I knew I could use the extended escutcheon, but for aesthetics, the customer, and I, prefer the semi-recessed. This type would give me 1" to 1-1/2" below the ceiling and hopefully, I would be far enough from the soffit. Plus there is ductwork in the soffit which will make it difficult to get pipes around. The floor to deck dimension is only 8'8".
Joseph C. Stough SET, CFPS Tilley Fire Equipment Co. Tel. 215-345-8066 X22 Fax: 215-345-9357 [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Steve Leyton Sent: Tuesday, September 18, 2007 11:48 AM To: [email protected] Subject: RE: Sprinklers in Soffit? Jay: Deflectors of spray sprinklers (and most if not all EC's) may be positioned up to 12" below smooth ceilings, and some sprinklers are specifically listed for greater distances. So if it's convenient, you could place sprinklers on the soffit and continue the pattern out into 8'0" ceiling across the rest of the room. Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jay Stough Sent: Tuesday, September 18, 2007 8:43 AM To: AFSA SprinklerFORUM Subject: Sprinklers in Soffit? I have a school with classrooms that have a ceiling of 8'. there is a soffit along one wall that is 10" lower than the ceiling and 36" wide. I am drawing a blank as to whether I need sprinklers in the soffit. 8.6.4.1.1.3 says that if the difference in heights in the ceiling is less than 36", I can consider it a flat ceiling. 8.6.5.1.2 (3) limits the soffit to 30" in width. I can comply with table 8.6.5.1.2 and be less than 7'6 away from the wall. So can I eliminate sprinklers in the soffits? Joseph C. Stough SET, CFPS Tilley Fire Equipment Co. Tel. 215-345-8066 X22 Fax: 215-345-9357 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)