Thanks for the info.  I guess what I'm looking for is something that states 
that all these existing double-check backflows are not a threat and replacing 
them all with RPZ is a lot of unnecessary extra cost for the owner.  As Matt 
stated, it may very well be a losing argument as long as it has been "adopted". 
 The info will be used to fight to keep the existing double-checks.> Date: Tue, 
9 Oct 2007 14:10:20 -0400> From: [EMAIL PROTECTED]> To: 
[email protected]> Subject: RE: Double-check vs RPs> > Gayle, 
Perhaps our regulations in New Jersey would be of assistance.> > John Drucker, 
Fire Protection Subcode Official, NJ> 
------------------------------------------------------------------------> 
------> > STATE OF NEW JERSEY> > DEPARTMENT OF ENVIRONMENTAL PROTECTION> > 
BUREAU OF SAFE DRINKING WATER> > SAFE DRINKING WATER ACT REGULATIONS> > 
(N.J.A.C. 7:10)> > ADOPTED: November 4, 2004> > 7:10-10.4 Installation> > (a) 
The approved physical connection installation shall be> installed on the 
customer's side of the water meter on the> pipe(s) conveying the water from the 
public community water> system into a facility, shall be installed as close to 
the meter as> is reasonably practicable, and shall be prior to any other> 
connection, unless such other connection is also protected by> means of an 
approved physical connection installation. For a> fire service line, the 
approved physical connection installation> shall be installed prior to the 
alarm check and siamese> connection.> (b) The approved physical connection 
installation shall be> installed so as to allow easy access, with adequate 
space for> maintenance, inspection, and testing. No part of the device> shall 
be submerged or subjected to freezing temperatures unless> such part is 
thermally protected.> > (c) The approved physical connection installation shall 
not> be installed in a pit or vault.> > 1. This subsection shall not apply to 
any physical> connection installation operated under a current physical> 
connection permit issued before the operative date of this> chapter until such 
time as the existing physical connection> installation is replaced or modified> 
> _______________________________________________> Sprinklerforum mailing list> 
[email protected]> 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To 
Unsubscribe, send an email to:[EMAIL PROTECTED]> (Put the word unsubscribe in 
the subject field)_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]