Never. But I can't remember using 6" bulk for an 8" header.

Ron 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Wednesday, September 19, 2007 11:34 AM
To: [email protected]
Subject: RE: pump test header location

Ron,

Lets say you got a pump that requires 8" discharge pipe, your sprinkler
bulk main is 6", and you decide to connect the test header to the end of
the bulk main.  Have you had any problems getting the test header calc
to work? (never, rarely, sometimes, etc.)

Ed Kramer
Littleton, CO


>It's more common to take the test header off the end of bulk main or 
>combine it with the FDC line if the header is remote from the pump
room.
>
>Ron Fletcher
>Aero Automatic
>Phoenix, AZ