Jay,

You will still need to adhere to Table 8.6.5.1.2.  As long as you can do
that, you can, in a sense, "ignore" the soffit.  With a 36" wide soffit it
is sometimes hard to stay within the 7'-6" distance, especially if you have
to hit center of tile.

Cliff Whitfield
Fire Design, Inc.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jay Stough
Sent: Tuesday, September 18, 2007 11:07 AM
To: [email protected]
Subject: Sprinklers in Soffit?

I knew I could use the extended escutcheon, but for aesthetics, the
customer, and I, prefer the semi-recessed.  This type would give me 1" to
1-1/2" below the ceiling and hopefully, I would be far enough from the
soffit.  Plus there is ductwork in the soffit which will make it difficult
to get pipes around.  The floor to deck dimension is only 8'8".

Joseph C. Stough SET, CFPS
Tilley Fire Equipment Co.
Tel. 215-345-8066 X22
Fax: 215-345-9357
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Steve
Leyton
Sent: Tuesday, September 18, 2007 11:48 AM
To: [email protected]
Subject: RE: Sprinklers in Soffit?


Jay:

Deflectors of spray sprinklers (and most if not all EC's) may be
positioned up to 12" below smooth ceilings, and some sprinklers are
specifically listed for greater distances.   So if it's convenient, you
could place sprinklers on the soffit and continue the pattern out into
8'0" ceiling across the rest of the room.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jay
Stough
Sent: Tuesday, September 18, 2007 8:43 AM
To: AFSA SprinklerFORUM
Subject: Sprinklers in Soffit?

I have a school with classrooms that have a ceiling of 8'.  there is a
soffit along one wall that is 10" lower than the ceiling and 36" wide.
I am
drawing a blank as to whether I need sprinklers in the soffit.
8.6.4.1.1.3
says that if the difference in heights in the ceiling is less than 36",
I
can consider it a flat ceiling.  8.6.5.1.2 (3) limits the soffit to 30"
in
width.  I can comply with table 8.6.5.1.2 and be less than 7'6 away from
the
wall.  So can I eliminate sprinklers in the soffits?

Joseph C. Stough SET, CFPS
Tilley Fire Equipment Co.
Tel. 215-345-8066 X22
Fax: 215-345-9357
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to