Presuming you were going to use a pre-action valve why would anyone
use a DIPA in anything other than a freezer warehouse? Wouldn't a SIPA
give you the same degree of protection anywhere that freezing the
water in the pipes due to accidental tripping wasn't a concern? And
for far less cost and complexity. Just a question since this
pre-action thing popped up again and no one seems to even consider
less than DIPA in any application.

On 4/5/07, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote:
George,
Like if you had put those pipe labels with the directional arrows on
them you wouldn't like need to worry about gravity, the water will like
know where to go.

Geez, rookie.

LOL



Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George
Church
Sent: Thursday, April 05, 2007 4:48 PM
To: [email protected]
Subject: RE: Server Closet

We try to go with high-temp concealed heads, too- K.I.S.S. instead of
DIPA, or a basketball of halon/purpleK with a spkr stuck in it
(CeaseFire).

Recently bid a doozie- 15,000 sf emergency services bldg for the county.
2 DIPA, one rm 9 hds, 1 was 12. FM200 in another, wet throughout the
rest.
Now the good part- dry uprights were shown to protect the attic- they'd
be 20' long, and pitched to be perpendicular to the 4/12 roof!!!
Realizing their mistake, they issued an addendum to provide a dry-pipe
system in the attic, except DIPA above the 3 rooms listed above. 4
systems in the attic!

Icing on the cake- tank buried outside, atmospheric vent at grade, water
to ignore gravity and jump up into the VI pump. Naturally we had to put
a transfer switch on it, since power (and the building) would be lost
before any water came out.

$22/sf and it wouldn't work (except the FM 200). Sealed by a PE.

Why would you stack kindling atop a bulletproof concept?

glc


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Thursday, April 05, 2007 4:25 PM
To: [email protected]
Subject: RE: Server Closet

And these same nit wits don't care about sinks and toilets, severe
weather, roof leaks, electrical issues, floods and all the other
possible causes of damage.  When I ask if they considered all the other
possible sources of damage or interruption with fire or sprinklers being
among the least probable they usually put it in the new context and drop
the issue.  Or at least stop pushing to spend the owner's money (vs.
theirs) and compromise on a concealer and high temp.

Bigger rooms with high value critical infrastructure for a mutli-million
business then maybe DIPA.  But these are usually multiple redundant
remote systems and thus any one site is not important and they accept
the risk all
3 (or more) won't have problems at the same time.

I'm not sure what John Drucker means about IFC 904.2. But be careful
about substituting alternate agents for sprinklers.  904.2 ('00 ed.)
last sentence may mean if the sprinklers are not in the room (closet) it
is an unsprinklered building.  The only exceptions are in 903.3.1.1.1
and I don't see server rooms covered.  At least the way I read it
alternate agents are
not sprinklers.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69
        Waverly, MN 55390

Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 05, 2007 2:22 PM
To: [email protected]
Subject: RE: Server Closet

The dry sidewall might appease them if all they were worried about was
an intermittent drip.  What I hear more often is the fear of someone
busting the head and millions of gallons of water dumping into the
closet resulting in numerous IT personnel drownings and electronic
equipment getting wet and ruined.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Thursday, April 05, 2007 3:15 PM
To: [email protected]
Subject: RE: Server Closet

Thanks.
One of my thoughts to offer them was a dry type sidewall.
I can get it set about 10" below the steel deck and still hide the pipe
above the corridor drop ceiling.
Maybe in a 360 degree rating?  It would keep the water (wata) out of the
room.

Tom

Dual Interlock Pre-Action?

For one head in a closet?  YIPERS!


DIPA??
In my best Sherman: "Gee Mr. Peabody, what's that?"

Tom

Sounds like they're concerned with water damage and not mission
continuity.  I would recommend a DIPA system.  Either way, it seems like
a lot of effort for one sprinkler.

Inergen would likely require pressure relief venting.

Ray Schmid

I was wondering if I could get recommendations of advice to give a
client.
Their IT guy is bugging them about a head we put in a server closet.
It's just a 6' w x 3' deep closet with their rack and a little ductless
ac unit.
No raised floor, liebert or big ups equipment and certainly not sealed.
I offered high temp head but they're scared about water (wata).
Should I suggest total flooding inergen?  Low temp rate of rise heat
detector?
I have to have an exhaust system installed with inergen, right?
I think they'd have to enclose the closet to keep in the gas.

Thanks,

Tom Duross
Go Red Sox



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to