Sorry Ed, I went back and re-read your post, and misunderstood you the first time. Between that and not getting these threads in the right order here at home, caused me to be confused. We do seem to be saying the same thing.
Ed Kramer <[EMAIL PROTECTED]> wrote: I think we're saying the same thing but different words. No adjustment can be made after the DA has been bumped to 3000 sf. But I'm not seeing anything that's says the QR reduction can't be taken prior to the 3000 sf adjustment (as in my example). Ed Kramer Littleton, CO -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt Sent: Wednesday, December 12, 2007 5:09 PM To: [email protected] Subject: Re: Design Area and Density Ken, I am not in the office, and don't have my copy of my 13 handbook, but off the top of my head, so to speak, I disagree with Ed's last post. It is my understanding that the NFPA 13 verbage states words to the effect of... the 3000 sq.ft adjustment shall be applied AFTER all other adjustments have been applied. Any suggestion of applying the QR reduction afterward is, in my opinion, incorrect. So, while I agree with any previous statement that you may "slide" along the appropriate occupancy class design curve to the appropriate lower density corresponding to 3000 sq.ft, it is not appropriate to apply additional corrections after the 3000 sq.ft. adjustment. Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State Fire Protection Corporation 636-946-0011 636-946-5172 "[EMAIL PROTECTED]" wrote: Ed, So, if I understand you: If I have an OH1 occupancy, and fall under the same criteria, say with a 10'-0" ceiling, I could design: a) With a minimum remote area of 3,000 square feet, using a density of 0.12 gpm/sqft, based on the area/density curve for OH1, and standard response sprinklers. b) With a minimum remote area of 3,000 square feet, using a density of 0.10 gpm/sqft, based on the area/density curve for OH1, with the area being reduced by use of quick-response sprinklers "without revising the density", but not less than 3,000 square feet, as required by 11.2.3.1.4(3). Is that about right? PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] e-mail www.ParsleyConsulting.com website Ed Kramer wrote: > Ken, > > Question #1: Yes > > Question #2: it depends. For light hazards, the answer is effectively 'no'. > Section 11.2.3.2.7.2 says to apply the 3000 sf after all other > modifications. Since the light hazard curve goes no higher than 3000 sf, > the credit for QR sprinklers does you no good. On the other hand, the > curves for the ordinary hazards go up to 4000 sf. So a designer could > select an initial density/area of .15/4000 (ord group II), then apply a QR > reduction, then increase the area back up to 3000 sf for a final > density/area of .15/3000. But the final area must always be 3000 sf minimum. > > Ed Kramer > Littleton, CO _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)