Hi Craig! Thanks for your attention, the hose I mentioned is for fire protection made by Kidde company. I agree with you that 21/2 in. connections are without hose and FD will bring their own hoses, but in an occupancy where Class II standpipe system is required and as per NFPA-14 I had to consider 65psi minimum pressure at 11/2 in outlets of hose stations, what happen if I use hose reels? Am I allowed to reduce pressure (Ex. to 45Psi) as hose reels work fine in lower pressure? Thanks, Reza [EMAIL PROTECTED] wrote: A word of caution when it comes to hoses. As stated before it is a bad idea to install hoses for use by untrained persons. In projects where internal hose valves are required we do not put hoses unless the owner requests them for use by their trained personnel. Otherwise we only provide hose valves for use by the fire department with them using their hose, not the owners hose. If there is a hose present, I've heard that the fire department will often disconnect them and hook up their own. Do you have a fire department that will respond to a fire? What is their preference as far as size of hoses or no hoses?
If you are directed to install hoses it is the owners choice most often when deciding whether to use flat hose or the hard rubber hose. So you can decide if the owner has no preference. Were the manufacturers you checked who sold the 1" hose reels labeling them for fire protection or just general use? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Reza Esmaeili Sent: Thursday, February 21, 2008 10:30 AM To: [email protected] Subject: Re: Hose Reels Requirements & Minimum Outlet Pressure As I was searching in NFPA codes, I noticed that there are not that much information about hose reels. Can we use 1 in. semi rigid hose on hose reels instead of lay flat hoses in occupancies required 1 1/2 hose stations? Because using a hose reel is much more easier for occupants, Is there any guide when I can use hose reels instead of lay flat hoses? What about minimum pressure requirements? As per NFPA-14 residual pressure should be 65 psi at the outlet of the hydraulically most remote 1 1/2 in. hose station, but as per my experience hose reels need lower pressure to work fine in comparison with lay flat hoses. Do I need 65 psi pressure even if I use hose reels? The reason I am asking this question is that in a combined system, as my standpipe system needs much more pressure than my sprinkler system, if I can reduce my standpipe required pressure using hose reels I can save much in selection of smaller fire pump & water tank, but I am not sure if I am allowed. I was checking a hose reel manufacture data sheets and I noticed that a 1 in. hose reel in 45 psi pressure flow is 21 Gpm with throw distance of 40 ft. Isn't it enough for a occupant use? am I allowed to design based on 45 psi instead of 65 psi in 1 1/2 in outlets while I am using hose reels? Thanks, Reza --------------------------------- Never miss a thing. Make Yahoo your homepage. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) --------------------------------- Looking for last minute shopping deals? Find them fast with Yahoo! Search. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)