I believe the informal interpretation of discharge pipe defines the discharge piping in the pump room. Once it leaves the pump room it is part of your sprinkler system (bulk main, feed or cross main, etc) and no longer part of the pump piping.
Cliff Whitfield Fire Design, Inc. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer Sent: Wednesday, September 19, 2007 3:46 PM To: [email protected] Subject: RE: pump test header location Good point. But I don't see where "discharge pipe" is defined anywhere. Section 5.15.1 hints at a definition, but doesn't quite get there. Without a formal definition, anything downstream of the pump could be considered discharge pipe. Ed Kramer Littleton, CO >How does 5.19.3.4 play into this? It mentions pump discharge piping >only... > > >R/ > >Matt > > >Matthew J. Willis >Living Water Fire Protection, LLC. >1160 McKenzie Rd. >PO Box 877 >Cantonment, FL. 32533 >850-937-1850 Voice >850-937-1852 Facsimile >[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)