I have done the reduced density to 0.07, but do not believe you can use the QR reduction.
I assume you are in a light hazard since you mentioned the 0.07 density. You may want to consider small orifice sprinklers to cut down on the over discharge you would have with 5.6k sprinklers. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Wednesday, December 12, 2007 11:36 AM To: [email protected] Subject: RE: Design Area and Density YES TO THE FIRST NO TO THE SECOND Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, December 12, 2007 11:21 AM To: [email protected] Subject: Design Area and Density Forumites, A question has arisen here on the correct application of a particular paragraph of NFPA-13, 2007 ed. "Section 11.2.3.1.4 (3) Unless the requirements of 11.2.3.1.4(4) are met for buildings having unsprinklered combustible concealed spaces, as described in 8.15.1.2 and 8.15.6, the minimum area of sprinkler operation for that portion of the building shall be 3000 ft2 (279 m2). The design area of 3000 ft2 shall be applied only to the sprinkler system or portions of the sprinkler system that are adjacent to the qualifying combustible concealed space." Here's the two issues we're discussing: 1) If the space in question must does not meet any of the conditions in 11.2.3.1.4(4) and does meet the descriptions in 8.15.1.2 and 8.15.6, and the area of sprinkler operation is increased to 3,000 square feet, is it acceptable to reduce the density for the area to the value shown in Figure 11.2.3.1.1? For example, if we're covering light hazard occupancy, and are forced to the 3,000 square foot remote area, is it acceptable to use a density of 0.07 gpm per square foot? 2) If the area of operation is increased to 3,000 square feet by this section, can the reduction for use of quick response sprinklers in areas with ceilings less than 20'-0" in height as noted in 11.2.3.2.3.1 be applied? The reason for asking #1 is that this section makes mention of an increase in the operating area without noting "without revising the density" as is found in the sections which establish the increase for dry systems and sloped ceilings greater than 2:12. So, because it's not there does that mean the density can be revised? The reason for asking #2 is that there's no clear guidance as to whether the minimum remote area can be reduced using QR's and low ceilings. Any help, greatly appreciated. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ NOD32 2719 (20071212) Information __________ This message was checked by NOD32 antivirus system. http://www.eset.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)