I believe the intent of the committee was to be prepared for the LARGE area
that could be involved when the fire breaks thru the drywall between the
interstitial space and the protected area.

The question is not solved by how fast the QR heads respond, since they are
blind to the heat of the fire on the other side of the barrier, burning thru
the TJI's or whatever. It's the anticipation that more than 900, or 1500 SF
of fire could reasonably be anticipated once the ceiling starts dropping
from the bottom chord of the TJI's letting loose.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Thursday, December 13, 2007 7:09 AM
To: [email protected]
Subject: RE: Design Area and Density

I have read the sections in question multiple times and I still do not see
conclusively why can't you reduce the 3000 demand area described in
11.2.3.1.1. Even if you apply the reduction with quick response sprinklers
there is still an 1,800 sqft area which is twice as large as the 900 sqft
allowable if the concealed spaces did not exist. This is obviously double
the size reduced; and without reduction the remote area of 1,500 sqft is
doubled to 3,000.

So in proportion you still are allowing for the delay using the same
reasoning used for reducing the 1,500 sqft to 900 sqft; QR heads respond
quicker.

I think if you can not reduce the 3,000 sqft it should state SPECIFICALLY
that no reduction is allowed.
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to