In the case you present, Craig, you'd need a valve room with heat (in TX, also AC)
But the code does not mandate a valve room, since one another job you could stick it on the other side of the wall in a heated area. Glc Ps- word to wise- don't pick code battles with JAD without a lot of research and ammo :) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, March 13, 2008 1:54 PM To: [email protected] Subject: RE: Dry System Size And in a wide open space where temps could fall below 40 degrees, how would you accomplish that without the valve room? Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Denhardt Sent: Thursday, March 13, 2008 1:43 PM To: [email protected] Subject: RE: Dry System Size You do not need a valve room. The valve must be maintained above freezing is the only requirement as far as temperature is concerned. John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)