Dan,

Who approved/listed the pump. The allowable deviations would be 
contained in the test standard.

Joe

danarbel wrote:
> Dear All,
>
> I have got a problem with a fire pump.
>
> The pump performance does not match the name plant data. 
>
> The cause is the Diesel Engine. 
>
> The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just
over
> 5% of the nominal (1760 rpm). 
>
> The result is too high pressure (5% excess) at churning causing operation
of
> the 175psi relief valves of the sprinkler systems,
>
> At the other end, 150% flow, the pressure is 5% below the name plant data.

>
> The question: To what extent the pump supplier is bound by the name plant
> performance data. 
>
> The supplier Rep. argues that 5% deviation is within the normal.  
>
>
> Dan Arbel
> Tel: 972-4-8243337
> Fax: 972-4-8243278
> M: 972-52-2810593
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to