Gayle,

Off the top of my head (which means it not nor will be enforceable glc!)
perhaps the installed BFP is an existing code violation ?. Yea it
happens stuff gets approved that shouldn't be. The water purveyor may
have simply caught it. However RPZ's in submersable locations has to the
best of my knowledge been prohibited.

While we are on that subject, remember a code violation is a violation
forever despite what "approval" you may have in hand. 

John Drucker
Fire Protection Subcode Official
New Jersey 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of GAYLE
KNOWLES
Sent: Tuesday, October 09, 2007 2:26 PM
To: [email protected]
Subject: RE: Double-check vs RPs


Thanks for the info.  I guess what I'm looking for is something that
states that all these existing double-check backflows are not a threat
and replacing them all with RPZ is a lot of unnecessary extra cost for
the owner.  As Matt stated, it may very well be a losing argument as
long as it has been "adopted".  The info will be used to fight to keep
the existing double-checks.> Date: Tue, 9 Oct 2007 14:10:20 -0400> From:
[EMAIL PROTECTED]> To: [email protected]> Subject:
RE: Double-check vs RPs> > Gayle, Perhaps our regulations in New Jersey
would be of assistance.> > John Drucker, Fire Protection Subcode
Official, NJ>
------------------------------------------------------------------------
> ------> > STATE OF NEW JERSEY> > DEPARTMENT OF ENVIRONMENTAL
PROTECTION> > BUREAU OF SAFE DRINKING WATER> > SAFE DRINKING WATER ACT
REGULATIONS> > (N.J.A.C. 7:10)> > ADOPTED: November 4, 2004> > 7:10-10.4
Installation> > (a) The approved physical connection installation shall
be> installed on the customer's side of the water meter on the> pipe(s)
conveying the water from the public community water> system into a
facility, shall be installed as close to the meter as> is reasonably
practicable, and shall be prior to any other> connection, unless such
other connection is also protected by> means of an approved physical
connection installation. For a> fire service line, the approved physical
connection installation> shall be installed prior to the alarm check and
siamese> connection.> (b) The approved physical connection installation
shall be> installed so as to allow easy access, with adequate space for>
maintenance, inspection, and testing. No part of the device> shall be
submerged or subjected to freezing temperatures unless> such part is
thermally protected.> > (c) The approved physical connection
installation shall not> be installed in a pit or vault.> > 1. This
subsection shall not apply to any physical> connection installation
operated under a current physical> connection permit issued before the
operative date of this> chapter until such time as the existing physical
connection> installation is replaced or modified> >
_______________________________________________> Sprinklerforum mailing
list> [email protected]>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To
Unsubscribe, send an email to:[EMAIL PROTECTED]>
(Put the word unsubscribe in the subject
field)_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to