mean if the sprinklers are not in the room (closet) it is an
unsprinklered building.  The only exceptions are in 903.3.1.1.1 and I don't
see server rooms covered.  At least the way I read it alternate agents are
not sprinklers.         

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 05, 2007 2:22 PM
To: [email protected]
Subject: RE: Server Closet

The dry sidewall might appease them if all they were worried about was
an intermittent drip.  What I hear more often is the fear of someone
busting the head and millions of gallons of water dumping into the
closet resulting in numerous IT personnel drownings and electronic
equipment getting wet and ruined.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Thursday, April 05, 2007 3:15 PM
To: [email protected]
Subject: RE: Server Closet

Thanks.
One of my thoughts to offer them was a dry type sidewall.
I can get it set about 10" below the steel deck and still hide the pipe
above the corridor drop ceiling.
Maybe in a 360 degree rating?  It would keep the water (wata) out of the
room.

Tom

Dual Interlock Pre-Action?

For one head in a closet?  YIPERS!


DIPA??
In my best Sherman: "Gee Mr. Peabody, what's that?"

Tom

Sounds like they're concerned with water damage and not mission
continuity.  I would recommend a DIPA system.  Either way, it seems like
a lot of effort for one sprinkler.

Inergen would likely require pressure relief venting.

Ray Schmid

I was wondering if I could get recommendations of advice to give a
client.
Their IT guy is bugging them about a head we put in a server closet.
It's just a 6' w x 3' deep closet with their rack and a little ductless
ac unit.
No raised floor, liebert or big ups equipment and certainly not sealed.
I offered high temp head but they're scared about water (wata).
Should I suggest total flooding inergen?  Low temp rate of rise heat
detector?
I have to have an exhaust system installed with inergen, right?
I think they'd have to enclose the closet to keep in the gas.

Thanks,

Tom Duross
Go Red Sox



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]