I'll bite - why not?   If the Fire Department pumps into the FDC, isn't
it likely to back pressure the BFP to at least 150?  And if so, wouldn't
it be prudent to test the assembly?

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Thursday, May 29, 2008 3:30 PM
To: IPA
Subject: Re: 200 psi test for components rated 175

Hello IPA,

I for one have never put 200 on the backflow, I will not either.

Thursday, May 29, 2008, 6:03:25 PM, you wrote:

> I've got this question posed to me:

> Backflow preventor is rated at 175 (as are most of the fire sprinkler
> components) yet we are required to do a 200 psi test. Is the keyword
here
> "working pressure" of 175 psi or am I missing something?

> thx,
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles Thurston
mailto:[EMAIL PROTECTED]
  Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to