I'm surprised that contractors don't read that as saying "ya don't need a BFP at all if ya gotta FDC."
Glc Ps- todd, can your FD draft up 250'? holy golf ball! -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Tuesday, October 09, 2007 7:12 PM To: [email protected] Subject: RE: Double-check vs RPs The 2006 NSPC eliminated 1700 Ft FDC criteria, now any FDC equals RPZ. Heres how the section now reads; 10.5.9 Exception (3) "Where fire protection systems include a fire department connection double check valve assemblies shall not be permitted." John http://phcc.files.cms-plus.com/Depts/Technical/2006NSPCNonIllustratedWeb _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)