The NFPA committee intent is for the top valve to be left open... And they indicate as much in the commentary of the NFPA-13 handbook.
The condensate nipple is required to collect condensate and other moisture from the system and to minimize the potential for excessive loss of air pressure, possibly tripping the dry-pipe or preaction valve. Ray Vance Chief Engineering Tech. Wayne Automatic Fire Sprinklers, (407) 656-3030 www.waynefire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Monday, May 14, 2007 9:01 AM To: [email protected] Subject: RE: drum drip We always close both because with one open and active spring breakers, we have had tripped systems. Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key, SET Sent: Monday, May 14, 2007 8:21 AM To: [email protected] Subject: RE: drum drip Todd, The fitter was probably telling you the truth, which is that he was taught to close both valves. When I started in the field in the late 70's, I was taught the same thing. This is a good reason to promote the AFSA apprenticeship program so the fitters coming up now can be taught the correct way to do things. And yes, according to the apprenticeship course, the top valve is to be left open. Gregg -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - work Sent: Sunday, May 13, 2007 8:15 AM To: [email protected] Subject: drum drip When a drum drip is left in 'normal' position, which valves are open and which closed? I always thought that the top valve is open and the bottom valve shut. A fitter told me that both valves are supposed to be shut. When I asked him where that came from, he admitted that's what he was taught. Which is correct, if either? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) Wayne Automatic Fire Sprinklers, Inc. 2006 Inductee into "The Players Hall of Fame" at The Great Games of Business Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work" Rated #1 in 2006 Large Business Category by Orlando Business Journal _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)