UL and FM -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Hankins Sent: 30 October, 2007 4:20 PM To: [email protected] Subject: Re: Fire Pump performance as per the name plate
Dan, Who approved/listed the pump. The allowable deviations would be contained in the test standard. Joe danarbel wrote: > Dear All, > > I have got a problem with a fire pump. > > The pump performance does not match the name plant data. > > The cause is the Diesel Engine. > > The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just over > 5% of the nominal (1760 rpm). > > The result is too high pressure (5% excess) at churning causing operation of > the 175psi relief valves of the sprinkler systems, > > At the other end, 150% flow, the pressure is 5% below the name plant data. > > The question: To what extent the pump supplier is bound by the name plant > performance data. > > The supplier Rep. argues that 5% deviation is within the normal. > > > Dan Arbel > Tel: 972-4-8243337 > Fax: 972-4-8243278 > M: 972-52-2810593 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)