It's easy to bash the ahj, so lets remember that we all are human and make
some mistakes.  I know that those of us who subscribe to this list are
perfect, so the statement only applies to those who do not subscribe.  I
think it has been well stated that you have to educate ahj many times.  Many
times the AHJ educated the contractor and so on.  If it is rule with the
iron first, you have to decide if it is a battle you want to take on.  But
in many cases this can be a great case for building relationships with AHJ's
so you can discuss code in an open forum.  

No one has mentioned the building or fire board of appeals process though.
I have been successful in convincing an AHJ to go that route and have both
sides make a code argument to a higher authority.   

  

Michael O'Brian
Code Savvy Consultants
www.codesavvyconsultants.com
313-618-6401
Fax 313-557-0294
 
************************************************
Take a look at www.inspector911.com the first site dedicated to code
enforcmenet (inspectors, fire marhsals, building officals, and plan
reviewers).  
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Vining
Sent: Wednesday, August 01, 2007 11:46 AM
To: [email protected]
Subject: Re: Telling an AHJ "No" ?

Travis, the AHJ may have been at the top of the food chain for the FD, but
not at the top of the code authority.  He gets his authority from someone
higher up,  City council, county supervisors, or whatever.

I once had a deputy state fire marshal tell me we had to sprinkler a
noncombustible stairway, when the code said we didn't.  He was adamant.  I
told him I would do it because the client had to get along with the project,
but that I would take it up with his superiors.  Several weeks afterward he
called me with apologies, saying he had been wrong.

In another case an AHJ said we had to treat a medical office building as a
hospital.  This time we had time, so I went unofficially to his leaders,
suggesting that he needed a bit of training, both on the code and customer
relations.  We won.

George is right.  Stand up and fight, even if it has to be after the fact.

 
[EMAIL PROTECTED]
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792



----- Original Message ----
From: Travis Mack <[EMAIL PROTECTED]>
To: [email protected]
Sent: Wednesday, August 1, 2007 8:27:26 AM
Subject: RE: Telling an AHJ "No" ?


George:

I completely agree.  Just a couple weeks ago, I had an AHJ review a set of
plans/calcs.  There was a small room that was light hazard.  The room was
about 150 sq ft.  However, due to lights and such, we were 7.5' off 2 walls.
I calc'd the head at 15gpm.  He called and said he wanted it calc'd at 22.5
gpm.  I started to tell him about the small room and how you take room area
and divide by # of heads to get flow for small rooms in light hazard.  The
exact quote was: "Don't try to justify anything to me.  You do what I want
or this will not get approved."  He then hung up, no further explanations.
This was in a relatively small jurisdiction in UT and we have to deal with
him frequently.  It ended up costing about $500 to change the piping to give
him what he wanted.  Nothing was installed, but it required a change of pipe
size and making a small loop.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to