In the case you present, Craig, you'd need a valve room with heat (in TX,
also AC)

But the code does not mandate a valve room, since one another job you could
stick it on the other side of the wall in a heated area.

Glc
Ps- word to wise- don't pick code battles with JAD without a lot of research
and ammo :)

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, March 13, 2008 1:54 PM
To: [email protected]
Subject: RE: Dry System Size

And in a wide open space where temps could fall below 40 degrees, how
would you accomplish that without the valve room? 


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Denhardt
Sent: Thursday, March 13, 2008 1:43 PM
To: [email protected]
Subject: RE: Dry System Size

You do not need a valve room.  The valve must be maintained above
freezing is the only requirement as far as temperature is concerned.

John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to