The reason the ball valves were approved for R systems was the statement that backflows are approved with them. This is NOT the case. There have always been backflows listed without the ball valves. One maker uses LBV(less ball valves) as the designator. I have many times had the ball valves removed and the gate/butterball installed. I do not ever remember being limited on backflows because of ball valves. I personally think the ball valves should go away, and stay gone.
R/ Matt Matthew J. Willis Living Water Fire Protection, LLC. 1160 McKenzie Rd. PO Box 877 Cantonment, FL. 32533 850-937-1850 Voice 850-937-1852 Facsimile [EMAIL PROTECTED] ----- >-----Original Message----- ----- >From: [EMAIL PROTECTED] ----- >[mailto:[EMAIL PROTECTED] On ----- >Behalf Of Ron Greenman ----- >Sent: Wednesday, May 21, 2008 6:14 PM ----- >To: [email protected] ----- >Subject: Re: Sectional Valves... ----- > ----- >Thom, ----- > ----- >You can look at the backflow in two ways. Because it is ----- >the water purveyors' rule that requires them (and in ----- >Washington at least plumber's work by law) you could say ----- >the sprinkler system doesn't start until after the ----- >second valve. Or you could say that because they are ----- >listed with those ball valves attached they are part of ----- >a listed system and so acceptable in the all alphabet ----- >soup flavors of 13. When on drum drips they under ----- >ancillary use and are also acceptable. ----- > ----- >On 5/22/08, Thom McMahon <[EMAIL PROTECTED]> wrote: ----- >> We use quite a few of them on our 13D backflows which ----- >all seem to come ----- >> with ball valves. ----- >> We've also installed them at the owner request on the ----- >drum drip ball ----- >> valves of dry systems. You need a slow close control ----- >valve for a ----- >> sectional valve, to prevent water hammer, so these ----- >won't work, since ----- >> 1/4 turn ball valves are anything but "Slow Close" ----- >> ----- >> ----- >> -----Original Message----- ----- >> From: [EMAIL PROTECTED] ----- >> [mailto:[EMAIL PROTECTED] On ----- >Behalf Of Tom ----- >> Duross ----- >> Sent: Wednesday, May 21, 2008 4:35 PM ----- >> To: [email protected] ----- >> Subject: RE: Sectional Valves... ----- >> ----- >> Actually Charles, it clamps to the valve body. Meant ----- >for a ball ----- >> valve only, like when you have a listed bfp assembly ----- >with ball valves ----- >> and they have to be monitored. ----- >> Not cheap! They list for $225. ----- >> ----- >> Tom ----- >> Go Red Sox! ----- >> ----- >> ----- >> Hello RFI, ----- >> ----- >> Potter makes a switch that can be added to ball ----- >valves for this RBVS, ----- >> BUT since it clamps to the pipe for mounting it might ----- >not be suitable ----- >> for use with CPVC. ----- >> ----- >> _______________________________________________ ----- >> Sprinklerforum mailing list ----- >> [email protected] ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum ----- >> ----- >> To Unsubscribe, send an email ----- >> to:[EMAIL PROTECTED] ----- >> (Put the word unsubscribe in the subject field) ----- >> ----- >> _______________________________________________ ----- >> Sprinklerforum mailing list ----- >> [email protected] ----- >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum ----- >> ----- >> To Unsubscribe, send an email ----- >> to:[EMAIL PROTECTED] ----- >> (Put the word unsubscribe in the subject field) ----- >> ----- > ----- > ----- >-- ----- >Ron Greenman ----- >at home.... ----- >_______________________________________________ ----- >Sprinklerforum mailing list ----- >[email protected] ----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum ----- > ----- >To Unsubscribe, send an email ----- >to:[EMAIL PROTECTED] ----- >(Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)