Gayle,

The argument that I have used with some success is a basic risk comparison
between the possibility of a backflow incident and the danger from a fire in
the building.  I don't think you will have much luck with arguing that the
RPZ and double check are no different.  According to the cross-connection
field, the RPZ is definitely safer.  However, if you can do some rough
hydraulic analysis and find that the extra 10 psi or so of friction loss
from an RPZ results in the need for a fire pump (which it often does), then
you can make an argument.  The argument is that the fire pump adds a
mechanical component to the sprinkler system making it a little less
reliable in the event of a fire which must be weighed against the marginal
increase in safety that an RPZ provides over the existing double-check BFP's
you have.  All of this is notwithstanding the additional expense to the
building owner.  It's a tradeoff between the safety of the building
inhabitants from fire and the safety of the community from a backflow
incident. 

The few times that I have explained this to the water guys, they have backed
off the requirement.  Good luck,

Steve 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of GAYLE KNOWLES
Sent: Tuesday, October 09, 2007 2:26 PM
To: [email protected]
Subject: RE: Double-check vs RPs


Thanks for the info.  I guess what I'm looking for is something that states
that all these existing double-check backflows are not a threat and
replacing them all with RPZ is a lot of unnecessary extra cost for the
owner.  As Matt stated, it may very well be a losing argument as long as it
has been "adopted".  The info will be used to fight to keep the existing
double-checks.> Date: Tue, 9 Oct 2007 14:10:20 -0400> From:
[EMAIL PROTECTED]> To: [email protected]> Subject: RE:
Double-check vs RPs> > Gayle, Perhaps our regulations in New Jersey would be
of assistance.> > John Drucker, Fire Protection Subcode Official, NJ>
------------------------------------------------------------------------>
------> > STATE OF NEW JERSEY> > DEPARTMENT OF ENVIRONMENTAL PROTECTION> >
BUREAU OF SAFE DRINKING WATER> > SAFE DRINKING WATER ACT REGULATIONS> >
(N.J.A.C. 7:10)> > ADOPTED: November 4, 2004> > 7:10-10.4 Installation> >
(a) The approved physical connection installation shall be> installed on the
customer's side of the water meter on the> pipe(s) conveying the water from
the public community water> system into a facility, shall be installed as
close to the meter as> is reasonably practicable, and shall be prior to any
other> connection, unless such other connection is also protected by> means
of an approved physical connection installation. For a> fire service line,
the approved physical connection installation> shall be installed prior to
the alarm check and siamese> connection.> (b) The approved physical
connection installation shall be> installed so as to allow easy access, with
adequate space for> maintenance, inspection, and testing. No part of the
device> shall be submerged or subjected to freezing temperatures unless>
such part is thermally protected.> > (c) The approved physical connection
installation shall not> be installed in a pit or vault.> > 1. This
subsection shall not apply to any physical> connection installation operated
under a current physical> connection permit issued before the operative date
of this> chapter until such time as the existing physical connection>
installation is replaced or modified> >
_______________________________________________> Sprinklerforum mailing
list> [email protected]>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To
Unsubscribe, send an email to:[EMAIL PROTECTED]> (Put
the word unsubscribe in the subject
field)_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to