Technically the pump selected at 135% of it's rated capacity is not
overloaded.  It is still within the allowable range as set forth by NFPA
20.  If our system demand exceeded 150% of the pumps rated capacity then
you are overloaded.  You do not have to supply 150% of the 135% value.

Again, much of this falls into using common sense and good judgment.
Much of what is written is written to be able to include many scenarios
and we must analyze the situation and make decisions based on our
specific project parameters.  


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Wednesday, October 31, 2007 11:47 AM
To: [email protected]
Subject: RE: Fire pump question/ Why 150% at not less than 65% ?

Thanks Craig,
  I would also never pick a 750 gpm pump for my required capacity of
1100 gpm, let's try another example with 135%.
  I have seen an example in fire protection handbook as below:
  Estimated water demand for sprinklers & hose streams: 1300Gpm at 90
Psi
  1300Gpm/1.35 = 936Gpm & 90Psi/0.75 = 120Psi, So I will pick a pump
rated at 1000Gpm, 120psi and will work at 135% of rated capacity to
supply my demand.
  My question is that, when I choose a pump which is going to work at
135% of rated capacity to supply my demand, then I have already
overloaded the pump, so in case of greater than ESTIMATED flow, it might
not be able to supply this extra demand at not less than 65 percent of
the total ESTIMATED head.
  For example if in case of fire the flow rises to 150% of estimated
flow (1300 x 150% = 1950Gpm) while my pump is rated at 1000Gpm, then can
I be sure than the total head is not less than 65 percent of the total
estimated head (120psi * 65% = 78Psi)?
  Should I check it from the pump curve that at 1950Gpm my head is not
lower than 78Psi?
   
  If NFPA says fire pumps shall furnish not less than 150 percent of
rated capacity at a total head of not less than 65 percent of the total
rated head to provide some safety factor in case of greater than
expected demand at the time of fire, THEN why allows us to choose a pump
working at 135% of rated capacity while this pump has been already
overloaded and might not be able to supply 150% over 135%?
Thanks,
  Reza


   
   
  
capacity to supply my required demand of 1100Gpm at 100Psi


[EMAIL PROTECTED] wrote:
  We would not pick a 750 gpm pump if the demand indicated a required
pump capacity of 1100 gpm. It would not be uncommon to select a 1000 gpm
pump for your 1100 gpm demand. That way you still have the additional
capacity of up to 1500 gpm. 

When you calculate a system at for example .30 gpm per square foot over
a 3,000 sq. ft hydraulically remote area, the numbers come out to a
demand of .30 x 3000 or 900 gpm. In reality the flow from sprinklers in
that 3,000 sq. ft remote area will be greater than that. So for example
I would take that 900 gpm add my hose stream allowance of 500 gpm and
come up with a total "theoretical" demand of 1400 gpm. If I pick a 1500
gpm pump then I have the ability to provide up to 2250 gpm. Many
designers will take that "theoretical" demand and add a safety factor of
10%-15% to that. If we did that we would be more realistically looking
at 1400 gpm + 10% -15% = 1540-1610 gpm of flow within that 3,000 sq. ft
design area. With the 1500 gpm pump selection we are still in a an
acceptable range of below that 150% of 2250 gpm. 

It's just not good to make a selection that tight. Things change
including the condition of underground piping, building layouts,
building uses and such. It's best to allow some flexibility when
selecting the pump so that a small change to one of these doesn't force
an owner to have to buy a new pump.


But I'm sure this is one of several theories and methods and ideas when
it comes to selecting pumps. 



DISCLAIMER: This is not intended to be a complete and detailed analysis
or approach to pump selection. There are other factors involved which
the fire protection technician/designer needs to consider. 

Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Wednesday, October 31, 2007 9:43 AM
To: [email protected]
Subject: Fire pump question/ Why 150% at not less than 65% ?

Hi!
I know that:
1- As per NFPA-20 listed fire pumps shall furnish not less than 150
percent of rated capacity at a total head of not less than 65 percent of
the total rated head to provide some safety factor in case of greater
than expected demand at the time of fire.
2- On the other hand, NFPA allows to choose a fire pump working at 150%
of rated capacity if it delivers the required water flow at required
pressure to fire protection system.

I think these two issues are against each other, because if I choose a
pump which is working at 150% of rated capacity, then I have already
overloaded the pump, so in case of greater than REQUIRED flow, it might
not be able to supply this extra demand at not less than 65 percent of
the total REQUIRED head.

for Example if he required demand is 1100GPM at 100Psi, I can do as
followings:
* 1100gpm/1.5 = 733Gpm, so I will choose a 750GPM Pump.
* 100psi/0.65 = 154Psi, so I will choose a 154psi Pump.
I know it is not usuall to choose a pump working at 150% of rated
capacity, and 135% is more common, this is just a scenario to ask my
question.
So the pump is rated at 750Gpm, 154psi and will work at 150% of rated
capacity to supply my required demand of 1100Gpm at 100Psi. My question
is that If in case of greater than expected demand at the time of fire
the demand increases to 150% of required flow (1100 * 150% = 1650Gpm),
then can I be sure than the total head is not less than 65 percent of
the total REQUIRED head? Should I check it from the pump curve?
Thanks for your attention,
Reza

__________________________________________________
Do You Yahoo!?
Tired of spam? Yahoo! Mail has the best spam protection around
http://mail.yahoo.com _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


 __________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around
http://mail.yahoo.com _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to