I disagree with item 2. If you have no loss or gain of gpm in the system to
the flow point and you measure the discharge pressure at the pump, where the
gpm is read makes no difference and will not effect the fire pump curve.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of SISPROFUEGO,
C.A. - José Prada
Sent: Thursday, September 20, 2007 1:00 PM
To: [email protected]
Subject: Re: pump test header location

Dear Sirs:

According to my experience there are two main reason to keep the test
header close to the pump and prior to the main shut off valve:

1.- This arragment isolates the pump from the rest of the system.
2.- Water flow measured in points to far away from the pump will be
afected by pressure droping across the pipe. Remember that the test
header is just for pump flow test, in the same way a flowmeter is. So,
as closer to the pump, more accurated will be the measuring.

Kindest regards,

Jose Prada