That's how I understand it.  Other opinions?

Ed Kramer
Littleton, CO

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, December 12, 2007 4:53 PM
To: [email protected]
Subject: Re: Design Area and Density

Ed,

So, if I understand you:

If I have an OH1 occupancy, and fall under the same criteria, say with a 
10'-0" ceiling, I could design:

a)  With a minimum remote area of 3,000 square feet, using a density of 
0.12 gpm/sqft, based on the
area/density curve for OH1, and standard response sprinklers.

b) With a minimum remote area of 3,000 square feet, using a density of 
0.10 gpm/sqft, based on the
area/density curve for OH1, with the area being reduced by use of 
quick-response sprinklers "without
revising the density", but not less than 3,000 square feet, as required 
by 11.2.3.1.4(3).

Is that about right?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Ed Kramer wrote:
> Ken,
>
> Question #1: Yes
>
> Question #2: it depends.  For light hazards, the answer is effectively
'no'.
> Section 11.2.3.2.7.2 says to apply the 3000 sf after all other
> modifications.  Since the light hazard curve goes no higher than 3000 sf,
> the credit for QR sprinklers does you no good.  On the other hand, the
> curves for the ordinary hazards go up to 4000 sf.  So a designer could
> select an initial density/area of .15/4000 (ord group II), then apply a QR
> reduction, then increase the area back up to 3000 sf for a final
> density/area of .15/3000. But the final area must always be 3000 sf
minimum.
>
> Ed Kramer
> Littleton, CO
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]