Thanks for the information - I will be adjusting my field acceptance testing
procedures now to include this requirement.  I see the problem as being a
gap between the sprinkler installer and alarm tech / electrician.  Even if
the sprinkler tech puts in the proper switch with double contacts to be code
compliant it then falls to the alarm contractor to know the requirement and
properly pick up boths sets of contacts for both high and low pressure
supervision.  I guess the way to handle this up front on plan review is to
specifically cite the requirement on the drawings instead of the typical
'low air supervisory device' notation.

In talking to some contractors on the matter there is an opinion that high
air monitoring isnt all so important but looking at things through my
AHJ-fire colored glasses Im well aware of the negative impact on water
delivery time a system with excessive pressure can have.  I recently had the
cooperation of a contractor during the acceptance testing process and after
we trip tested the system at the design pressures we had a water delivery
time of 53 seconds.  We then refilled the system and increased air pressure
5 and 9 psi above the design pressure.  At 5 psi above the water delivery
was just about 1:45 but at 9 psi over the water delivery was just over 3
minutes.  Im sure we've all seen one or more test video burns in our time
and the thought of delaying water delivery nearly three times over is not
only unacceptable but plain dangerous.

Funny thing though, now that I have a better education - even at 9psi excess
pressure the supervisory alarm might not have sounded.  Even though 13 & 25
only specify testing of the LOW air supervisory device I'd like to offer
that since the sprinkler industry knows better and is educated that we make
it a point to test for high air during our semi-annual inspections and
should the switch not be properly wired by the alarm contractor we note it
as an exception and notify the owners to have it corrected.  I'm pretty sure
that the alarm contractor isnt going to fiddle with the air filling device
to simulate this test so its most likely not connected or even being done.

Opinion time over - work day begins.

Dave,
An AHJ in NJ

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to