I have done the reduced density to 0.07, but do not believe you can use the
QR reduction.

I assume you are in a light hazard since you mentioned the 0.07 density.
You may want to consider small orifice sprinklers to cut down on the over
discharge you would have with 5.6k sprinklers. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Wednesday, December 12, 2007 11:36 AM
To: [email protected]
Subject: RE: Design Area and Density

YES TO THE FIRST NO TO THE SECOND

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, December 12, 2007 11:21 AM
To: [email protected]
Subject: Design Area and Density

Forumites,

A question has arisen here on the correct application of a particular
paragraph of NFPA-13, 2007 ed.

"Section 11.2.3.1.4 (3) Unless the requirements of 11.2.3.1.4(4) are met for
buildings having unsprinklered combustible concealed spaces, as described in
8.15.1.2 and 8.15.6, the minimum area of sprinkler operation for that
portion of the building shall be 3000 ft2 (279 m2). The design area of 3000
ft2 shall be applied only to the sprinkler system or portions of the
sprinkler system that are adjacent to the qualifying combustible concealed
space."

Here's the two issues we're discussing:

1)  If the space in question must does not meet any of the conditions in
11.2.3.1.4(4) and does meet
the descriptions in 8.15.1.2 and 8.15.6, and the area of sprinkler operation
is increased to 3,000 square feet, is it acceptable to reduce the density
for the area to the value shown in Figure 11.2.3.1.1?

For example, if we're covering light hazard occupancy, and are forced to the
3,000 square foot remote area, is it acceptable to use a density of 0.07 gpm
per square foot?

2)  If the area of operation is increased to 3,000 square feet by this
section, can the reduction for use of quick response sprinklers in areas
with ceilings less than 20'-0" in height as noted in 11.2.3.2.3.1 be
applied?

The reason for asking #1 is that this section makes mention of an increase
in the operating area without noting "without revising the density" as is
found in the sections which establish the increase for dry
systems and sloped ceilings greater than 2:12.   So, because it's not 
there does that mean the density
can be revised?

The reason for asking #2 is that there's no clear guidance as to whether the
minimum remote area can be reduced using QR's and low ceilings. 

Any help, greatly appreciated. 

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

__________ NOD32 2719 (20071212) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to