Ken,
   
  I am not in the office, and don't have my copy of my 13 handbook, but off the 
top of my head, so to speak, I disagree with Ed's last post.
   
  It is my understanding that the NFPA 13 verbage states words to the effect 
of...
  the 3000 sq.ft adjustment shall be applied AFTER all other adjustments have 
been applied.  Any suggestion of applying the QR reduction afterward is, in my 
opinion, incorrect.
   
  So, while I agree with any previous statement that you may "slide" along the 
appropriate occupancy class design curve to the appropriate lower density 
corresponding to 3000 sq.ft, it is not appropriate to apply additional 
corrections after the 3000 sq.ft. adjustment.
   
   
  Jeff Hewitt, PE, SET, SFPE (Professional Member)
  Corporate Engineer
  Bi-State Fire Protection Corporation
  636-946-0011
  636-946-5172
   

"[EMAIL PROTECTED]" <[EMAIL PROTECTED]> wrote:
  Ed,

So, if I understand you:

If I have an OH1 occupancy, and fall under the same criteria, say with a 
10'-0" ceiling, I could design:

a) With a minimum remote area of 3,000 square feet, using a density of 
0.12 gpm/sqft, based on the
area/density curve for OH1, and standard response sprinklers.

b) With a minimum remote area of 3,000 square feet, using a density of 
0.10 gpm/sqft, based on the
area/density curve for OH1, with the area being reduced by use of 
quick-response sprinklers "without
revising the density", but not less than 3,000 square feet, as required 
by 11.2.3.1.4(3).

Is that about right?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] e-mail
www.ParsleyConsulting.com website



Ed Kramer wrote:
> Ken,
>
> Question #1: Yes
>
> Question #2: it depends. For light hazards, the answer is effectively 'no'.
> Section 11.2.3.2.7.2 says to apply the 3000 sf after all other
> modifications. Since the light hazard curve goes no higher than 3000 sf,
> the credit for QR sprinklers does you no good. On the other hand, the
> curves for the ordinary hazards go up to 4000 sf. So a designer could
> select an initial density/area of .15/4000 (ord group II), then apply a QR
> reduction, then increase the area back up to 3000 sf for a final
> density/area of .15/3000. But the final area must always be 3000 sf minimum.
>
> Ed Kramer
> Littleton, CO
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to