If the closure of those valves will impair the operation of the system
(which I believe they will) they need to be monitored.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of RFI -
Bismarck
Sent: Wednesday, May 21, 2008 10:40 AM
To: [email protected]
Subject: Sectional Valves...

 

I think I asked this already... and apologize for regurgitating it!  I
have a bldg. that is 'U-shaped' in nature.  The system is of CPVC in
nature - fairly small.  Prior to going into the 'legs' of the 'U' - the
contractor wants to have (2) ball valves installed to isolate each wing
for maintenance purposes.  Do these ball valves need to be of a
'monitored' (wired to panel) type or can they be just run-of-the-mill
ball valves?

 

Imho - I believe they should be 'monitored' valves.  Thanks!

 