Dave-
This may come as some surprise to you, and seems counter-intuitive BUT-
A HIGHER AIR PRESSURE IN THE SYSTEM CAN RESULT IN A FASTER WATER DELIVERY
TIME.
There are several variables within the equation of what it takes to get
water to the ITC.

Instead of summarizing them here, I'm simply going to point you to James'
G's White Paper on Performnace of Dry Pipe Systems which I'm sure you can
find on Tyco's website. 

I will back up my surprising (to some) intro by stating that when we've done
water delivery calcs, the results were at first counter-intuitive almost
every time!

But realize that beyond the time it takes to TRIP the system, there is
TRANSIT time that's ignored by those going toward lower and lower
supervisory air settings. While that lowers compressor size and refill
times, it also means that when the water enters the system, much more of it
is diverted from its course toward the ITC (or flowing heads) and goes up
each branchline to equalize pressure. If you have 500 GPM diverted into
filling pipe not in the path, that's the time (the time it takes to
introduce 500 Gal) you'll lose toward getting water to the ITC.

The right Quick Opening Device will trip the system quicker regardless of
the pressure since its looking at RATE of decrease. Then, when water enters
the system, if the air pressure is higher than you'd have expected, there is
less water diverted and the vast majority of it heads for the ITC.

Any non-believers simply have to watch the "video" replay of the FDT calcs
to illustrate and light the light bulb of Aha! for them. Once a couple of
scenarios of high and low pressure are run, it becomes more and more obvious
that reduction of one variable (supervisory pressure) to an extreme while
focusing on one component of water delivery (Trip Time) can have a greater
offsetting NEGATIVE impact on the second component (Transit Time).

Its not as apparent when doing a simple 1/2" ITC flow, but if you've seen a
calc run with 4 k17's open, there's not much holding back the forward inrush
of water as lots of air can get out of four K17 orifi.

Read the White Paper. See the Video. Be the water, and do good works.

Class dismissed.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dave Phelan
Sent: Thursday, October 25, 2007 7:55 AM
To: [email protected]
Subject: Supervisory Alarm - Low Air

Thanks for the information - I will be adjusting my field acceptance testing
procedures now to include this requirement.  I see the problem as being a
gap between the sprinkler installer and alarm tech / electrician.  Even if
the sprinkler tech puts in the proper switch with double contacts to be code
compliant it then falls to the alarm contractor to know the requirement and
properly pick up boths sets of contacts for both high and low pressure
supervision.  I guess the way to handle this up front on plan review is to
specifically cite the requirement on the drawings instead of the typical
'low air supervisory device' notation.

In talking to some contractors on the matter there is an opinion that high
air monitoring isnt all so important but looking at things through my
AHJ-fire colored glasses Im well aware of the negative impact on water
delivery time a system with excessive pressure can have.  I recently had the
cooperation of a contractor during the acceptance testing process and after
we trip tested the system at the design pressures we had a water delivery
time of 53 seconds.  We then refilled the system and increased air pressure
5 and 9 psi above the design pressure.  At 5 psi above the water delivery
was just about 1:45 but at 9 psi over the water delivery was just over 3
minutes.  Im sure we've all seen one or more test video burns in our time
and the thought of delaying water delivery nearly three times over is not
only unacceptable but plain dangerous.

Funny thing though, now that I have a better education - even at 9psi excess
pressure the supervisory alarm might not have sounded.  Even though 13 & 25
only specify testing of the LOW air supervisory device I'd like to offer
that since the sprinkler industry knows better and is educated that we make
it a point to test for high air during our semi-annual inspections and
should the switch not be properly wired by the alarm contractor we note it
as an exception and notify the owners to have it corrected.  I'm pretty sure
that the alarm contractor isnt going to fiddle with the air filling device
to simulate this test so its most likely not connected or even being done.

Opinion time over - work day begins.

Dave,
An AHJ in NJ

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to