A word of caution when it comes to hoses.  As stated before it is a bad
idea to install hoses for use by untrained persons.   In projects where
internal hose valves are required we do not put hoses unless the owner
requests them for use by their trained personnel.  Otherwise we only
provide hose valves for use by the fire department with them using their
hose, not the owners hose.  If there is a hose present, I've heard that
the fire department will often disconnect them and hook up their own.
Do you have a fire department that will respond to a fire?  What is
their preference as far as size of hoses or no hoses?  

If you are directed to install hoses it is the owners choice most often
when deciding whether to use flat hose or the hard rubber hose.  So you
can decide if the owner has no preference.  

Were the manufacturers you checked who sold the 1" hose reels labeling
them for fire protection or just general use?  




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reza
Esmaeili
Sent: Thursday, February 21, 2008 10:30 AM
To: [email protected]
Subject: Re: Hose Reels Requirements & Minimum Outlet Pressure

As I was searching in NFPA codes, I noticed that there are not that
much information about hose reels. Can we use 1 in. semi rigid hose on
hose reels instead of lay flat hoses in occupancies required 1 1/2 hose
stations? Because using a hose reel is much more easier for occupants,
Is  there any guide when I can use hose reels instead of lay flat hoses?
   
  What about minimum pressure requirements? As per NFPA-14 residual
pressure should be 65 psi at the outlet of the hydraulically most remote
1
 1/2 in. hose station, but as per my experience hose reels need lower
pressure to work fine in comparison with lay flat hoses. Do I need 65
psi pressure even if I use hose reels?
   
  The reason I am asking this question is that in a combined system, as
my standpipe system needs much more pressure than my sprinkler system,
if I can reduce my standpipe required pressure using hose reels I can
save much in selection of smaller fire pump & water tank, but I am not
sure if I am allowed.
  I was checking a hose reel manufacture data sheets and I noticed that
a 1 in. hose reel in 45 psi pressure flow is 21 Gpm with throw  distance
of 40 ft. Isn't it enough for a occupant use? am I allowed to design
based on 45 psi instead of 65 psi in 1 1/2 in outlets while I am using
hose reels?
  Thanks,
  Reza


       
---------------------------------
Never miss a thing.   Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to