Gayle - if the systems are within 1700 feet of a non potable water source
they are supposed to be RPZs anyway. or if you have A-F.  Also be wary of
the installation location, a RPZ can not be placed below grade regardless
where the DCV is unless a gravity drain capable of handling the discharge of
the device when it fouls is present.  Just because a DCV is installed in a
pit and has to be changed out does not allow you to place the RPZ in the
pit.  DCV and RPZ are NOT the same protection.
Sounds like you need to ask politely for the Code section that is being
referenced so that you might have it handy for the next project.  If it can
be produced, comply.

Garth
----- Original Message ----- 
From: "GAYLE KNOWLES" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, October 09, 2007 1:26 PM
Subject: RE: Double-check vs RPs



Thanks for the info.  I guess what I'm looking for is something that states
that all these existing double-check backflows are not a threat and
replacing them all with RPZ is a lot of unnecessary extra cost for the
owner.  As Matt stated, it may very well be a losing argument as long as it
has been "adopted".  The info will be used to fight to keep the existing
double-checks.> Date: Tue, 9 Oct 2007 14:10:20 -0400> From:
[EMAIL PROTECTED]> To: [email protected]> Subject: RE:
Double-check vs RPs> > Gayle, Perhaps our regulations in New Jersey would be
of assistance.> > John Drucker, Fire Protection Subcode Official,
NJ> ------------------------------------------------------------------------
> ------> > STATE OF NEW JERSEY> > DEPARTMENT OF ENVIRONMENTAL PROTECTION> >
BUREAU OF SAFE DRINKING WATER> > SAFE DRINKING WATER ACT REGULATIONS> >
(N.J.A.C. 7:10)> > ADOPTED: November 4, 2004> > 7:10-10.4 Installation> >
(a) The approved physical connection installation shall be> installed on the
customer's side of the water meter on the> pipe(s) conveying the water from
the public community water> system into a facility, shall be installed as
close to the meter as> is reasonably practicable, and shall be prior to any
other> connection, unless such other connection is also protected by> means
of an approved physical connection installation. For a> fire service line,
the approved physical connection installation> shall be installed prior to
the alarm check and siamese> connection.> (b) The approved physical
connection installation shall be> installed so as to allow easy access, with
adequate space for> maintenance, inspection, and testing. No part of the
device> shall be submerged or subjected to freezing temperatures unless>
such part is thermally protected.> > (c) The approved physical connection
installation shall not> be installed in a pit or vault.> > 1. This
subsection shall not apply to any physical> connection installation operated
under a current physical> connection permit issued before the operative date
of this> chapter until such time as the existing physical connection>
installation is replaced or modified> >
_______________________________________________> Sprinklerforum mailing
list> [email protected]>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> > To
Unsubscribe, send an email to:[EMAIL PROTECTED]> (Put
the word unsubscribe in the subject
field)_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to