I'd considered a surge bladder for this, but do't have any field experience
with them.
May have to wait for the 8-5'ers to get to the office.....I've only used
bladderes on AF loops.

Did talk to Clarke, they thought either would work (bladder or PRV). I think
the main criteria may be operating speed, in which the bladder would win.
Have asked CLA Val and OCV about reaction speed.

Ps- TD- are ready to go out or are you coming back in from an early test?

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Thursday, September 20, 2007 5:38 AM
To: [email protected]
Subject: RE: PLD and PRV

I thought these were out-coded for oversized diesels, constant speed or
variable.
I'd go back to Clarke.  How about a surge/bladder tank?

Tom


Fire only, manufacturing/warehouse occupancies.
:) next to two 2,000 GPM pumps, I thought 2.5" WAS small !
I want to make sure it doesn't get clogged, but DUH, pilot lines aren't 2.5"
or ", are they.
Will look at 2", smallest without switching styles down to a 3/4".

glc

Since your only using it to restore the lower operation pressure in the
mains why use a 2.5" device? The smaller a device the lower the impact if it
fails open. Also if the only usage on this system is for fire, you'll have a
small spike at start up, but a very low volume to deal with to return it to
155 / 160 Psi. If the system feeds domestic / industrial uses wouldn't that
relieve the excess?

Thom McMahon


>
> We've noticed the PLD's we've installed allow brief surge of 
> overpressurization while the diesel starts up, builds pressure, and 
> for the time it takes the PLD to react, there's an inrush of some of 
> the churn pressure until the governor kicks in and backs it down. Guy 
> at Clarke confirmed this.
>
> We have a project with what is possibly fragile UG in many sections of 
> the facility. We're trying to keep it, and the related interior 
> systems, from creeping up to high pressure (isn't that why we have the 
> PLD?). This particular site is getting twin 2,000 @ 150 diesel 
> vertical turbines, which feed a large looped yard system, in turn 
> feeding -oh, couple dozen risers scattered around.
>
> We're thinking a small (2.5"?) Relief valve located past the pump 
> discharge valve, just before it drops into the yard system, PRV 
> discharge piped back to the reservoir, set point 5 PSI above the PLD, 
> set adjustment on reaction time to ASAP setting, so it will bleed off 
> the excess pressure as soon as possible. We think the size of the yard 
> loop- complete with sectionals, hydrants, etc.- will absorb the shock 
> with only a small amount of it getting into the interior systems. If 
> some does, 1/2" relief valves on the grid will take care of anything > 
> 175. But we want to be able to have the UG drop back to the 155~160 
> range as soon as possible.
>
> Since the twin pumps go into one yard system, the small PRV only has 
> to be installed on one of these. Since its relatively small, even if 
> it failed OPEN the loss wouldn't de-rail the train, we have 150 @ 
> 4,000 when combined, and demand is about 150 @3,000. Assuming the 2.5" 
> PRV stuck open wouldn't flow more than 1,000 GPM, it could drop the 
> water back in the hole to be re-pumped all day long.
>
> Both pumps will start remotely from elec detection systems on these 
> large demand systems, and on pressure drop for the conventional wets.
>
> Yes, the owner has authorized high pressure testing of the UG, still 
> doesn't mean we can slam the heck out of it or let it sit at 175+ and 
> not see a main break in a couple yrs.
>
> Any other thoughts from those with some PLD experience?
>
> glc


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to