Joe,

Not to beat a dead horse, but where in NFPA 13 does it say a draft
curtain is required if the control modes are QR?

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Thursday, September 20, 2007 3:30 PM
To: [email protected]
Subject: Re: Mezzanine/ ESFR

Art,
No, because the QR doesn't mean very much in control mode. Unless you
get suppression below the mezzanine (which you won't with control-mode
protection), there is a high likelihood that you will operate sprinklers
at the roof.  The only way to take the ceiling sprinklers out of the
picture is suppression mode under the mezzanine or a draft curtain
around it.

Joe

art wrote:
> Joe,
> If the mezz sprinklers are the same temperature and also quick 
> response would the conditions change from what you describe below  
> assuming the correct density for control?
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Joe 
> Hankins
> Sent: Thursday, September 20, 2007 1:32 PM
> To: [email protected]
> Subject: Re: Mezzanine/ ESFR
>
> If the area below the mezzanine is protected with control-mode 
> sprinklers and the area above with ESFR, a fire below the mezzanine 
> will operate ESFRs at the ceiling above. It's exactly the same as a 
> roof elevation change with ESFRs on the high side and control mode on 
> the low side, where you need a draft curtain and an aisle to separate
the areas.
>
> FM recommends a draft curtain around the perimeter of the mezzanine if

> ESFRs are not provided under it.  If ESFRs are provided under the 
> mezzanine, then you can forget the draft curtain as long as there are 
> ESFRs near the perimeter of the mezzanine and no storage beyond them.
>
> Sometimes the issue is not the hazard you are protecting, but what 
> will happen during the fire.  If you design for the hazard under the 
> mezannine using control mode protection, a fire there can open 
> sprinklers well beyond the actual fire area, up to the design area. If

> the fire starts near the edge of the mezzanine, the heat that would be

> expected to operate control mode sprinklers if they were there will 
> operate ESFRs at the ceiling, as well..
>
> Joe
>
> Fletcher, Ron wrote:
>   
>> Sprinklers below and ESFR above just like an office area. The 
>> mezzanine is too big to be an obstruction (my opinion), too low to 
>> require ESFR's and you can't omit sprinklers. The 15 ft. rule would 
>> be applied to the full height warehouse and extend 15 ft. past the
edge of the mezzanine.
>> Not an issue here unless you want to pull the ESFR's above the 
>> mezzanine and do area density with control mode, but why?
>>
>> Ron
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Jimmy 
>> Waite
>> Sent: Wednesday, September 19, 2007 2:32 PM
>> To: [email protected]
>> Subject: RE: Mezzanine/ ESFR
>>
>> Ron, Thanks for your response.  Can I ask your reasoning behind it?
>>
>>
>> Jimmy
>>
>>
>>
>>
>>
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of 
>> Fletcher, Ron
>> Sent: Wednesday, September 19, 2007 2:45 PM
>> To: [email protected]
>> Subject: RE: Mezzanine/ ESFR
>>
>> Forget the ESFR's. Just sprinkler the mezzanine.
>>
>> Ron Fletcher
>> Aero Automatic
>> Phoenix, AZ
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Jimmy 
>> Waite
>> Sent: Wednesday, September 19, 2007 12:25 PM
>> To: [email protected]
>> Subject: Mezzanine/ ESFR
>>
>> Hello all again,
>>
>>  
>>
>> Apparently the thing to do out west is to add mezzanines years after 
>> the original building is built, and then sprinkle them after you get 
>> caught/get in trouble.  We have a job that is a warehouse designed 
>> with and ESFR system.  The owner has since come in and built a
mezzanine.
>> The mezzanine is roughly 67' by 33.5' and is about 9'-10 tall.  The 
>> mezzanine is located on an exterior wall, and the warehouse is 30' 
>> tall at the peak.  There is no separation around the exterior of the 
>> mezzanine.
>>
>>  
>>
>> Now that I have explained the space, let me explain the scenario.  
>> The space under the mezzanine is used to pull orders.  They keep the 
>> merchandise in plastic totes while it is under the mezzanine.  So all

>> the storage is transient.  The totes sit in a flow through racks, to 
>> hold orders before they go to a truck, that doesn't store above 5'.
>>
>>  
>>
>> Now to my question.  Now the standard seems to be pretty clear, that 
>> since there is no separation, the '07 in sections 11.1.2 (1) and 12.3
>> (1) say that since there is no separation the hazard needs to be 
>> carried 15'-0 beyond the hazard perimeter.  Do these sections apply 
>> to both above and below the mezzanine?  Would I have to carry the 
>> ESFR design criteria 15' into the mezzanine floor area?  This seems a

>> bit much considering the space would normally be misc. storage in 
>> the'07.  But I also can see the justification to increase the design 
>> criteria since the mezzanine is surrounded on three sides by storage.
>>
>>  
>>
>> If ESFR is required I know I'll have several problems.  I won't have 
>> the clearance needed between the deflector and storage.  Also, the 
>> mezzanine is non-combustible Obstructed construction.  Would there be

>> any other design criteria I could use, other than ESFR?
>>
>>  
>>
>> I've never done an ESFR system before and definitely need the help.  
>> I have pictures that could clarify what I'm talking about if anyone 
>> would like them that I willing to give some suggestions.
>>
>>  
>>
>>  
>>
>> Jimmy Waite
>>
>> Burtell Fire Protection, Inc.
>>
>> [EMAIL PROTECTED]
>>
>> (406) 652-7697
>>
>>  
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field) 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field) 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email 
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>>   
>>     
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]