Ken,

Question #1: Yes

Question #2: it depends.  For light hazards, the answer is effectively 'no'.
Section 11.2.3.2.7.2 says to apply the 3000 sf after all other
modifications.  Since the light hazard curve goes no higher than 3000 sf,
the credit for QR sprinklers does you no good.  On the other hand, the
curves for the ordinary hazards go up to 4000 sf.  So a designer could
select an initial density/area of .15/4000 (ord group II), then apply a QR
reduction, then increase the area back up to 3000 sf for a final
density/area of .15/3000. But the final area must always be 3000 sf minimum.

Ed Kramer
Littleton, CO





Forumites,

A question has arisen here on the correct application of a particular 
paragraph of NFPA-13, 2007 ed.

"Section 11.2.3.1.4 (3) Unless the requirements of 11.2.3.1.4(4) are met 
for buildings having
unsprinklered combustible concealed spaces, as described in 8.15.1.2 and 
8.15.6, the minimum
area of sprinkler operation for that portion of the building shall be 
3000 ft2 (279 m2). The design
area of 3000 ft2 shall be applied only to the sprinkler system or 
portions of the sprinkler system
that are adjacent to the qualifying combustible concealed space."

Here's the two issues we're discussing:

1)  If the space in question must does not meet any of the conditions in 
11.2.3.1.4(4) and does meet
the descriptions in 8.15.1.2 and 8.15.6, and the area of sprinkler 
operation is increased to 3,000
square feet, is it acceptable to reduce the density for the area to the 
value shown in Figure 11.2.3.1.1?

For example, if we're covering light hazard occupancy, and are forced to 
the 3,000 square foot remote
area, is it acceptable to use a density of 0.07 gpm per square foot?

2)  If the area of operation is increased to 3,000 square feet by this 
section, can the reduction for use of
quick response sprinklers in areas with ceilings less than 20'-0" in 
height as noted in 11.2.3.2.3.1 be
applied?

The reason for asking #1 is that this section makes mention of an 
increase in the operating area without
noting "without revising the density" as is found in the sections which 
establish the increase for dry
systems and sloped ceilings greater than 2:12.   So, because it's not 
there does that mean the density
can be revised?

The reason for asking #2 is that there's no clear guidance as to whether 
the minimum remote area can be
reduced using QR's and low ceilings. 

Any help, greatly appreciated. 

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website