Good try George,

But you have to read 10.5.9 a. which only lists four permissible BFP's,  Two
DC's and Two RPZ's. Take away the two DC's prohibited by  10.5.9 Exception
(3) and what are you left with ?.

I figure by now Garth is saying that damn AHJ is behind all this, actually
no not even a proposal, however as a code official I have no choice to
enforce it. 

John

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Tuesday, October 09, 2007 7:25 PM
To: [email protected]
Subject: RE: Double-check vs RPs

I'm surprised that contractors don't read that as saying "ya don't need a
BFP at all if ya gotta FDC."

Glc

Ps- todd, can your FD draft up 250'? holy golf ball!

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Drucker
Sent: Tuesday, October 09, 2007 7:12 PM
To: [email protected]
Subject: RE: Double-check vs RPs

The 2006 NSPC eliminated 1700 Ft FDC criteria, now any FDC equals RPZ.
Heres how the section now reads;

10.5.9 Exception (3) "Where fire protection systems include a fire
department connection double check valve assemblies shall not be permitted."

John

http://phcc.files.cms-plus.com/Depts/Technical/2006NSPCNonIllustratedWeb



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to