Thom,

You can look at the backflow in two ways. Because it is the water
purveyors' rule that requires them (and in Washington at least
plumber's work by law) you could say the sprinkler system doesn't
start until after the second valve. Or you could say that because they
are listed with those ball valves attached they are part of a listed
system and so acceptable in the all alphabet soup flavors of 13. When
on drum drips they under ancillary use and are also acceptable.

On 5/22/08, Thom McMahon <[EMAIL PROTECTED]> wrote:
> We use quite a few of them on our 13D backflows which all seem to come with
>  ball valves.
>  We've also installed them at the owner request on the drum drip ball valves
>  of dry systems. You need a slow close control valve for a sectional valve,
>  to prevent water hammer, so these won't work, since 1/4 turn ball valves are
>  anything but "Slow Close"
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
>  Sent: Wednesday, May 21, 2008 4:35 PM
>  To: [email protected]
>  Subject: RE: Sectional Valves...
>
>  Actually Charles, it clamps to the valve body.  Meant for a ball valve only,
>  like when you have a listed bfp assembly with ball valves and they have to
>  be monitored.
>  Not cheap!  They list for $225.
>
>  Tom
>  Go Red Sox!
>
>
>  Hello RFI,
>
>  Potter makes a switch that can be added to ball valves for this RBVS, BUT
>  since it clamps to the pipe for mounting it might not be suitable for use
>  with CPVC.
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to