You've got it! Working or continuous pressure is the rating of the
components, not the maximum pressure to which they may be subjected. Just as
a 125# screw flange will hold 400 Psi of water pressure, but not steam or
oil. All things are relative.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of IPA
Sent: Thursday, May 29, 2008 4:03 PM
To: sprinklerforum
Subject: 200 psi test for components rated 175

I've got this question posed to me:

Backflow preventor is rated at 175 (as are most of the fire sprinkler
components) yet we are required to do a 200 psi test. Is the keyword here
"working pressure" of 175 psi or am I missing something?

thx,