Good try George, But you have to read 10.5.9 a. which only lists four permissible BFP's, Two DC's and Two RPZ's. Take away the two DC's prohibited by 10.5.9 Exception (3) and what are you left with ?.
I figure by now Garth is saying that damn AHJ is behind all this, actually no not even a proposal, however as a code official I have no choice to enforce it. John -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church Sent: Tuesday, October 09, 2007 7:25 PM To: [email protected] Subject: RE: Double-check vs RPs I'm surprised that contractors don't read that as saying "ya don't need a BFP at all if ya gotta FDC." Glc Ps- todd, can your FD draft up 250'? holy golf ball! -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Tuesday, October 09, 2007 7:12 PM To: [email protected] Subject: RE: Double-check vs RPs The 2006 NSPC eliminated 1700 Ft FDC criteria, now any FDC equals RPZ. Heres how the section now reads; 10.5.9 Exception (3) "Where fire protection systems include a fire department connection double check valve assemblies shall not be permitted." John http://phcc.files.cms-plus.com/Depts/Technical/2006NSPCNonIllustratedWeb _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)