Ed,

So, if I understand you:

If I have an OH1 occupancy, and fall under the same criteria, say with a 10'-0" ceiling, I could design:

a) With a minimum remote area of 3,000 square feet, using a density of 0.12 gpm/sqft, based on the
area/density curve for OH1, and standard response sprinklers.

b) With a minimum remote area of 3,000 square feet, using a density of 0.10 gpm/sqft, based on the area/density curve for OH1, with the area being reduced by use of quick-response sprinklers "without revising the density", but not less than 3,000 square feet, as required by 11.2.3.1.4(3).

Is that about right?

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Ed Kramer wrote:
Ken,

Question #1: Yes

Question #2: it depends.  For light hazards, the answer is effectively 'no'.
Section 11.2.3.2.7.2 says to apply the 3000 sf after all other
modifications.  Since the light hazard curve goes no higher than 3000 sf,
the credit for QR sprinklers does you no good.  On the other hand, the
curves for the ordinary hazards go up to 4000 sf.  So a designer could
select an initial density/area of .15/4000 (ord group II), then apply a QR
reduction, then increase the area back up to 3000 sf for a final
density/area of .15/3000. But the final area must always be 3000 sf minimum.

Ed Kramer
Littleton, CO