I phoned NFPA & asked the below question from them, they told me in an 
occupancy where you need class II standpipe system, it is not difference if you 
connect flat hose or hard hose reel to 1 1/2 hose connection and as per NFPA-14 
residual pressure should be 65 psi at the outlet of the hydraulically most 
remote 11/2 in outlet.
  As per my per my experience hose reels need lower pressure to work fine in 
comparison with lay flat hoses. I was checking a fire hose reel manufacture 
data sheets and I noticed that a 1 in. hose reel in 45 psi pressure flow is 21 
Gpm with throw
distance of 40 ft. Isn't it enough for a occupant use? Why I am not allowed to 
design
based on 45 psi instead of 65 psi in 1 1/2 in outlets while I am using hose 
reels?
  Thanks,
  Reza

Reza Esmaeili <[EMAIL PROTECTED]> wrote:
  As I was searching in NFPA codes, I noticed that there are not that
much information about hose reels. Can we use 1 in. semi rigid hose on
hose reels instead of lay flat hoses in occupancies required 1 1/2 hose
stations? Because using a hose reel is much more easier for occupants, Is
there any guide when I can use hose reels instead of lay flat hoses?

What about minimum pressure requirements? As per NFPA-14 residual
pressure should be 65 psi at the outlet of the hydraulically most remote 1
1/2 in. hose station, but as per my experience hose reels need lower
pressure to work fine in comparison with lay flat hoses. Do I need 65
psi pressure even if I use hose reels?

The reason I am asking this question is that in a combined system, as
my standpipe system needs much more pressure than my sprinkler system,
if I can reduce my standpipe required pressure using hose reels I can
save much in selection of smaller fire pump & water tank, but I am not
sure if I am allowed.
I was checking a hose reel manufacture data sheets and I noticed that
a 1 in. hose reel in 45 psi pressure flow is 21 Gpm with throw
distance of 40 ft. Isn't it enough for a occupant use? am I allowed to design
based on 45 psi instead of 65 psi in 1 1/2 in outlets while I am using
hose reels?
Thanks,
Reza



---------------------------------
Never miss a thing. Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Looking for last minute shopping deals?  Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to