Ken, Question #1: Yes
Question #2: it depends. For light hazards, the answer is effectively 'no'. Section 11.2.3.2.7.2 says to apply the 3000 sf after all other modifications. Since the light hazard curve goes no higher than 3000 sf, the credit for QR sprinklers does you no good. On the other hand, the curves for the ordinary hazards go up to 4000 sf. So a designer could select an initial density/area of .15/4000 (ord group II), then apply a QR reduction, then increase the area back up to 3000 sf for a final density/area of .15/3000. But the final area must always be 3000 sf minimum. Ed Kramer Littleton, CO Forumites, A question has arisen here on the correct application of a particular paragraph of NFPA-13, 2007 ed. "Section 11.2.3.1.4 (3) Unless the requirements of 11.2.3.1.4(4) are met for buildings having unsprinklered combustible concealed spaces, as described in 8.15.1.2 and 8.15.6, the minimum area of sprinkler operation for that portion of the building shall be 3000 ft2 (279 m2). The design area of 3000 ft2 shall be applied only to the sprinkler system or portions of the sprinkler system that are adjacent to the qualifying combustible concealed space." Here's the two issues we're discussing: 1) If the space in question must does not meet any of the conditions in 11.2.3.1.4(4) and does meet the descriptions in 8.15.1.2 and 8.15.6, and the area of sprinkler operation is increased to 3,000 square feet, is it acceptable to reduce the density for the area to the value shown in Figure 11.2.3.1.1? For example, if we're covering light hazard occupancy, and are forced to the 3,000 square foot remote area, is it acceptable to use a density of 0.07 gpm per square foot? 2) If the area of operation is increased to 3,000 square feet by this section, can the reduction for use of quick response sprinklers in areas with ceilings less than 20'-0" in height as noted in 11.2.3.2.3.1 be applied? The reason for asking #1 is that this section makes mention of an increase in the operating area without noting "without revising the density" as is found in the sections which establish the increase for dry systems and sloped ceilings greater than 2:12. So, because it's not there does that mean the density can be revised? The reason for asking #2 is that there's no clear guidance as to whether the minimum remote area can be reduced using QR's and low ceilings. Any help, greatly appreciated. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)