Not a code violation, just a new code is wanting to come into playGayle 
Knowles, SET 
 
 
> Date: Tue, 9 Oct 2007 14:43:13 -0400> From: [EMAIL PROTECTED]> To: 
> [email protected]> Subject: RE: Double-check vs RPs> > Gayle,> 
> > Off the top of my head (which means it not nor will be enforceable glc!)> 
> perhaps the installed BFP is an existing code violation ?. Yea it> happens 
> stuff gets approved that shouldn't be. The water purveyor may> have simply 
> caught it. However RPZ's in submersable locations has to the> best of my 
> knowledge been prohibited.> > While we are on that subject, remember a code 
> violation is a violation> forever despite what "approval" you may have in 
> hand. > > John Drucker> Fire Protection Subcode Official> New Jersey > > 
> -----Original Message-----> From: [EMAIL PROTECTED]> [mailto:[EMAIL 
> PROTECTED] On Behalf Of GAYLE> KNOWLES> Sent: Tuesday, October 09, 2007 2:26 
> PM> To: [email protected]> Subject: RE: Double-check vs RPs> > 
> > Thanks for the info. I guess what I'm looking for is something that> states 
> that all these existing double-check backflows are not a threat> and 
> replacing them all with RPZ is a lot of unnecessary extra cost for> the 
> owner. As Matt stated, it may very well be a losing argument as> long as it 
> has been "adopted". The info will be used to fight to keep> the existing 
> double-checks.> Date: Tue, 9 Oct 2007 14:10:20 -0400> From:> [EMAIL 
> PROTECTED]> To: [email protected]> Subject:> RE: Double-check 
> vs RPs> > Gayle, Perhaps our regulations in New Jersey> would be of 
> assistance.> > John Drucker, Fire Protection Subcode> Official, NJ>> 
> ------------------------------------------------------------------------> > 
> ------> > STATE OF NEW JERSEY> > DEPARTMENT OF ENVIRONMENTAL> PROTECTION> > 
> BUREAU OF SAFE DRINKING WATER> > SAFE DRINKING WATER ACT> REGULATIONS> > 
> (N.J.A.C. 7:10)> > ADOPTED: November 4, 2004> > 7:10-10.4> Installation> > 
> (a) The approved physical connection installation shall> be> installed on the 
> customer's side of the water meter on the> pipe(s)> conveying the water from 
> the public community water> system into a> facility, shall be installed as 
> close to the meter as> is reasonably> practicable, and shall be prior to any 
> other> connection, unless such> other connection is also protected by> means 
> of an approved physical> connection installation. For a> fire service line, 
> the approved physical> connection installation> shall be installed prior to 
> the alarm check and> siamese> connection.> (b) The approved physical 
> connection installation> shall be> installed so as to allow easy access, with 
> adequate space for>> maintenance, inspection, and testing. No part of the 
> device> shall be> submerged or subjected to freezing temperatures unless> 
> such part is> thermally protected.> > (c) The approved physical connection> 
> installation shall not> be installed in a pit or vault.> > 1. This> 
> subsection shall not apply to any physical> connection installation> operated 
> under a current physical> connection permit issued before the> operative date 
> of this> chapter until such time as the existing physical> connection> 
> installation is replaced or modified> >> 
> _______________________________________________> Sprinklerforum mailing> 
> list> [email protected]>> 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To> 
> Unsubscribe, send an email to:[EMAIL PROTECTED]>> (Put the word unsubscribe 
> in the subject> field)_______________________________________________> 
> Sprinklerforum mailing list> [email protected]> 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To 
> Unsubscribe, send an email> to:[EMAIL PROTECTED]> (Put the word unsubscribe 
> in the subject field)> > > _______________________________________________> 
> Sprinklerforum mailing list> [email protected]> 
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To 
> Unsubscribe, send an email to:[EMAIL PROTECTED]> (Put the word unsubscribe in 
> the subject field)_______________________________________________