Bobby:

If you had a soffit that was 4" deep and 40" long, you wouldn't need a head
under it if you can position the sprinkler to throw under it.  I believe
that you have to either comply with the beam rule, or the soffit rule (if
you have a soffit that is <30").  However, I could easily be wrong on that. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bobby Gillett
Sent: Tuesday, September 18, 2007 1:17 PM
To: [email protected]
Subject: RE: Sprinklers in Soffit?

If I'm reading 8.6.5.1.2 correctly, it says if you are against the wall- the
soffit has to be 30" or under to be able to use this.
Anything over 30" that is against the wall would require additional
sprinklers. Or am I having another Monday today?

Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jay Stough
Sent: Tuesday, September 18, 2007 10:43 AM
To: AFSA SprinklerFORUM
Subject: Sprinklers in Soffit?

I have a school with classrooms that have a ceiling of 8'.  there is a
soffit along one wall that is 10" lower than the ceiling and 36" wide.  I am
drawing a blank as to whether I need sprinklers in the soffit.  8.6.4.1.1.3
says that if the difference in heights in the ceiling is less than 36", I
can consider it a flat ceiling.  8.6.5.1.2 (3) limits the soffit to 30" in
width.  I can comply with table 8.6.5.1.2 and be less than 7'6 away from the
wall.  So can I eliminate sprinklers in the soffits?

Joseph C. Stough SET, CFPS
Tilley Fire Equipment Co.
Tel. 215-345-8066 X22
Fax: 215-345-9357
[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2540 (20070919) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to