Well, we'd be bleeding down to 150~160 PSI in this case, and a pair of 3/4"
ones would give some redundancy as well as what could be sufficient flow-
tough to judge what flow is needed to drop a mile of UG, but if we
undersized, it would only mean another 30 seconds of bleed time. And two
3/4" 55L's would be, I'll guess, less than one 2" pilot operated main
reliefs (90-21's)- not that either is significant $ in this particular
application, million dollar customer being treated as HPR since owner is
self-insured and there are some BI poison pills we can't have damaged or a
major mfr loses a product line (only place they make packaging for this
product line, even tho they have other plants making the product, so if we
lose that area, they can't put it on the shelves, and they'd immediately
lose market share). 

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Thursday, September 20, 2007 6:14 AM
To: [email protected]
Subject: RE: PLD and PRV

On reaction speed...

I did 12 Cla-Val 90-21G PRV's at the Convention Ctr. last week, all fed off
twin 2000 GPM diesels at 175 PSI (we adjusted the driver speed down a touch)
to maintain 80 PSI for the overhead large drop systems in the HUGE
exhibition hall.  (God bless Paul T., what an amazing engineer he was)
Cla-Val's creep but also slam a little which is why we require safeties
after the valves.  A 3/4" 55L will open and close very quickly and they do
take the hammer out of these pilot operated valves very well.
If you use a Cal-Val(s), size it for FLOW and not pipe size and put some
careful thought into the size of the safety.  They (55L's) react quickly but
don't pass much water unless you've got 150+ PSI behind them.

Tom


I'd considered a surge bladder for this, but do't have any field experience
with them.
May have to wait for the 8-5'ers to get to the office.....I've only used
bladderes on AF loops.

Did talk to Clarke, they thought either would work (bladder or PRV). I think
the main criteria may be operating speed, in which the bladder would win.
Have asked CLA Val and OCV about reaction speed.

Ps- TD- are ready to go out or are you coming back in from an early test?

glc

I thought these were out-coded for oversized diesels, constant speed or
variable.
I'd go back to Clarke.  How about a surge/bladder tank?

Tom


Fire only, manufacturing/warehouse occupancies.
:) next to two 2,000 GPM pumps, I thought 2.5" WAS small !
I want to make sure it doesn't get clogged, but DUH, pilot lines aren't 2.5"
or ", are they.
Will look at 2", smallest without switching styles down to a 3/4".

glc

Since your only using it to restore the lower operation pressure in the
mains why use a 2.5" device? The smaller a device the lower the impact if it
fails open. Also if the only usage on this system is for fire, you'll have a
small spike at start up, but a very low volume to deal with to return it to
155 / 160 Psi. If the system feeds domestic / industrial uses wouldn't that
relieve the excess?

Thom McMahon


>
> We've noticed the PLD's we've installed allow brief surge of 
> overpressurization while the diesel starts up, builds pressure, and 
> for the time it takes the PLD to react, there's an inrush of some of 
> the churn pressure until the governor kicks in and backs it down. Guy 
> at Clarke confirmed this.
>
> We have a project with what is possibly fragile UG in many sections of 
> the facility. We're trying to keep it, and the related interior 
> systems, from creeping up to high pressure (isn't that why we have the 
> PLD?). This particular site is getting twin 2,000 @ 150 diesel 
> vertical turbines, which feed a large looped yard system, in turn 
> feeding -oh, couple dozen risers scattered around.
>
> We're thinking a small (2.5"?) Relief valve located past the pump 
> discharge valve, just before it drops into the yard system, PRV 
> discharge piped back to the reservoir, set point 5 PSI above the PLD, 
> set adjustment on reaction time to ASAP setting, so it will bleed off 
> the excess pressure as soon as possible. We think the size of the yard
> loop- complete with sectionals, hydrants, etc.- will absorb the shock 
> with only a small amount of it getting into the interior systems. If 
> some does, 1/2" relief valves on the grid will take care of anything > 
> 175. But we want to be able to have the UG drop back to the 155~160 
> range as soon as possible.
>
> Since the twin pumps go into one yard system, the small PRV only has 
> to be installed on one of these. Since its relatively small, even if 
> it failed OPEN the loss wouldn't de-rail the train, we have 150 @ 
> 4,000 when combined, and demand is about 150 @3,000. Assuming the 2.5"
> PRV stuck open wouldn't flow more than 1,000 GPM, it could drop the 
> water back in the hole to be re-pumped all day long.
>
> Both pumps will start remotely from elec detection systems on these 
> large demand systems, and on pressure drop for the conventional wets.
>
> Yes, the owner has authorized high pressure testing of the UG, still 
> doesn't mean we can slam the heck out of it or let it sit at 175+ and 
> not see a main break in a couple yrs.
>
> Any other thoughts from those with some PLD experience?
>
> glc


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to